What the Design Got Right, and What It Didn’t

Previously:

The design works.

After a full heating season, the system delivered a seasonal COP of 4.21, used 68% less energy than the LPG boiler it replaced, ran at 46% lower cost, and held the house at setpoint through every observed outdoor condition. The 12 kW Vaillant aroTHERM Plus, sized on paper at 11.94 kW, met its design demand on the coldest day of the year. Indoor temperature stayed comfortably above 19°C throughout. By every measurable functional standard, the design is doing what it was designed to do.

That part of the story is closed.

But the design isn’t perfect. A year of operation has shown me where the gap is. And the gap is worth talking about — not as a confession, but as the next iteration.

What experience would have caught at design time. There is a real difference between an experienced professional and a first time amateur, and it is not a question of effort or care.

An experienced professional designs many systems. An amateur designs one. The professional brings calibration the amateur can’t yet have — a sense for which conservatisms cost something and which ones don’t. The first iteration of an amateur’s design is, almost by definition, more conservative than a professional’s would have been, because the amateur doesn’t yet know where conservatism is free and where it has a price tag.

In my case, the conservatism or the amateurism that had a price tag was the design flow temperature.

The system was sized for 50°C flow at the −2.7°C design point. That number was set by the existing radiators — most of which are K2 panels, kept in place because replacing every radiator in the house was off the table at design time. The original installers, the ones who wanted to quote a 37 kW heat pump, had also wanted to replace many radiators in the house. Rip out the lot, fit triples, start again. I had pushed back on that by instinct not knowledge — the radiators were fine, I said, the system would work with what was there — and broadly I was right. The radiators do work for the designed flow temperature. The house is warm.

But broadly right is a specific kind of trap. It’s the trap of being correct on the headline question and wrong on the subtler one underneath it. The headline question was do the radiators need replacing? The answer was no. The subtler question was do all of them carry their share at the same flow temperature? And the answer to that one was no, but I didn’t know to ask it.

A professional would have known that 50°C design flow was higher than it needed to be, and that leaving the radiators alone wasn’t a free choice. it would cost efficiency in the regime that carries most of the season’s energy — getting the system to a lower flow temperature on day one.

I didn’t. Not for lack of attention. The subtlety wasn’t in my vocabulary at the time.

What the data showed. A year of operation made the gap visible.

Across December, January and February, the system ran at an average outdoor temperature of 4.9°C, an average flow temperature of 39.3°C, and a heating sCOP of 4.03. That’s the meat of the heating season. That’s where the kWh actually go.

On the coldest day, the outdoor temperature dropped to −1.6°C through the daytime hours and the flow temperature peaked at 44°C. Indoor temperature held at 19.5°C. Then, briefly, in the small hours of that morning, the outdoor temperature reached −2.7°C — the design point itself, the temperature for which the whole system had been sized. The flow rose to 46°C. Indoor sat at 19.8°C.

Six degrees below the 50°C design ceiling. Even at the worst moment of the worst day of the year. The radiators were not, in fact, working at their thermal limit.

That headroom is where the inefficiency sits.

Not on the cold days — those are rare. The inefficiency sits in the long shoulder weeks of December to February, the stretches at outdoor temperatures between 0°C and 8°C, where the heat curve is forced higher than it needs to be because the design ceiling was set high. January is the highest-energy month and the most expensive. It is also the month in which the gap between operational reality and design ceiling does the most damage.

What the change is. The fix is small.

Two large K2 radiators in the main living space are going up to a K3 format. The rest stays. Every radiator upstairs stays. They have margin already at the current flow regime; replacing them would buy nothing.

The target is to reduce the design flow temperature from 50°C to roughly 40°C at the −2.7°C outdoor design point. The radiator change is the lever. The heat curve will then re-tune itself, both in the coarse layer and the fine trim, around the new operating envelope.

This is not a system overhaul. It is two radiators in two rooms, picked because the data identified them.

What it will buy us, in numbers. I don’t know.

That is the honest answer, and it is the answer this chapter is built around.

A professional, designing from experience, would commit to a predicted gain. An amateur with monitoring will measure. The exact figure is the kind of thing a heating season of post-change data will settle better than any prediction.

What I can say is the shape of it. The lever is flow temperature. The regime where the lever matters most is the 0–8°C outdoor band. That regime carries the bulk of January’s energy. Lowering flow temperature in that band lifts COP. The COP improvement, applied across the kWh that actually flow through the band, produces a reduction in electricity used and money spent.

The shape of the gain is clear. The magnitude is what the data will tell us.

I would rather not predict a number that turns out to be wrong. I would rather measure a number that turns out to be right.

The position. The design met the requirements. It didn’t meet them perfectly.

A professional, with experience, would have caught at the start what a year of data caught at the end. The amateur route is slower. It is also, given good monitoring, more precise — because the second iteration is informed by observation that the professional would have had to estimate.

Two radiators are going to change. The flow temperature ceiling will come down. The COP will improve in the regime where most of the season’s energy is consumed. The data will settle the question of by how much.

The design works. The design has room to be better. The data shows where. The discipline is patience.

Maybe it’s just me, but these AI generated, or at least AI-augmented, posts leave a sour taste…

Maybe a language problem? He claims to be in Scotland, but has a French email address.

Im sure @abidamr means well but I also get that feeling @ectoplasmosis. What would help here @abidamr if you plan on more of these posts and if you are using AI? is that you use it to summarize what you want to say in as compact a form as you can.

As I read it, your core point is that you were able to run your system at a lower flow temperature on the coldest days than you expected, 46C briefly at -2.7C, 44C during day, 39C at 5C outside vs 50C design temp.

That’s great that you find this and it is consistent with what a lot of us are finding. If I can plug my own work :sweat_smile: you might enjoy What SCOP can you expect from a system that runs at 55C and 50C flow temperatures on the coldest days?

What I don’t think is clear enough from your analysis on this page at least is how you are only targeting the upgrade to 2 radiators. Are the room temperatures higher than expected in the other rooms?

Yes — French expat in Scotland :grinning_face:.

On the AI point, I’m not sure where that’s coming from. After benefiting from the resources of OEM, I thought I’d give back and share my experience, in case it’s helpful to someone in a similar situation, i.e. someone who can’t have an air source heat pump as I was told. Engaging with the substance of the post rather than its style would be more useful to everyone, I think :person_shrugging: .

My logic regarding the radiators is that the upstairs ones are correctly sized — i.e. if I drop the flow temperature, I’ll still achieve the desired room temperatures. The downstairs, being the living space, needs to be 1–1.5 °C warmer than upstairs, and that’s what’s pushing the flow temperature higher to achieve the desired average temperature. This is why I’m targeting two large radiators downstairs to bring the flow temperature back down. I may be wrong though?

If the upstairs radiators are either turned down on their TRV’s and still hitting expected room temps or the room temps are already too hot upstairs then your right that you could run these at a lower flow temp and in turn upgrade the other two radiators so that they increase the downstairs temperatures whilst working at the lower flow temps that match the upstairs requirement.

Apologies, I didn’t mean to offend with my comment regarding AI. I can’t, however, help but feel a chilling effect when reading posts on community forums like this and realising that they’re written or summarised/rephrased by AI.

It creates an uneasy sensation of doubt and uncertainty as to the level of actual human input. Forums like this are havens of genuine discussion, and the fear of this being diluted by AI is real, for me at least.

Apologies again for veering off-topic!

I understand and agree with your concern. Open forums like OEM can sometimes lead to misunderstandings. No hard feelings :grinning_face: .

@abidamr Thanks for your contributions. I have found them to be very thorough, interesting and helpful.