EmonHub stops sending data to Emoncms.org
My EmonHub service has stopped sending data to Emoncms.org. It has happened three times since the issue below.
Each time I have discovered it I have found the EmonHub service is still running and posting data to the local EmonBase but not to Emoncms.org.
When I restart the EmonHub service the posts to Emoncms.org recommence and things appear normal.
@TrystanLea @Gwil @glyn.hudson
Sometimes the queues at emoncms.org get stuck. Your data is still received (you should see an ‘ok’ in the logs), but it doesn’t appear in your dashboard.
If emonhub cannot reach the server, you will see that in the logs and then emonhub will buffer the data.
Actually the worst thing you could do is to restart the service as any buffered data is then lost.
Thanks Brian. The tip about restarting the service is noted.
On the previous occasions, when I looked at the logs there was no indication that the data was being sent to emoncms.org (and no ‘ok’). Normally the log looks like this.
However on the subject occasions, the ‘emoncmsorg sending’ entries were not present.
I will post back here again if the problem reoccurs.
Hi Brian,
EmonHub appears to have stopped posting to emoncms.org again. This is what the log looks like tonight.
From the data on emoncms.org, it looks like the posting stopped approximately 24 hours ago.
Noting your comments above, I will not restart the service until advised in case someone wants to explore the state of my emonbase.
The MQTT posting is to the local Pi not emoncms.org. you should have emoncmsorg entries.
Please do not post screenshots, but rather post the actual text between 3 backticks on a line above and below.
I agree - I should have emoncmsorg entries …
Any thoughts on why they have stopped?
Edit the emonhub config via the Web UI and set the log level to debug
[hub]
loglevel = DEBUG
wait for that to propagate (no need to restart emonhub) and debug messages will flow.
Please post a short extract - you will see the same messages appear.
Here is the debug level extract.
2020-06-30 23:16:36,933 DEBUG    RFM2Pi     22428 NEW FRAME : OK 15 166 106 84 85 168 8 118 70 85 85 85 85 175 85 85 85 71 69 86 85 173 114 85 85 126 148 87 85 85 85 85 85 171 170 170 170 108 85 85 85 106 81 101 32 101 32 101 32 85 85 85 85 85 (-69)
2020-06-30 23:16:36,937 DEBUG    RFM2Pi     22428 Timestamp : 1593522996.9333172
2020-06-30 23:16:36,938 DEBUG    RFM2Pi     22428 From Node : 15
2020-06-30 23:16:36,938 DEBUG    RFM2Pi     22428    Values : [81907, 240.61, 48.99, 0, 0, 250, 0, 200722, 10232, 180523, 0, -0.02, -0.01, 0.5700000000000001, 0, 10.870000000000001, 300, 300, 300, 0, 0]
2020-06-30 23:16:36,939 DEBUG    RFM2Pi     22428      RSSI : -69
2020-06-30 23:16:36,939 DEBUG    RFM2Pi     22428 Sent to channel(start)' : ToEmonCMS
2020-06-30 23:16:36,940 DEBUG    RFM2Pi     22428 Sent to channel(end)' : ToEmonCMS
2020-06-30 23:16:37,097 DEBUG    MQTT       Publishing: emon/emontx3cm15/MSG 81907
2020-06-30 23:16:37,099 DEBUG    MQTT       Publishing: emon/emontx3cm15/Vrms 240.61
2020-06-30 23:16:37,101 DEBUG    MQTT       Publishing: emon/emontx3cm15/F 48.99
2020-06-30 23:16:37,103 DEBUG    MQTT       Publishing: emon/emontx3cm15/P1 0
2020-06-30 23:16:37,104 DEBUG    MQTT       Publishing: emon/emontx3cm15/P2 0
2020-06-30 23:16:37,106 DEBUG    MQTT       Publishing: emon/emontx3cm15/P3 250
2020-06-30 23:16:37,107 DEBUG    MQTT       Publishing: emon/emontx3cm15/P4 0
2020-06-30 23:16:37,108 DEBUG    MQTT       Publishing: emon/emontx3cm15/E1 200722
2020-06-30 23:16:37,110 DEBUG    MQTT       Publishing: emon/emontx3cm15/E2 10232
2020-06-30 23:16:37,112 DEBUG    MQTT       Publishing: emon/emontx3cm15/E3 180523
2020-06-30 23:16:37,113 DEBUG    MQTT       Publishing: emon/emontx3cm15/E4 0
2020-06-30 23:16:37,115 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf1 -0.02
2020-06-30 23:16:37,116 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf2 -0.01
2020-06-30 23:16:37,118 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf3 0.5700000000000001
2020-06-30 23:16:37,119 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf4 0
2020-06-30 23:16:37,121 DEBUG    MQTT       Publishing: emon/emontx3cm15/T1 10.870000000000001
2020-06-30 23:16:37,122 DEBUG    MQTT       Publishing: emon/emontx3cm15/T2 300
2020-06-30 23:16:37,124 DEBUG    MQTT       Publishing: emon/emontx3cm15/T3 300
2020-06-30 23:16:37,126 DEBUG    MQTT       Publishing: emon/emontx3cm15/T4 300
2020-06-30 23:16:37,127 DEBUG    MQTT       Publishing: emon/emontx3cm15/pulse 0
2020-06-30 23:16:37,129 DEBUG    MQTT       Publishing: emon/emontx3cm15/error 0
2020-06-30 23:16:37,130 DEBUG    MQTT       Publishing: emon/emontx3cm15/rssi -69
2020-06-30 23:16:37,131 INFO     MQTT       Publishing: emonhub/rx/15/values 81907,240.61,48.99,0,0,250,0,200722,10232,180523,0,-0.02,-0.01,0.5700000000000001,0,10.870000000000001,300,300,300,0,0,-69
At least the next 6 sets of entries look like they follow the same pattern.
Ok can you now restart emonhub and post the log - first 6 cycles or so.
As requested.
2020-06-30 23:36:08,882 DEBUG    RFM2Pi     7 NEW FRAME : OK 15 61 21 84 85 187 8 221 70 85 85 85 85 95 87 85 85 71 69 86 85 173 114 85 85 217 148 87 85 85 85 85 85 171 170 171 170 11 85 85 85 106 81 101 32 101 32 101 32 85 85 85 85 85 (-68)
2020-06-30 23:36:08,886 DEBUG    RFM2Pi     7 Timestamp : 1593524168.88166
2020-06-30 23:36:08,887 DEBUG    RFM2Pi     7 From Node : 15
2020-06-30 23:36:08,887 DEBUG    RFM2Pi     7    Values : [82024, 240.46, 50, 0, 0, 522, 0, 200722, 10232, 180620, 0, -0.02, -0.02, 0.9400000000000001, 0, 10.870000000000001, 300, 300, 300, 0, 0]
2020-06-30 23:36:08,888 DEBUG    RFM2Pi     7      RSSI : -68
2020-06-30 23:36:08,888 DEBUG    RFM2Pi     7 Sent to channel(start)' : ToEmonCMS
2020-06-30 23:36:08,889 DEBUG    RFM2Pi     7 Sent to channel(end)' : ToEmonCMS
2020-06-30 23:36:08,987 INFO     MQTT       Connecting to MQTT Server
2020-06-30 23:36:09,083 DEBUG    emoncmsorg Buffer size: 1
2020-06-30 23:36:09,085 INFO     emoncmsorg sending: https://emoncms.org/input/bulk.json?apikey=E-M-O-N-C-M-S-A-P-I-K-E-Y&data=[[1593524168.88166,15,82024,240.46,50,0,0,522,0,200722,10232,180620,0,-0.02,-0.02,0.9400000000000001,0,10.870000000000001,300,300,300,0,0,-68]]&sentat=1593524169
2020-06-30 23:36:09,098 INFO     MQTT       connection status: Connection successful
2020-06-30 23:36:09,100 DEBUG    MQTT       CONACK => Return code: 0
2020-06-30 23:36:09,203 INFO     MQTT       on_subscribe
2020-06-30 23:36:10,110 DEBUG    emoncmsorg acknowledged receipt with 'ok' from https://emoncms.org
2020-06-30 23:36:18,882 DEBUG    RFM2Pi     8 NEW FRAME : OK 15 60 21 84 85 184 8 221 70 85 85 85 85 84 87 85 85 71 69 86 85 173 114 85 85 216 148 87 85 85 85 85 85 171 170 171 170 11 85 85 85 106 81 101 32 101 32 101 32 85 85 85 85 85 (-69)
2020-06-30 23:36:18,886 DEBUG    RFM2Pi     8 Timestamp : 1593524178.882304
2020-06-30 23:36:18,886 DEBUG    RFM2Pi     8 From Node : 15
2020-06-30 23:36:18,887 DEBUG    RFM2Pi     8    Values : [82025, 240.45000000000002, 50, 0, 0, 513, 0, 200722, 10232, 180621, 0, -0.02, -0.02, 0.9400000000000001, 0, 10.870000000000001, 300, 300, 300, 0, 0]
2020-06-30 23:36:18,888 DEBUG    RFM2Pi     8      RSSI : -69
2020-06-30 23:36:18,888 DEBUG    RFM2Pi     8 Sent to channel(start)' : ToEmonCMS
2020-06-30 23:36:18,889 DEBUG    RFM2Pi     8 Sent to channel(end)' : ToEmonCMS
2020-06-30 23:36:18,968 DEBUG    MQTT       Publishing: emon/emontx3cm15/MSG 82025
2020-06-30 23:36:18,970 DEBUG    MQTT       Publishing: emon/emontx3cm15/Vrms 240.45000000000002
2020-06-30 23:36:18,971 DEBUG    MQTT       Publishing: emon/emontx3cm15/F 50
2020-06-30 23:36:18,972 DEBUG    MQTT       Publishing: emon/emontx3cm15/P1 0
2020-06-30 23:36:18,973 DEBUG    MQTT       Publishing: emon/emontx3cm15/P2 0
2020-06-30 23:36:18,975 DEBUG    MQTT       Publishing: emon/emontx3cm15/P3 513
2020-06-30 23:36:18,976 DEBUG    MQTT       Publishing: emon/emontx3cm15/P4 0
2020-06-30 23:36:18,977 DEBUG    MQTT       Publishing: emon/emontx3cm15/E1 200722
2020-06-30 23:36:18,978 DEBUG    MQTT       Publishing: emon/emontx3cm15/E2 10232
2020-06-30 23:36:18,979 DEBUG    MQTT       Publishing: emon/emontx3cm15/E3 180621
2020-06-30 23:36:18,981 DEBUG    MQTT       Publishing: emon/emontx3cm15/E4 0
2020-06-30 23:36:18,982 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf1 -0.02
2020-06-30 23:36:18,983 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf2 -0.02
2020-06-30 23:36:18,985 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf3 0.9400000000000001
2020-06-30 23:36:18,986 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf4 0
2020-06-30 23:36:18,987 DEBUG    MQTT       Publishing: emon/emontx3cm15/T1 10.870000000000001
2020-06-30 23:36:18,989 DEBUG    MQTT       Publishing: emon/emontx3cm15/T2 300
2020-06-30 23:36:18,990 DEBUG    MQTT       Publishing: emon/emontx3cm15/T3 300
2020-06-30 23:36:18,992 DEBUG    MQTT       Publishing: emon/emontx3cm15/T4 300
2020-06-30 23:36:18,993 DEBUG    MQTT       Publishing: emon/emontx3cm15/pulse 0
2020-06-30 23:36:18,994 DEBUG    MQTT       Publishing: emon/emontx3cm15/error 0
2020-06-30 23:36:18,995 DEBUG    MQTT       Publishing: emon/emontx3cm15/rssi -69
2020-06-30 23:36:18,995 INFO     MQTT       Publishing: emonhub/rx/15/values 82025,240.45000000000002,50,0,0,513,0,200722,10232,180621,0,-0.02,-0.02,0.9400000000000001,0,10.870000000000001,300,300,300,0,0,-69
2020-06-30 23:36:28,876 DEBUG    RFM2Pi     9 NEW FRAME : OK 15 63 21 84 85 187 8 221 70 85 85 85 85 86 87 85 85 71 69 86 85 173 114 85 85 219 148 87 85 85 85 85 85 171 170 171 170 11 85 85 85 106 81 101 32 101 32 101 32 85 85 85 85 85 (-69)
2020-06-30 23:36:28,880 DEBUG    RFM2Pi     9 Timestamp : 1593524188.8760293
2020-06-30 23:36:28,881 DEBUG    RFM2Pi     9 From Node : 15
2020-06-30 23:36:28,881 DEBUG    RFM2Pi     9    Values : [82026, 240.46, 50, 0, 0, 515, 0, 200722, 10232, 180622, 0, -0.02, -0.02, 0.9400000000000001, 0, 10.870000000000001, 300, 300, 300, 0, 0]
2020-06-30 23:36:28,882 DEBUG    RFM2Pi     9      RSSI : -69
2020-06-30 23:36:28,883 DEBUG    RFM2Pi     9 Sent to channel(start)' : ToEmonCMS
2020-06-30 23:36:28,883 DEBUG    RFM2Pi     9 Sent to channel(end)' : ToEmonCMS
2020-06-30 23:36:29,209 DEBUG    MQTT       Publishing: emon/emontx3cm15/MSG 82026
2020-06-30 23:36:29,210 DEBUG    MQTT       Publishing: emon/emontx3cm15/Vrms 240.46
2020-06-30 23:36:29,212 DEBUG    MQTT       Publishing: emon/emontx3cm15/F 50
2020-06-30 23:36:29,213 DEBUG    MQTT       Publishing: emon/emontx3cm15/P1 0
2020-06-30 23:36:29,214 DEBUG    MQTT       Publishing: emon/emontx3cm15/P2 0
2020-06-30 23:36:29,215 DEBUG    MQTT       Publishing: emon/emontx3cm15/P3 515
2020-06-30 23:36:29,217 DEBUG    MQTT       Publishing: emon/emontx3cm15/P4 0
2020-06-30 23:36:29,218 DEBUG    MQTT       Publishing: emon/emontx3cm15/E1 200722
2020-06-30 23:36:29,220 DEBUG    MQTT       Publishing: emon/emontx3cm15/E2 10232
2020-06-30 23:36:29,221 DEBUG    MQTT       Publishing: emon/emontx3cm15/E3 180622
2020-06-30 23:36:29,223 DEBUG    MQTT       Publishing: emon/emontx3cm15/E4 0
2020-06-30 23:36:29,225 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf1 -0.02
2020-06-30 23:36:29,227 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf2 -0.02
2020-06-30 23:36:29,228 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf3 0.9400000000000001
2020-06-30 23:36:29,230 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf4 0
2020-06-30 23:36:29,231 DEBUG    MQTT       Publishing: emon/emontx3cm15/T1 10.870000000000001
2020-06-30 23:36:29,232 DEBUG    MQTT       Publishing: emon/emontx3cm15/T2 300
2020-06-30 23:36:29,234 DEBUG    MQTT       Publishing: emon/emontx3cm15/T3 300
2020-06-30 23:36:29,235 DEBUG    MQTT       Publishing: emon/emontx3cm15/T4 300
2020-06-30 23:36:29,236 DEBUG    MQTT       Publishing: emon/emontx3cm15/pulse 0
2020-06-30 23:36:29,238 DEBUG    MQTT       Publishing: emon/emontx3cm15/error 0
2020-06-30 23:36:29,239 DEBUG    MQTT       Publishing: emon/emontx3cm15/rssi -69
2020-06-30 23:36:29,240 INFO     MQTT       Publishing: emonhub/rx/15/values 82026,240.46,50,0,0,515,0,200722,10232,180622,0,-0.02,-0.02,0.9400000000000001,0,10.870000000000001,300,300,300,0,0,-69
2020-06-30 23:36:38,880 DEBUG    RFM2Pi     10 NEW FRAME : OK 15 62 21 84 85 186 8 221 70 85 85 85 85 80 87 85 85 71 69 86 85 173 114 85 85 197 148 87 85 85 85 85 85 171 170 171 170 11 85 85 85 25 81 101 32 101 32 101 32 85 85 85 85 85 (-69)
2020-06-30 23:36:38,884 DEBUG    RFM2Pi     10 Timestamp : 1593524198.8800588
2020-06-30 23:36:38,884 DEBUG    RFM2Pi     10 From Node : 15
2020-06-30 23:36:38,885 DEBUG    RFM2Pi     10    Values : [82027, 240.47, 50, 0, 0, 517, 0, 200722, 10232, 180624, 0, -0.02, -0.02, 0.9400000000000001, 0, 11, 300, 300, 300, 0, 0]
2020-06-30 23:36:38,885 DEBUG    RFM2Pi     10      RSSI : -69
2020-06-30 23:36:38,886 DEBUG    RFM2Pi     10 Sent to channel(start)' : ToEmonCMS
2020-06-30 23:36:38,886 DEBUG    RFM2Pi     10 Sent to channel(end)' : ToEmonCMS
2020-06-30 23:36:38,966 DEBUG    MQTT       Publishing: emon/emontx3cm15/MSG 82027
2020-06-30 23:36:38,968 DEBUG    MQTT       Publishing: emon/emontx3cm15/Vrms 240.47
2020-06-30 23:36:38,969 DEBUG    MQTT       Publishing: emon/emontx3cm15/F 50
2020-06-30 23:36:38,970 DEBUG    MQTT       Publishing: emon/emontx3cm15/P1 0
2020-06-30 23:36:38,972 DEBUG    MQTT       Publishing: emon/emontx3cm15/P2 0
2020-06-30 23:36:38,973 DEBUG    MQTT       Publishing: emon/emontx3cm15/P3 517
2020-06-30 23:36:38,974 DEBUG    MQTT       Publishing: emon/emontx3cm15/P4 0
2020-06-30 23:36:38,975 DEBUG    MQTT       Publishing: emon/emontx3cm15/E1 200722
2020-06-30 23:36:38,976 DEBUG    MQTT       Publishing: emon/emontx3cm15/E2 10232
2020-06-30 23:36:38,978 DEBUG    MQTT       Publishing: emon/emontx3cm15/E3 180624
2020-06-30 23:36:38,979 DEBUG    MQTT       Publishing: emon/emontx3cm15/E4 0
2020-06-30 23:36:38,980 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf1 -0.02
2020-06-30 23:36:38,982 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf2 -0.02
2020-06-30 23:36:38,983 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf3 0.9400000000000001
2020-06-30 23:36:38,984 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf4 0
2020-06-30 23:36:38,985 DEBUG    MQTT       Publishing: emon/emontx3cm15/T1 11
2020-06-30 23:36:38,987 DEBUG    MQTT       Publishing: emon/emontx3cm15/T2 300
2020-06-30 23:36:38,988 DEBUG    MQTT       Publishing: emon/emontx3cm15/T3 300
2020-06-30 23:36:38,990 DEBUG    MQTT       Publishing: emon/emontx3cm15/T4 300
2020-06-30 23:36:38,991 DEBUG    MQTT       Publishing: emon/emontx3cm15/pulse 0
2020-06-30 23:36:38,992 DEBUG    MQTT       Publishing: emon/emontx3cm15/error 0
2020-06-30 23:36:38,993 DEBUG    MQTT       Publishing: emon/emontx3cm15/rssi -69
2020-06-30 23:36:38,994 INFO     MQTT       Publishing: emonhub/rx/15/values 82027,240.47,50,0,0,517,0,200722,10232,180624,0,-0.02,-0.02,0.9400000000000001,0,11,300,300,300,0,0,-69
2020-06-30 23:36:40,126 DEBUG    emoncmsorg Buffer size: 3
2020-06-30 23:36:40,127 INFO     emoncmsorg sending: https://emoncms.org/input/bulk.json?apikey=E-M-O-N-C-M-S-A-P-I-K-E-Y&data=[[1593524178.882304,15,82025,240.45000000000002,50,0,0,513,0,200722,10232,180621,0,-0.02,-0.02,0.9400000000000001,0,10.870000000000001,300,300,300,0,0,-69],[1593524188.8760293,15,82026,240.46,50,0,0,515,0,200722,10232,180622,0,-0.02,-0.02,0.9400000000000001,0,10.870000000000001,300,300,300,0,0,-69],[1593524198.8800588,15,82027,240.47,50,0,0,517,0,200722,10232,180624,0,-0.02,-0.02,0.9400000000000001,0,11,300,300,300,0,0,-69]]&sentat=1593524200
2020-06-30 23:36:41,134 DEBUG    emoncmsorg acknowledged receipt with 'ok' from https://emoncms.org
2020-06-30 23:36:48,882 DEBUG    RFM2Pi     11 NEW FRAME : OK 15 57 21 84 85 186 8 221 70 85 85 85 85 87 87 85 85 71 69 86 85 173 114 85 85 196 148 87 85 85 85 85 85 171 170 171 170 11 85 85 85 106 81 101 32 101 32 101 32 85 85 85 85 85 (-69)
2020-06-30 23:36:48,895 DEBUG    RFM2Pi     11 Timestamp : 1593524208.882299
2020-06-30 23:36:48,895 DEBUG    RFM2Pi     11 From Node : 15
2020-06-30 23:36:48,896 DEBUG    RFM2Pi     11    Values : [82028, 240.47, 50, 0, 0, 514, 0, 200722, 10232, 180625, 0, -0.02, -0.02, 0.9400000000000001, 0, 10.870000000000001, 300, 300, 300, 0, 0]
2020-06-30 23:36:48,897 DEBUG    RFM2Pi     11      RSSI : -69
2020-06-30 23:36:48,897 DEBUG    RFM2Pi     11 Sent to channel(start)' : ToEmonCMS
2020-06-30 23:36:48,898 DEBUG    RFM2Pi     11 Sent to channel(end)' : ToEmonCMS
2020-06-30 23:36:49,119 DEBUG    MQTT       Publishing: emon/emontx3cm15/MSG 82028
2020-06-30 23:36:49,121 DEBUG    MQTT       Publishing: emon/emontx3cm15/Vrms 240.47
2020-06-30 23:36:49,121 DEBUG    MQTT       Publishing: emon/emontx3cm15/F 50
2020-06-30 23:36:49,122 DEBUG    MQTT       Publishing: emon/emontx3cm15/P1 0
2020-06-30 23:36:49,122 DEBUG    MQTT       Publishing: emon/emontx3cm15/P2 0
2020-06-30 23:36:49,123 DEBUG    MQTT       Publishing: emon/emontx3cm15/P3 514
2020-06-30 23:36:49,124 DEBUG    MQTT       Publishing: emon/emontx3cm15/P4 0
2020-06-30 23:36:49,124 DEBUG    MQTT       Publishing: emon/emontx3cm15/E1 200722
2020-06-30 23:36:49,125 DEBUG    MQTT       Publishing: emon/emontx3cm15/E2 10232
2020-06-30 23:36:49,125 DEBUG    MQTT       Publishing: emon/emontx3cm15/E3 180625
2020-06-30 23:36:49,126 DEBUG    MQTT       Publishing: emon/emontx3cm15/E4 0
2020-06-30 23:36:49,126 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf1 -0.02
2020-06-30 23:36:49,127 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf2 -0.02
2020-06-30 23:36:49,127 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf3 0.9400000000000001
2020-06-30 23:36:49,128 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf4 0
2020-06-30 23:36:49,128 DEBUG    MQTT       Publishing: emon/emontx3cm15/T1 10.870000000000001
2020-06-30 23:36:49,130 DEBUG    MQTT       Publishing: emon/emontx3cm15/T2 300
2020-06-30 23:36:49,131 DEBUG    MQTT       Publishing: emon/emontx3cm15/T3 300
2020-06-30 23:36:49,131 DEBUG    MQTT       Publishing: emon/emontx3cm15/T4 300
2020-06-30 23:36:49,132 DEBUG    MQTT       Publishing: emon/emontx3cm15/pulse 0
2020-06-30 23:36:49,133 DEBUG    MQTT       Publishing: emon/emontx3cm15/error 0
2020-06-30 23:36:49,133 DEBUG    MQTT       Publishing: emon/emontx3cm15/rssi -69
2020-06-30 23:36:49,134 INFO     MQTT       Publishing: emonhub/rx/15/values 82028,240.47,50,0,0,514,0,200722,10232,180625,0,-0.02,-0.02,0.9400000000000001,0,10.870000000000001,300,300,300,0,0,-69
2020-06-30 23:36:58,874 DEBUG    RFM2Pi     12 NEW FRAME : OK 15 56 21 84 85 186 8 210 70 85 85 85 85 170 84 85 85 71 69 86 85 173 114 85 85 198 148 87 85 85 85 85 85 171 170 171 170 11 85 85 85 106 81 101 32 101 32 101 32 85 85 85 85 85 (-69)
2020-06-30 23:36:58,877 DEBUG    RFM2Pi     12 Timestamp : 1593524218.873719
2020-06-30 23:36:58,878 DEBUG    RFM2Pi     12 From Node : 15
2020-06-30 23:36:58,878 DEBUG    RFM2Pi     12    Values : [82029, 240.47, 49.99, 0, 0, 511, 0, 200722, 10232, 180627, 0, -0.02, -0.02, 0.9400000000000001, 0, 10.870000000000001, 300, 300, 300, 0, 0]
2020-06-30 23:36:58,879 DEBUG    RFM2Pi     12      RSSI : -69
2020-06-30 23:36:58,880 DEBUG    RFM2Pi     12 Sent to channel(start)' : ToEmonCMS
2020-06-30 23:36:58,880 DEBUG    RFM2Pi     12 Sent to channel(end)' : ToEmonCMS
2020-06-30 23:36:59,142 DEBUG    MQTT       Publishing: emon/emontx3cm15/MSG 82029
2020-06-30 23:36:59,143 DEBUG    MQTT       Publishing: emon/emontx3cm15/Vrms 240.47
2020-06-30 23:36:59,145 DEBUG    MQTT       Publishing: emon/emontx3cm15/F 49.99
2020-06-30 23:36:59,146 DEBUG    MQTT       Publishing: emon/emontx3cm15/P1 0
2020-06-30 23:36:59,147 DEBUG    MQTT       Publishing: emon/emontx3cm15/P2 0
2020-06-30 23:36:59,148 DEBUG    MQTT       Publishing: emon/emontx3cm15/P3 511
2020-06-30 23:36:59,149 DEBUG    MQTT       Publishing: emon/emontx3cm15/P4 0
2020-06-30 23:36:59,151 DEBUG    MQTT       Publishing: emon/emontx3cm15/E1 200722
2020-06-30 23:36:59,152 DEBUG    MQTT       Publishing: emon/emontx3cm15/E2 10232
2020-06-30 23:36:59,153 DEBUG    MQTT       Publishing: emon/emontx3cm15/E3 180627
2020-06-30 23:36:59,154 DEBUG    MQTT       Publishing: emon/emontx3cm15/E4 0
2020-06-30 23:36:59,155 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf1 -0.02
2020-06-30 23:36:59,157 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf2 -0.02
2020-06-30 23:36:59,158 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf3 0.9400000000000001
2020-06-30 23:36:59,159 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf4 0
2020-06-30 23:36:59,163 DEBUG    MQTT       Publishing: emon/emontx3cm15/T1 10.870000000000001
2020-06-30 23:36:59,166 DEBUG    MQTT       Publishing: emon/emontx3cm15/T2 300
2020-06-30 23:36:59,168 DEBUG    MQTT       Publishing: emon/emontx3cm15/T3 300
2020-06-30 23:36:59,170 DEBUG    MQTT       Publishing: emon/emontx3cm15/T4 300
2020-06-30 23:36:59,173 DEBUG    MQTT       Publishing: emon/emontx3cm15/pulse 0
2020-06-30 23:36:59,180 DEBUG    MQTT       Publishing: emon/emontx3cm15/error 0
2020-06-30 23:36:59,182 DEBUG    MQTT       Publishing: emon/emontx3cm15/rssi -69
2020-06-30 23:36:59,183 INFO     MQTT       Publishing: emonhub/rx/15/values 82029,240.47,49.99,0,0,511,0,200722,10232,180627,0,-0.02,-0.02,0.9400000000000001,0,10.870000000000001,300,300,300,0,0,-69
2020-06-30 23:37:08,889 DEBUG    RFM2Pi     13 NEW FRAME : OK 15 59 21 84 85 165 8 221 70 85 85 85 85 85 87 85 85 71 69 86 85 173 114 85 85 193 148 87 85 85 85 85 85 171 170 171 170 11 85 85 85 106 81 101 32 101 32 101 32 85 85 85 85 85 (-69)
2020-06-30 23:37:08,893 DEBUG    RFM2Pi     13 Timestamp : 1593524228.8894403
2020-06-30 23:37:08,894 DEBUG    RFM2Pi     13 From Node : 15
2020-06-30 23:37:08,894 DEBUG    RFM2Pi     13    Values : [82030, 240.48000000000002, 50, 0, 0, 512, 0, 200722, 10232, 180628, 0, -0.02, -0.02, 0.9400000000000001, 0, 10.870000000000001, 300, 300, 300, 0, 0]
2020-06-30 23:37:08,895 DEBUG    RFM2Pi     13      RSSI : -69
2020-06-30 23:37:08,895 DEBUG    RFM2Pi     13 Sent to channel(start)' : ToEmonCMS
2020-06-30 23:37:08,896 DEBUG    RFM2Pi     13 Sent to channel(end)' : ToEmonCMS
2020-06-30 23:37:08,902 DEBUG    MQTT       Publishing: emon/emontx3cm15/MSG 82030
2020-06-30 23:37:08,904 DEBUG    MQTT       Publishing: emon/emontx3cm15/Vrms 240.48000000000002
2020-06-30 23:37:08,906 DEBUG    MQTT       Publishing: emon/emontx3cm15/F 50
2020-06-30 23:37:08,907 DEBUG    MQTT       Publishing: emon/emontx3cm15/P1 0
2020-06-30 23:37:08,910 DEBUG    MQTT       Publishing: emon/emontx3cm15/P2 0
2020-06-30 23:37:08,912 DEBUG    MQTT       Publishing: emon/emontx3cm15/P3 512
2020-06-30 23:37:08,913 DEBUG    MQTT       Publishing: emon/emontx3cm15/P4 0
2020-06-30 23:37:08,915 DEBUG    MQTT       Publishing: emon/emontx3cm15/E1 200722
2020-06-30 23:37:08,917 DEBUG    MQTT       Publishing: emon/emontx3cm15/E2 10232
2020-06-30 23:37:08,918 DEBUG    MQTT       Publishing: emon/emontx3cm15/E3 180628
2020-06-30 23:37:08,920 DEBUG    MQTT       Publishing: emon/emontx3cm15/E4 0
2020-06-30 23:37:08,922 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf1 -0.02
2020-06-30 23:37:08,923 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf2 -0.02
2020-06-30 23:37:08,925 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf3 0.9400000000000001
2020-06-30 23:37:08,926 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf4 0
2020-06-30 23:37:08,928 DEBUG    MQTT       Publishing: emon/emontx3cm15/T1 10.870000000000001
2020-06-30 23:37:08,930 DEBUG    MQTT       Publishing: emon/emontx3cm15/T2 300
2020-06-30 23:37:08,932 DEBUG    MQTT       Publishing: emon/emontx3cm15/T3 300
2020-06-30 23:37:08,933 DEBUG    MQTT       Publishing: emon/emontx3cm15/T4 300
2020-06-30 23:37:08,935 DEBUG    MQTT       Publishing: emon/emontx3cm15/pulse 0
2020-06-30 23:37:08,937 DEBUG    MQTT       Publishing: emon/emontx3cm15/error 0
2020-06-30 23:37:08,938 DEBUG    MQTT       Publishing: emon/emontx3cm15/rssi -69
2020-06-30 23:37:08,940 INFO     MQTT       Publishing: emonhub/rx/15/values 82030,240.48000000000002,50,0,0,512,0,200722,10232,180628,0,-0.02,-0.02,0.9400000000000001,0,10.870000000000001,300,300,300,0,0,-69
2020-06-30 23:37:11,174 DEBUG    emoncmsorg Buffer size: 3
2020-06-30 23:37:11,176 INFO     emoncmsorg sending: https://emoncms.org/input/bulk.json?apikey=E-M-O-N-C-M-S-A-P-I-K-E-Y&data=[[1593524208.882299,15,82028,240.47,50,0,0,514,0,200722,10232,180625,0,-0.02,-0.02,0.9400000000000001,0,10.870000000000001,300,300,300,0,0,-69],[1593524218.873719,15,82029,240.47,49.99,0,0,511,0,200722,10232,180627,0,-0.02,-0.02,0.9400000000000001,0,10.870000000000001,300,300,300,0,0,-69],[1593524228.8894403,15,82030,240.48000000000002,50,0,0,512,0,200722,10232,180628,0,-0.02,-0.02,0.9400000000000001,0,10.870000000000001,300,300,300,0,0,-69]]&sentat=1593524231
2020-06-30 23:37:12,506 DEBUG    emoncmsorg acknowledged receipt with 'ok' from https://emoncms.org
2020-06-30 23:37:18,875 DEBUG    RFM2Pi     14 NEW FRAME : OK 15 58 21 84 85 165 8 210 70 85 85 85 85 168 84 85 85 71 69 86 85 173 114 85 85 195 148 87 85 85 85 85 85 171 170 171 170 11 85 85 85 25 81 101 32 101 32 101 32 85 85 85 85 85 (-68)
2020-06-30 23:37:18,879 DEBUG    RFM2Pi     14 Timestamp : 1593524238.8749921
2020-06-30 23:37:18,880 DEBUG    RFM2Pi     14 From Node : 15
2020-06-30 23:37:18,880 DEBUG    RFM2Pi     14    Values : [82031, 240.48000000000002, 49.99, 0, 0, 509, 0, 200722, 10232, 180630, 0, -0.02, -0.02, 0.9400000000000001, 0, 11, 300, 300, 300, 0, 0]
2020-06-30 23:37:18,881 DEBUG    RFM2Pi     14      RSSI : -68
2020-06-30 23:37:18,881 DEBUG    RFM2Pi     14 Sent to channel(start)' : ToEmonCMS
2020-06-30 23:37:18,882 DEBUG    RFM2Pi     14 Sent to channel(end)' : ToEmonCMS
2020-06-30 23:37:19,137 DEBUG    MQTT       Publishing: emon/emontx3cm15/MSG 82031
2020-06-30 23:37:19,138 DEBUG    MQTT       Publishing: emon/emontx3cm15/Vrms 240.48000000000002
Are you happy to SSH in?
Really need to follow the emonhub log and see if there is an error message when it stops sending. I am anticipating it might be the same as this - UnboundLocalError: local variable 'reply' referenced before assignment
The emonhub log rotates quite often so if you find something copy it quick!
First check the log for an error
grep emoncmsorg /var/log/emonhub/emonhub.log
If you find one, find the right part of the log and post it.
To follow the log, something like
 tail -f /var/log/emonhub/emonhub.log | grep emoncmsorg
I am happy to SSH in.
The entries in the log only went back 30 min or so and there were no errors.
I now have a window now with the emoncmsorg debug and info entries slowly scrolling.
This could take a while … The three previous stoppages were after a day or so of operating properly.
That is always the issue :grin:
I am very new to administering a unix system.
I am using Putty for the SSH session and think I have convinced it to log the session output to a file. I will leave the session open overnight and see what happens.
That’s OK. All of us were noobs at one time. :wink:
GOOD attitude.
+1 for diving in and tackling the job at hand. thumbsup
Posting to emonsmcorg stopped again last night and the log file had already rotated before I could examine it. The tail output terminated at the same time - see below from the SSH session log.
2020-07-01 23:45:32,726 DEBUG    e[01;31me[Kemoncmsorge[me[K Buffer size: 4
2020-07-01 23:45:32,727 INFO     e[01;31me[Kemoncmsorge[me[K sending: https://emoncms.org/input/bulk.json?apikey=E-M-O-N-C-M-S-A-P-I-K-E-Y&data=[[1593611102.2690256,15,90717,240.69,49.99,0,0,211,0,222299,10229,203273,0,-0.02,-0.02,0.51,0,11.25,300,300,300,0,0,-70],[1593611112.2609804,15,90718,240.70000000000002,50,0,0,211,0,222299,10229,203274,0,-0.02,-0.02,0.51,0,11.25,300,300,300,0,0,-70],[1593611122.2516007,15,90719,240.70000000000002,50,0,0,211,0,222299,10229,203274,0,-0.02,-0.02,0.51,0,11.370000000000001,300,300,300,0,0,-69],[1593611132.2605166,15,90720,240.70000000000002,49.99,0,0,211,0,222299,10229,203275,0,-0.02,-0.02,0.51,0,11.25,300,300,300,0,0,-71]]&sentat=1593611132
2020-07-01 23:45:34,082 DEBUG    e[01;31me[Kemoncmsorge[me[K acknowledged receipt with 'ok' from https://emoncms.org
2020-07-01 23:46:04,085 DEBUG    e[01;31me[Kemoncmsorge[me[K Buffer size: 3
2020-07-01 23:46:04,086 INFO     e[01;31me[Kemoncmsorge[me[K sending: https://emoncms.org/input/bulk.json?apikey=E-M-O-N-C-M-S-A-P-I-K-E-Y&data=[[1593611142.243777,15,90721,240.70000000000002,50,0,0,211,0,222299,10229,203275,0,-0.02,-0.02,0.51,0,11.25,300,300,300,0,0,-70],[1593611152.240948,15,90722,240.70000000000002,49.99,0,0,211,0,222299,10229,203276,0,-0.02,-0.02,0.51,0,11.25,300,300,300,0,0,-71],[1593611162.2398117,15,90723,240.71,50,0,0,213,0,222299,10229,203276,0,-0.02,-0.02,0.52,0,11.25,300,300,300,0,0,-71]]&sentat=1593611164
tail: /var/log/emonhub/emonhub.log: file truncated
The time of the stoppages has been at a roughly similar time of night - just after I have turned in…
Found what appeared to be a rotated log in /var/log.old/emonhub over the period in question. Extract follows.
2020-07-01 23:45:32,360 INFO     MQTT       Publishing: emonhub/rx/15/values 90720,240.70000000000002,49.99,0,0,211,0,222299,10229,203275,0,-0.02,-0.02,0.51,0,11.25,300,300,300,0,0,-71
2020-07-01 23:45:32,726 DEBUG    emoncmsorg Buffer size: 4
2020-07-01 23:45:32,727 INFO     emoncmsorg sending: https://emoncms.org/input/bulk.json?apikey=E-M-O-N-C-M-S-A-P-I-K-E-Y&data=[[1593611102.2690256,15,90717,240.69,49.99,0,0,211,0,222299,10229,203273,0,-0.02,-0.02,0.51,0,11.25,300,300,300,0,0,-70],[1593611112.2609804,15,90718,240.70000000000002,50,0,0,211,0,222299,10229,203274,0,-0.02,-0.02,0.51,0,11.25,300,300,300,0,0,-70],[1593611122.2516007,15,90719,240.70000000000002,50,0,0,211,0,222299,10229,203274,0,-0.02,-0.02,0.51,0,11.370000000000001,300,300,300,0,0,-69],[1593611132.2605166,15,90720,240.70000000000002,49.99,0,0,211,0,222299,10229,203275,0,-0.02,-0.02,0.51,0,11.25,300,300,300,0,0,-71]]&sentat=1593611132
2020-07-01 23:45:34,082 DEBUG    emoncmsorg acknowledged receipt with 'ok' from https://emoncms.org
2020-07-01 23:45:42,244 DEBUG    RFM2Pi     8693 NEW FRAME : OK 15 52 55 84 85 83 11 221 70 85 85 85 85 134 85 85 85 14 49 86 85 160 114 85 85 94 79 86 85 85 85 85 85 171 170 171 170 102 85 85 85 48 81 101 32 101 32 101 32 85 85 85 85 85 (-70)
2020-07-01 23:45:42,248 DEBUG    RFM2Pi     8693 Timestamp : 1593611142.243777
2020-07-01 23:45:42,248 DEBUG    RFM2Pi     8693 From Node : 15
2020-07-01 23:45:42,249 DEBUG    RFM2Pi     8693    Values : [90721, 240.70000000000002, 50, 0, 0, 211, 0, 222299, 10229, 203275, 0, -0.02, -0.02, 0.51, 0, 11.25, 300, 300, 300, 0, 0]
2020-07-01 23:45:42,250 DEBUG    RFM2Pi     8693      RSSI : -70
2020-07-01 23:45:42,251 DEBUG    RFM2Pi     8693 Sent to channel(start)' : ToEmonCMS
2020-07-01 23:45:42,251 DEBUG    RFM2Pi     8693 Sent to channel(end)' : ToEmonCMS
2020-07-01 23:45:42,535 DEBUG    MQTT       Publishing: emon/emontx3cm15/MSG 90721
2020-07-01 23:45:42,537 DEBUG    MQTT       Publishing: emon/emontx3cm15/Vrms 240.70000000000002
2020-07-01 23:45:42,538 DEBUG    MQTT       Publishing: emon/emontx3cm15/F 50
2020-07-01 23:45:42,540 DEBUG    MQTT       Publishing: emon/emontx3cm15/P1 0
2020-07-01 23:45:42,541 DEBUG    MQTT       Publishing: emon/emontx3cm15/P2 0
2020-07-01 23:45:42,543 DEBUG    MQTT       Publishing: emon/emontx3cm15/P3 211
2020-07-01 23:45:42,544 DEBUG    MQTT       Publishing: emon/emontx3cm15/P4 0
2020-07-01 23:45:42,545 DEBUG    MQTT       Publishing: emon/emontx3cm15/E1 222299
2020-07-01 23:45:42,547 DEBUG    MQTT       Publishing: emon/emontx3cm15/E2 10229
2020-07-01 23:45:42,548 DEBUG    MQTT       Publishing: emon/emontx3cm15/E3 203275
2020-07-01 23:45:42,549 DEBUG    MQTT       Publishing: emon/emontx3cm15/E4 0
2020-07-01 23:45:42,551 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf1 -0.02
2020-07-01 23:45:42,552 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf2 -0.02
2020-07-01 23:45:42,555 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf3 0.51
2020-07-01 23:45:42,556 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf4 0
2020-07-01 23:45:42,558 DEBUG    MQTT       Publishing: emon/emontx3cm15/T1 11.25
2020-07-01 23:45:42,559 DEBUG    MQTT       Publishing: emon/emontx3cm15/T2 300
2020-07-01 23:45:42,561 DEBUG    MQTT       Publishing: emon/emontx3cm15/T3 300
2020-07-01 23:45:42,562 DEBUG    MQTT       Publishing: emon/emontx3cm15/T4 300
2020-07-01 23:45:42,563 DEBUG    MQTT       Publishing: emon/emontx3cm15/pulse 0
2020-07-01 23:45:42,564 DEBUG    MQTT       Publishing: emon/emontx3cm15/error 0
2020-07-01 23:45:42,565 DEBUG    MQTT       Publishing: emon/emontx3cm15/rssi -70
2020-07-01 23:45:42,566 INFO     MQTT       Publishing: emonhub/rx/15/values 90721,240.70000000000002,50,0,0,211,0,222299,10229,203275,0,-0.02,-0.02,0.51,0,11.25,300,300,300,0,0,-70
2020-07-01 23:45:52,241 DEBUG    RFM2Pi     8694 NEW FRAME : OK 15 55 55 84 85 83 11 210 70 85 85 85 85 134 85 85 85 14 49 86 85 160 114 85 85 89 79 86 85 85 85 85 85 171 170 171 170 102 85 85 85 48 81 101 32 101 32 101 32 85 85 85 85 85 (-71)
2020-07-01 23:45:52,245 DEBUG    RFM2Pi     8694 Timestamp : 1593611152.240948
2020-07-01 23:45:52,246 DEBUG    RFM2Pi     8694 From Node : 15
2020-07-01 23:45:52,247 DEBUG    RFM2Pi     8694    Values : [90722, 240.70000000000002, 49.99, 0, 0, 211, 0, 222299, 10229, 203276, 0, -0.02, -0.02, 0.51, 0, 11.25, 300, 300, 300, 0, 0]
2020-07-01 23:45:52,247 DEBUG    RFM2Pi     8694      RSSI : -71
2020-07-01 23:45:52,248 DEBUG    RFM2Pi     8694 Sent to channel(start)' : ToEmonCMS
2020-07-01 23:45:52,249 DEBUG    RFM2Pi     8694 Sent to channel(end)' : ToEmonCMS
2020-07-01 23:45:52,352 DEBUG    MQTT       Publishing: emon/emontx3cm15/MSG 90722
2020-07-01 23:45:52,354 DEBUG    MQTT       Publishing: emon/emontx3cm15/Vrms 240.70000000000002
2020-07-01 23:45:52,355 DEBUG    MQTT       Publishing: emon/emontx3cm15/F 49.99
2020-07-01 23:45:52,356 DEBUG    MQTT       Publishing: emon/emontx3cm15/P1 0
2020-07-01 23:45:52,358 DEBUG    MQTT       Publishing: emon/emontx3cm15/P2 0
2020-07-01 23:45:52,359 DEBUG    MQTT       Publishing: emon/emontx3cm15/P3 211
2020-07-01 23:45:52,361 DEBUG    MQTT       Publishing: emon/emontx3cm15/P4 0
2020-07-01 23:45:52,362 DEBUG    MQTT       Publishing: emon/emontx3cm15/E1 222299
2020-07-01 23:45:52,364 DEBUG    MQTT       Publishing: emon/emontx3cm15/E2 10229
2020-07-01 23:45:52,365 DEBUG    MQTT       Publishing: emon/emontx3cm15/E3 203276
2020-07-01 23:45:52,366 DEBUG    MQTT       Publishing: emon/emontx3cm15/E4 0
2020-07-01 23:45:52,368 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf1 -0.02
2020-07-01 23:45:52,369 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf2 -0.02
2020-07-01 23:45:52,371 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf3 0.51
2020-07-01 23:45:52,372 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf4 0
2020-07-01 23:45:52,373 DEBUG    MQTT       Publishing: emon/emontx3cm15/T1 11.25
2020-07-01 23:45:52,375 DEBUG    MQTT       Publishing: emon/emontx3cm15/T2 300
2020-07-01 23:45:52,376 DEBUG    MQTT       Publishing: emon/emontx3cm15/T3 300
2020-07-01 23:45:52,378 DEBUG    MQTT       Publishing: emon/emontx3cm15/T4 300
2020-07-01 23:45:52,379 DEBUG    MQTT       Publishing: emon/emontx3cm15/pulse 0
2020-07-01 23:45:52,380 DEBUG    MQTT       Publishing: emon/emontx3cm15/error 0
2020-07-01 23:45:52,381 DEBUG    MQTT       Publishing: emon/emontx3cm15/rssi -71
2020-07-01 23:45:52,382 INFO     MQTT       Publishing: emonhub/rx/15/values 90722,240.70000000000002,49.99,0,0,211,0,222299,10229,203276,0,-0.02,-0.02,0.51,0,11.25,300,300,300,0,0,-71
2020-07-01 23:46:02,240 DEBUG    RFM2Pi     8695 NEW FRAME : OK 15 54 55 84 85 82 11 221 70 85 85 85 85 128 85 85 85 14 49 86 85 160 114 85 85 89 79 86 85 85 85 85 85 171 170 171 170 97 85 85 85 48 81 101 32 101 32 101 32 85 85 85 85 85 (-71)
2020-07-01 23:46:02,243 DEBUG    RFM2Pi     8695 Timestamp : 1593611162.2398117
2020-07-01 23:46:02,244 DEBUG    RFM2Pi     8695 From Node : 15
2020-07-01 23:46:02,245 DEBUG    RFM2Pi     8695    Values : [90723, 240.71, 50, 0, 0, 213, 0, 222299, 10229, 203276, 0, -0.02, -0.02, 0.52, 0, 11.25, 300, 300, 300, 0, 0]
2020-07-01 23:46:02,245 DEBUG    RFM2Pi     8695      RSSI : -71
2020-07-01 23:46:02,246 DEBUG    RFM2Pi     8695 Sent to channel(start)' : ToEmonCMS
2020-07-01 23:46:02,247 DEBUG    RFM2Pi     8695 Sent to channel(end)' : ToEmonCMS
2020-07-01 23:46:02,377 DEBUG    MQTT       Publishing: emon/emontx3cm15/MSG 90723
2020-07-01 23:46:02,378 DEBUG    MQTT       Publishing: emon/emontx3cm15/Vrms 240.71
2020-07-01 23:46:02,380 DEBUG    MQTT       Publishing: emon/emontx3cm15/F 50
2020-07-01 23:46:02,381 DEBUG    MQTT       Publishing: emon/emontx3cm15/P1 0
2020-07-01 23:46:02,383 DEBUG    MQTT       Publishing: emon/emontx3cm15/P2 0
2020-07-01 23:46:02,384 DEBUG    MQTT       Publishing: emon/emontx3cm15/P3 213
2020-07-01 23:46:02,386 DEBUG    MQTT       Publishing: emon/emontx3cm15/P4 0
2020-07-01 23:46:02,387 DEBUG    MQTT       Publishing: emon/emontx3cm15/E1 222299
2020-07-01 23:46:02,388 DEBUG    MQTT       Publishing: emon/emontx3cm15/E2 10229
2020-07-01 23:46:02,390 DEBUG    MQTT       Publishing: emon/emontx3cm15/E3 203276
2020-07-01 23:46:02,391 DEBUG    MQTT       Publishing: emon/emontx3cm15/E4 0
2020-07-01 23:46:02,393 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf1 -0.02
2020-07-01 23:46:02,394 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf2 -0.02
2020-07-01 23:46:02,395 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf3 0.52
2020-07-01 23:46:02,397 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf4 0
2020-07-01 23:46:02,398 DEBUG    MQTT       Publishing: emon/emontx3cm15/T1 11.25
2020-07-01 23:46:02,399 DEBUG    MQTT       Publishing: emon/emontx3cm15/T2 300
2020-07-01 23:46:02,401 DEBUG    MQTT       Publishing: emon/emontx3cm15/T3 300
2020-07-01 23:46:02,402 DEBUG    MQTT       Publishing: emon/emontx3cm15/T4 300
2020-07-01 23:46:02,403 DEBUG    MQTT       Publishing: emon/emontx3cm15/pulse 0
2020-07-01 23:46:02,405 DEBUG    MQTT       Publishing: emon/emontx3cm15/error 0
2020-07-01 23:46:02,406 DEBUG    MQTT       Publishing: emon/emontx3cm15/rssi -71
2020-07-01 23:46:02,406 INFO     MQTT       Publishing: emonhub/rx/15/values 90723,240.71,50,0,0,213,0,222299,10229,203276,0,-0.02,-0.02,0.52,0,11.25,300,300,300,0,0,-71
2020-07-01 23:46:04,085 DEBUG    emoncmsorg Buffer size: 3
2020-07-01 23:46:04,086 INFO     emoncmsorg sending: https://emoncms.org/input/bulk.json?apikey=E-M-O-N-C-M-S-A-P-I-K-E-Y&data=[[1593611142.243777,15,90721,240.70000000000002,50,0,0,211,0,222299,10229,203275,0,-0.02,-0.02,0.51,0,11.25,300,300,300,0,0,-70],[1593611152.240948,15,90722,240.70000000000002,49.99,0,0,211,0,222299,10229,203276,0,-0.02,-0.02,0.51,0,11.25,300,300,300,0,0,-71],[1593611162.2398117,15,90723,240.71,50,0,0,213,0,222299,10229,203276,0,-0.02,-0.02,0.52,0,11.25,300,300,300,0,0,-71]]&sentat=1593611164
2020-07-01 23:46:12,229 DEBUG    RFM2Pi     8696 NEW FRAME : OK 15 49 55 84 85 82 11 221 70 85 85 85 85 131 85 85 85 14 49 86 85 160 114 85 85 88 79 86 85 85 85 85 85 171 170 171 170 97 85 85 85 48 81 101 32 101 32 101 32 85 85 85 85 85 (-70)
2020-07-01 23:46:12,233 DEBUG    RFM2Pi     8696 Timestamp : 1593611172.2288036
2020-07-01 23:46:12,233 DEBUG    RFM2Pi     8696 From Node : 15
2020-07-01 23:46:12,234 DEBUG    RFM2Pi     8696    Values : [90724, 240.71, 50, 0, 0, 214, 0, 222299, 10229, 203277, 0, -0.02, -0.02, 0.52, 0, 11.25, 300, 300, 300, 0, 0]
2020-07-01 23:46:12,235 DEBUG    RFM2Pi     8696      RSSI : -70
2020-07-01 23:46:12,235 DEBUG    RFM2Pi     8696 Sent to channel(start)' : ToEmonCMS
2020-07-01 23:46:12,236 DEBUG    RFM2Pi     8696 Sent to channel(end)' : ToEmonCMS
2020-07-01 23:46:12,514 DEBUG    MQTT       Publishing: emon/emontx3cm15/MSG 90724
2020-07-01 23:46:12,516 DEBUG    MQTT       Publishing: emon/emontx3cm15/Vrms 240.71
2020-07-01 23:46:12,518 DEBUG    MQTT       Publishing: emon/emontx3cm15/F 50
2020-07-01 23:46:12,519 DEBUG    MQTT       Publishing: emon/emontx3cm15/P1 0
2020-07-01 23:46:12,520 DEBUG    MQTT       Publishing: emon/emontx3cm15/P2 0
2020-07-01 23:46:12,522 DEBUG    MQTT       Publishing: emon/emontx3cm15/P3 214
2020-07-01 23:46:12,523 DEBUG    MQTT       Publishing: emon/emontx3cm15/P4 0
2020-07-01 23:46:12,524 DEBUG    MQTT       Publishing: emon/emontx3cm15/E1 222299
2020-07-01 23:46:12,526 DEBUG    MQTT       Publishing: emon/emontx3cm15/E2 10229
2020-07-01 23:46:12,527 DEBUG    MQTT       Publishing: emon/emontx3cm15/E3 203277
2020-07-01 23:46:12,528 DEBUG    MQTT       Publishing: emon/emontx3cm15/E4 0
2020-07-01 23:46:12,530 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf1 -0.02
2020-07-01 23:46:12,531 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf2 -0.02
2020-07-01 23:46:12,533 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf3 0.52
2020-07-01 23:46:12,534 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf4 0
2020-07-01 23:46:12,535 DEBUG    MQTT       Publishing: emon/emontx3cm15/T1 11.25
2020-07-01 23:46:12,537 DEBUG    MQTT       Publishing: emon/emontx3cm15/T2 300
2020-07-01 23:46:12,538 DEBUG    MQTT       Publishing: emon/emontx3cm15/T3 300
2020-07-01 23:46:12,539 DEBUG    MQTT       Publishing: emon/emontx3cm15/T4 300
2020-07-01 23:46:12,541 DEBUG    MQTT       Publishing: emon/emontx3cm15/pulse 0
2020-07-01 23:46:12,542 DEBUG    MQTT       Publishing: emon/emontx3cm15/error 0
2020-07-01 23:46:12,543 DEBUG    MQTT       Publishing: emon/emontx3cm15/rssi -70
2020-07-01 23:46:12,544 INFO     MQTT       Publishing: emonhub/rx/15/values 90724,240.71,50,0,0,214,0,222299,10229,203277,0,-0.02,-0.02,0.52,0,11.25,300,300,300,0,0,-70
2020-07-01 23:46:22,183 DEBUG    RFM2Pi     8697 NEW FRAME : OK 15 48 55 84 85 82 11 210 70 85 85 85 85 134 85 85 85 14 49 86 85 160 114 85 85 91 79 86 85 85 85 85 85 171 170 171 170 102 85 85 85 48 81 101 32 101 32 101 32 85 85 85 85 85 (-69)
2020-07-01 23:46:22,187 DEBUG    RFM2Pi     8697 Timestamp : 1593611182.1832366
2020-07-01 23:46:22,188 DEBUG    RFM2Pi     8697 From Node : 15
2020-07-01 23:46:22,188 DEBUG    RFM2Pi     8697    Values : [90725, 240.71, 49.99, 0, 0, 211, 0, 222299, 10229, 203278, 0, -0.02, -0.02, 0.51, 0, 11.25, 300, 300, 300, 0, 0]
2020-07-01 23:46:22,189 DEBUG    RFM2Pi     8697      RSSI : -69
2020-07-01 23:46:22,190 DEBUG    RFM2Pi     8697 Sent to channel(start)' : ToEmonCMS
2020-07-01 23:46:22,190 DEBUG    RFM2Pi     8697 Sent to channel(end)' : ToEmonCMS
2020-07-01 23:46:22,278 DEBUG    MQTT       Publishing: emon/emontx3cm15/MSG 90725
2020-07-01 23:46:22,280 DEBUG    MQTT       Publishing: emon/emontx3cm15/Vrms 240.71
2020-07-01 23:46:22,282 DEBUG    MQTT       Publishing: emon/emontx3cm15/F 49.99
2020-07-01 23:46:22,283 DEBUG    MQTT       Publishing: emon/emontx3cm15/P1 0
2020-07-01 23:46:22,284 DEBUG    MQTT       Publishing: emon/emontx3cm15/P2 0
2020-07-01 23:46:22,286 DEBUG    MQTT       Publishing: emon/emontx3cm15/P3 211
2020-07-01 23:46:22,287 DEBUG    MQTT       Publishing: emon/emontx3cm15/P4 0
2020-07-01 23:46:22,289 DEBUG    MQTT       Publishing: emon/emontx3cm15/E1 222299
2020-07-01 23:46:22,290 DEBUG    MQTT       Publishing: emon/emontx3cm15/E2 10229
2020-07-01 23:46:22,292 DEBUG    MQTT       Publishing: emon/emontx3cm15/E3 203278
2020-07-01 23:46:22,293 DEBUG    MQTT       Publishing: emon/emontx3cm15/E4 0
2020-07-01 23:46:22,295 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf1 -0.02
2020-07-01 23:46:22,296 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf2 -0.02
2020-07-01 23:46:22,298 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf3 0.51
2020-07-01 23:46:22,299 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf4 0
2020-07-01 23:46:22,300 DEBUG    MQTT       Publishing: emon/emontx3cm15/T1 11.25
2020-07-01 23:46:22,302 DEBUG    MQTT       Publishing: emon/emontx3cm15/T2 300
2020-07-01 23:46:22,303 DEBUG    MQTT       Publishing: emon/emontx3cm15/T3 300
2020-07-01 23:46:22,305 DEBUG    MQTT       Publishing: emon/emontx3cm15/T4 300
2020-07-01 23:46:22,306 DEBUG    MQTT       Publishing: emon/emontx3cm15/pulse 0
2020-07-01 23:46:22,307 DEBUG    MQTT       Publishing: emon/emontx3cm15/error 0
2020-07-01 23:46:22,309 DEBUG    MQTT       Publishing: emon/emontx3cm15/rssi -69
2020-07-01 23:46:22,310 INFO     MQTT       Publishing: emonhub/rx/15/values 90725,240.71,49.99,0,0,211,0,222299,10229,203278,0,-0.02,-0.02,0.51,0,11.25,300,300,300,0,0,-69
2020-07-01 23:46:32,222 DEBUG    RFM2Pi     8698 NEW FRAME : OK 15 51 55 84 85 82 11 221 70 85 85 85 85 134 85 85 85 14 49 86 85 160 114 85 85 91 79 86 85 85 85 85 85 171 170 171 170 102 85 85 85 48 81 101 32 101 32 101 32 85 85 85 85 85 (-69)
2020-07-01 23:46:32,231 DEBUG    RFM2Pi     8698 Timestamp : 1593611192.222322
2020-07-01 23:46:32,232 DEBUG    RFM2Pi     8698 From Node : 15
2020-07-01 23:46:32,232 DEBUG    RFM2Pi     8698    Values : [90726, 240.71, 50, 0, 0, 211, 0, 222299, 10229, 203278, 0, -0.02, -0.02, 0.51, 0, 11.25, 300, 300, 300, 0, 0]
2020-07-01 23:46:32,233 DEBUG    RFM2Pi     8698      RSSI : -69
2020-07-01 23:46:32,234 DEBUG    RFM2Pi     8698 Sent to channel(start)' : ToEmonCMS
2020-07-01 23:46:32,234 DEBUG    RFM2Pi     8698 Sent to channel(end)' : ToEmonCMS
2020-07-01 23:46:32,508 DEBUG    MQTT       Publishing: emon/emontx3cm15/MSG 90726
2020-07-01 23:46:32,510 DEBUG    MQTT       Publishing: emon/emontx3cm15/Vrms 240.71
2020-07-01 23:46:32,511 DEBUG    MQTT       Publishing: emon/emontx3cm15/F 50
2020-07-01 23:46:32,513 DEBUG    MQTT       Publishing: emon/emontx3cm15/P1 0
2020-07-01 23:46:32,514 DEBUG    MQTT       Publishing: emon/emontx3cm15/P2 0
2020-07-01 23:46:32,515 DEBUG    MQTT       Publishing: emon/emontx3cm15/P3 211
2020-07-01 23:46:32,517 DEBUG    MQTT       Publishing: emon/emontx3cm15/P4 0
2020-07-01 23:46:32,518 DEBUG    MQTT       Publishing: emon/emontx3cm15/E1 222299
2020-07-01 23:46:32,519 DEBUG    MQTT       Publishing: emon/emontx3cm15/E2 10229
2020-07-01 23:46:32,521 DEBUG    MQTT       Publishing: emon/emontx3cm15/E3 203278
2020-07-01 23:46:32,522 DEBUG    MQTT       Publishing: emon/emontx3cm15/E4 0
2020-07-01 23:46:32,524 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf1 -0.02
2020-07-01 23:46:32,525 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf2 -0.02
2020-07-01 23:46:32,526 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf3 0.51
2020-07-01 23:46:32,528 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf4 0
2020-07-01 23:46:32,529 DEBUG    MQTT       Publishing: emon/emontx3cm15/T1 11.25
2020-07-01 23:46:32,531 DEBUG    MQTT       Publishing: emon/emontx3cm15/T2 300
2020-07-01 23:46:32,532 DEBUG    MQTT       Publishing: emon/emontx3cm15/T3 300
2020-07-01 23:46:32,533 DEBUG    MQTT       Publishing: emon/emontx3cm15/T4 300
2020-07-01 23:46:32,535 DEBUG    MQTT       Publishing: emon/emontx3cm15/pulse 0
2020-07-01 23:46:32,536 DEBUG    MQTT       Publishing: emon/emontx3cm15/error 0
2020-07-01 23:46:32,537 DEBUG    MQTT       Publishing: emon/emontx3cm15/rssi -69
2020-07-01 23:46:32,538 INFO     MQTT       Publishing: emonhub/rx/15/values 90726,240.71,50,0,0,211,0,222299,10229,203278,0,-0.02,-0.02,0.51,0,11.25,300,300,300,0,0,-69
2020-07-01 23:46:42,228 DEBUG    RFM2Pi     8699 NEW FRAME : OK 15 50 55 84 85 82 11 221 70 85 85 85 85 134 85 85 85 14 49 86 85 160 114 85 85 90 79 86 85 85 85 85 85 171 170 171 170 102 85 85 85 48 81 101 32 101 32 101 32 85 85 85 85 85 (-70)
2020-07-01 23:46:42,232 DEBUG    RFM2Pi     8699 Timestamp : 1593611202.2277093
2020-07-01 23:46:42,232 DEBUG    RFM2Pi     8699 From Node : 15
2020-07-01 23:46:42,233 DEBUG    RFM2Pi     8699    Values : [90727, 240.71, 50, 0, 0, 211, 0, 222299, 10229, 203279, 0, -0.02, -0.02, 0.51, 0, 11.25, 300, 300, 300, 0, 0]
2020-07-01 23:46:42,234 DEBUG    RFM2Pi     8699      RSSI : -70
2020-07-01 23:46:42,234 DEBUG    RFM2Pi     8699 Sent to channel(start)' : ToEmonCMS
2020-07-01 23:46:42,235 DEBUG    RFM2Pi     8699 Sent to channel(end)' : ToEmonCMS
2020-07-01 23:46:42,414 DEBUG    MQTT       Publishing: emon/emontx3cm15/MSG 90727
2020-07-01 23:46:42,415 DEBUG    MQTT       Publishing: emon/emontx3cm15/Vrms 240.71
2020-07-01 23:46:42,417 DEBUG    MQTT       Publishing: emon/emontx3cm15/F 50
2020-07-01 23:46:42,418 DEBUG    MQTT       Publishing: emon/emontx3cm15/P1 0
2020-07-01 23:46:42,420 DEBUG    MQTT       Publishing: emon/emontx3cm15/P2 0
2020-07-01 23:46:42,421 DEBUG    MQTT       Publishing: emon/emontx3cm15/P3 211
2020-07-01 23:46:42,423 DEBUG    MQTT       Publishing: emon/emontx3cm15/P4 0
2020-07-01 23:46:42,424 DEBUG    MQTT       Publishing: emon/emontx3cm15/E1 222299
2020-07-01 23:46:42,425 DEBUG    MQTT       Publishing: emon/emontx3cm15/E2 10229
2020-07-01 23:46:42,427 DEBUG    MQTT       Publishing: emon/emontx3cm15/E3 203279
2020-07-01 23:46:42,428 DEBUG    MQTT       Publishing: emon/emontx3cm15/E4 0
2020-07-01 23:46:42,430 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf1 -0.02
2020-07-01 23:46:42,431 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf2 -0.02
2020-07-01 23:46:42,433 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf3 0.51
2020-07-01 23:46:42,434 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf4 0
2020-07-01 23:46:42,436 DEBUG    MQTT       Publishing: emon/emontx3cm15/T1 11.25
2020-07-01 23:46:42,437 DEBUG    MQTT       Publishing: emon/emontx3cm15/T2 300
2020-07-01 23:46:42,439 DEBUG    MQTT       Publishing: emon/emontx3cm15/T3 300
2020-07-01 23:46:42,440 DEBUG    MQTT       Publishing: emon/emontx3cm15/T4 300
2020-07-01 23:46:42,442 DEBUG    MQTT       Publishing: emon/emontx3cm15/pulse 0
2020-07-01 23:46:42,443 DEBUG    MQTT       Publishing: emon/emontx3cm15/error 0
2020-07-01 23:46:42,444 DEBUG    MQTT       Publishing: emon/emontx3cm15/rssi -70
2020-07-01 23:46:42,445 INFO     MQTT       Publishing: emonhub/rx/15/values 90727,240.71,50,0,0,211,0,222299,10229,203279,0,-0.02,-0.02,0.51,0,11.25,300,300,300,0,0,-70
2020-07-01 23:46:52,224 DEBUG    RFM2Pi     8700 NEW FRAME : OK 15 61 55 84 85 82 11 210 70 85 85 85 85 134 85 85 85 14 49 86 85 160 114 85 85 90 79 86 85 85 85 85 85 171 170 171 170 102 85 85 85 36 81 101 32 101 32 101 32 85 85 85 85 85 (-69)
2020-07-01 23:46:52,228 DEBUG    RFM2Pi     8700 Timestamp : 1593611212.22406
2020-07-01 23:46:52,229 DEBUG    RFM2Pi     8700 From Node : 15
2020-07-01 23:46:52,230 DEBUG    RFM2Pi     8700    Values : [90728, 240.71, 49.99, 0, 0, 211, 0, 222299, 10229, 203279, 0, -0.02, -0.02, 0.51, 0, 11.370000000000001, 300, 300, 300, 0, 0]
2020-07-01 23:46:52,230 DEBUG    RFM2Pi     8700      RSSI : -69
2020-07-01 23:46:52,231 DEBUG    RFM2Pi     8700 Sent to channel(start)' : ToEmonCMS
2020-07-01 23:46:52,231 DEBUG    RFM2Pi     8700 Sent to channel(end)' : ToEmonCMS
2020-07-01 23:46:52,378 DEBUG    MQTT       Publishing: emon/emontx3cm15/MSG 90728
2020-07-01 23:46:52,380 DEBUG    MQTT       Publishing: emon/emontx3cm15/Vrms 240.71
2020-07-01 23:46:52,382 DEBUG    MQTT       Publishing: emon/emontx3cm15/F 49.99
2020-07-01 23:46:52,384 DEBUG    MQTT       Publishing: emon/emontx3cm15/P1 0
2020-07-01 23:46:52,385 DEBUG    MQTT       Publishing: emon/emontx3cm15/P2 0
2020-07-01 23:46:52,387 DEBUG    MQTT       Publishing: emon/emontx3cm15/P3 211
2020-07-01 23:46:52,388 DEBUG    MQTT       Publishing: emon/emontx3cm15/P4 0
2020-07-01 23:46:52,390 DEBUG    MQTT       Publishing: emon/emontx3cm15/E1 222299
2020-07-01 23:46:52,391 DEBUG    MQTT       Publishing: emon/emontx3cm15/E2 10229
2020-07-01 23:46:52,393 DEBUG    MQTT       Publishing: emon/emontx3cm15/E3 203279
2020-07-01 23:46:52,394 DEBUG    MQTT       Publishing: emon/emontx3cm15/E4 0
2020-07-01 23:46:52,396 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf1 -0.02
2020-07-01 23:46:52,398 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf2 -0.02
2020-07-01 23:46:52,399 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf3 0.51
2020-07-01 23:46:52,401 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf4 0
2020-07-01 23:46:52,402 DEBUG    MQTT       Publishing: emon/emontx3cm15/T1 11.370000000000001
2020-07-01 23:46:52,404 DEBUG    MQTT       Publishing: emon/emontx3cm15/T2 300
2020-07-01 23:46:52,405 DEBUG    MQTT       Publishing: emon/emontx3cm15/T3 300
2020-07-01 23:46:52,407 DEBUG    MQTT       Publishing: emon/emontx3cm15/T4 300
2020-07-01 23:46:52,408 DEBUG    MQTT       Publishing: emon/emontx3cm15/pulse 0
2020-07-01 23:46:52,410 DEBUG    MQTT       Publishing: emon/emontx3cm15/error 0
2020-07-01 23:46:52,411 DEBUG    MQTT       Publishing: emon/emontx3cm15/rssi -69
2020-07-01 23:46:52,412 INFO     MQTT       Publishing: emonhub/rx/15/values 90728,240.71,49.99,0,0,211,0,222299,10229,203279,0,-0.02,-0.02,0.51,0,11.370000000000001,300,300,300,0,0,-69
2020-07-01 23:47:02,222 DEBUG    RFM2Pi     8701 NEW FRAME : OK 15 60 55 84 85 82 11 221 70 85 85 85 85 134 85 85 85 14 49 86 85 160 114 85 85 69 79 86 85 85 85 85 85 171 170 171 170 102 85 85 85 36 81 101 32 101 32 101 32 85 85 85 85 85 (-70)
2020-07-01 23:47:02,226 DEBUG    RFM2Pi     8701 Timestamp : 1593611222.2223597
2020-07-01 23:47:02,227 DEBUG    RFM2Pi     8701 From Node : 15
2020-07-01 23:47:02,228 DEBUG    RFM2Pi     8701    Values : [90729, 240.71, 50, 0, 0, 211, 0, 222299, 10229, 203280, 0, -0.02, -0.02, 0.51, 0, 11.370000000000001, 300, 300, 300, 0, 0]
2020-07-01 23:47:02,228 DEBUG    RFM2Pi     8701      RSSI : -70
2020-07-01 23:47:02,229 DEBUG    RFM2Pi     8701 Sent to channel(start)' : ToEmonCMS
2020-07-01 23:47:02,230 DEBUG    RFM2Pi     8701 Sent to channel(end)' : ToEmonCMS
2020-07-01 23:47:02,320 DEBUG    MQTT       Publishing: emon/emontx3cm15/MSG 90729
2020-07-01 23:47:02,322 DEBUG    MQTT       Publishing: emon/emontx3cm15/Vrms 240.71
2020-07-01 23:47:02,324 DEBUG    MQTT       Publishing: emon/emontx3cm15/F 50
2020-07-01 23:47:02,326 DEBUG    MQTT       Publishing: emon/emontx3cm15/P1 0
2020-07-01 23:47:02,327 DEBUG    MQTT       Publishing: emon/emontx3cm15/P2 0
2020-07-01 23:47:02,329 DEBUG    MQTT       Publishing: emon/emontx3cm15/P3 211
2020-07-01 23:47:02,331 DEBUG    MQTT       Publishing: emon/emontx3cm15/P4 0
2020-07-01 23:47:02,333 DEBUG    MQTT       Publishing: emon/emontx3cm15/E1 222299
2020-07-01 23:47:02,335 DEBUG    MQTT       Publishing: emon/emontx3cm15/E2 10229
2020-07-01 23:47:02,336 DEBUG    MQTT       Publishing: emon/emontx3cm15/E3 203280
2020-07-01 23:47:02,338 DEBUG    MQTT       Publishing: emon/emontx3cm15/E4 0
2020-07-01 23:47:02,340 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf1 -0.02
2020-07-01 23:47:02,342 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf2 -0.02
2020-07-01 23:47:02,343 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf3 0.51
2020-07-01 23:47:02,345 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf4 0
2020-07-01 23:47:02,347 DEBUG    MQTT       Publishing: emon/emontx3cm15/T1 11.370000000000001
2020-07-01 23:47:02,348 DEBUG    MQTT       Publishing: emon/emontx3cm15/T2 300
2020-07-01 23:47:02,350 DEBUG    MQTT       Publishing: emon/emontx3cm15/T3 300
2020-07-01 23:47:02,352 DEBUG    MQTT       Publishing: emon/emontx3cm15/T4 300
2020-07-01 23:47:02,354 DEBUG    MQTT       Publishing: emon/emontx3cm15/pulse 0
2020-07-01 23:47:02,356 DEBUG    MQTT       Publishing: emon/emontx3cm15/error 0
2020-07-01 23:47:02,357 DEBUG    MQTT       Publishing: emon/emontx3cm15/rssi -70
2020-07-01 23:47:02,358 INFO     MQTT       Publishing: emonhub/rx/15/values 90729,240.71,50,0,0,211,0,222299,10229,203280,0,-0.02,-0.02,0.51,0,11.370000000000001,300,300,300,0,0,-70
2020-07-01 23:47:12,221 DEBUG    RFM2Pi     8702 NEW FRAME : OK 15 63 55 84 85 82 11 210 70 85 85 85 85 134 85 85 85 14 49 86 85 160 114 85 85 68 79 86 85 85 85 85 85 171 170 171 170 102 85 85 85 48 81 101 32 101 32 101 32 85 85 85 85 85 (-69)
2020-07-01 23:47:12,225 DEBUG    RFM2Pi     8702 Timestamp : 1593611232.2211173
2020-07-01 23:47:12,226 DEBUG    RFM2Pi     8702 From Node : 15
2020-07-01 23:47:12,226 DEBUG    RFM2Pi     8702    Values : [90730, 240.71, 49.99, 0, 0, 211, 0, 222299, 10229, 203281, 0, -0.02, -0.02, 0.51, 0, 11.25, 300, 300, 300, 0, 0]
2020-07-01 23:47:12,227 DEBUG    RFM2Pi     8702      RSSI : -69
2020-07-01 23:47:12,228 DEBUG    RFM2Pi     8702 Sent to channel(start)' : ToEmonCMS
2020-07-01 23:47:12,228 DEBUG    RFM2Pi     8702 Sent to channel(end)' : ToEmonCMS
2020-07-01 23:47:12,454 DEBUG    MQTT       Publishing: emon/emontx3cm15/MSG 90730
2020-07-01 23:47:12,456 DEBUG    MQTT       Publishing: emon/emontx3cm15/Vrms 240.71
2020-07-01 23:47:12,457 DEBUG    MQTT       Publishing: emon/emontx3cm15/F 49.99
2020-07-01 23:47:12,459 DEBUG    MQTT       Publishing: emon/emontx3cm15/P1 0
2020-07-01 23:47:12,461 DEBUG    MQTT       Publishing: emon/emontx3cm15/P2 0
2020-07-01 23:47:12,462 DEBUG    MQTT       Publishing: emon/emontx3cm15/P3 211
2020-07-01 23:47:12,464 DEBUG    MQTT       Publishing: emon/emontx3cm15/P4 0
2020-07-01 23:47:12,465 DEBUG    MQTT       Publishing: emon/emontx3cm15/E1 222299
2020-07-01 23:47:12,467 DEBUG    MQTT       Publishing: emon/emontx3cm15/E2 10229
2020-07-01 23:47:12,469 DEBUG    MQTT       Publishing: emon/emontx3cm15/E3 203281
2020-07-01 23:47:12,470 DEBUG    MQTT       Publishing: emon/emontx3cm15/E4 0
2020-07-01 23:47:12,472 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf1 -0.02
2020-07-01 23:47:12,473 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf2 -0.02
2020-07-01 23:47:12,475 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf3 0.51
2020-07-01 23:47:12,477 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf4 0
2020-07-01 23:47:12,478 DEBUG    MQTT       Publishing: emon/emontx3cm15/T1 11.25
2020-07-01 23:47:12,480 DEBUG    MQTT       Publishing: emon/emontx3cm15/T2 300
2020-07-01 23:47:12,482 DEBUG    MQTT       Publishing: emon/emontx3cm15/T3 300
2020-07-01 23:47:12,484 DEBUG    MQTT       Publishing: emon/emontx3cm15/T4 300
2020-07-01 23:47:12,485 DEBUG    MQTT       Publishing: emon/emontx3cm15/pulse 0
2020-07-01 23:47:12,487 DEBUG    MQTT       Publishing: emon/emontx3cm15/error 0
2020-07-01 23:47:12,488 DEBUG    MQTT       Publishing: emon/emontx3cm15/rssi -69
2020-07-01 23:47:12,489 INFO     MQTT       Publishing: emonhub/rx/15/values 90730,240.71,49.99,0,0,211,0,222299,10229,203281,0,-0.02,-0.02,0.51,0,11.25,300,300,300,0,0,-69
2020-07-01 23:47:22,209 DEBUG    RFM2Pi     8703 NEW FRAME : OK 15 62 55 84 85 82 11 221 70 85 85 85 85 134 85 85 85 14 49 86 85 160 114 85 85 68 79 86 85 85 85 85 85 171 170 171 170 102 85 85 85 48 81 101 32 101 32 101 32 85 85 85 85 85 (-70)
2020-07-01 23:47:22,213 DEBUG    RFM2Pi     8703 Timestamp : 1593611242.2095156
2020-07-01 23:47:22,214 DEBUG    RFM2Pi     8703 From Node : 15
2020-07-01 23:47:22,215 DEBUG    RFM2Pi     8703    Values : [90731, 240.71, 50, 0, 0, 211, 0, 222299, 10229, 203281, 0, -0.02, -0.02, 0.51, 0, 11.25, 300, 300, 300, 0, 0]
2020-07-01 23:47:22,216 DEBUG    RFM2Pi     8703      RSSI : -70
2020-07-01 23:47:22,216 DEBUG    RFM2Pi     8703 Sent to channel(start)' : ToEmonCMS
2020-07-01 23:47:22,217 DEBUG    RFM2Pi     8703 Sent to channel(end)' : ToEmonCMS
2020-07-01 23:47:22,473 DEBUG    MQTT       Publishing: emon/emontx3cm15/MSG 90731
2020-07-01 23:47:22,474 DEBUG    MQTT       Publishing: emon/emontx3cm15/Vrms 240.71
2020-07-01 23:47:22,476 DEBUG    MQTT       Publishing: emon/emontx3cm15/F 50
2020-07-01 23:47:22,478 DEBUG    MQTT       Publishing: emon/emontx3cm15/P1 0
2020-07-01 23:47:22,479 DEBUG    MQTT       Publishing: emon/emontx3cm15/P2 0
2020-07-01 23:47:22,481 DEBUG    MQTT       Publishing: emon/emontx3cm15/P3 211
2020-07-01 23:47:22,482 DEBUG    MQTT       Publishing: emon/emontx3cm15/P4 0
2020-07-01 23:47:22,484 DEBUG    MQTT       Publishing: emon/emontx3cm15/E1 222299
2020-07-01 23:47:22,485 DEBUG    MQTT       Publishing: emon/emontx3cm15/E2 10229
2020-07-01 23:47:22,487 DEBUG    MQTT       Publishing: emon/emontx3cm15/E3 203281
2020-07-01 23:47:22,488 DEBUG    MQTT       Publishing: emon/emontx3cm15/E4 0
2020-07-01 23:47:22,490 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf1 -0.02
2020-07-01 23:47:22,492 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf2 -0.02
2020-07-01 23:47:22,493 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf3 0.51
2020-07-01 23:47:22,495 DEBUG    MQTT       Publishing: emon/emontx3cm15/pf4 0
2020-07-01 23:47:22,497 DEBUG    MQTT       Publishing: emon/emontx3cm15/T1 11.25
2020-07-01 23:47:22,498 DEBUG    MQTT       Publishing: emon/emontx3cm15/T2 300
2020-07-01 23:47:22,500 DEBUG    MQTT       Publishing: emon/emontx3cm15/T3 300
2020-07-01 23:47:22,501 DEBUG    MQTT       Publishing: emon/emontx3cm15/T4 300
2020-07-01 23:47:22,503 DEBUG    MQTT       Publishing: emon/emontx3cm15/pulse 0
2020-07-01 23:47:22,504 DEBUG    MQTT       Publishing: emon/emontx3cm15/error 0
2020-07-01 23:47:22,505 DEBUG    MQTT       Publishing: emon/emontx3cm15/rssi -70
The last send to emoncmsorg is at 23:46:04 and there is no acknowledge record.
Have a look in syslog for the same period (possibly gone by now) as exceptions sometimes propagate to there rather than the emonhub log.
I found the syslog for the same period. Nothing of interest in there unfortunately.
Watch the timezone, syslog may be UTC and emonhub might be BST. Check by following both (got caught out earlier by this).