Both your posts and previous confirm that sensors mismatch lead to under or over-reporting.
Since my previous post, an engineer from Vaillant has now replaced both sensors.
Before: Return sensor temp was displaying +0.6 higher than Flow (Pessimistic COP)
Now: Return sensor temp is displaying -0.3 lower than Flow (Optimistic COP)
Therefore a DT increase of +0.9 deg compared to how it was originally.
Before I was seeing a COP of around 2.6 @3.3 deg outdoor. After the sensor replacements and refitting at the same 3.3 deg outdoor temp, the COP reported jumped from around 2.6 to 4.0.
Assuming F&R temps should exactly equalise when the HP is off, pump circulating for a period and water temp stabilised?
Without MID metering, true and accurate COP etc is unknown or unproven but figures now make more sense in my case.
I asked the engineer if Vaillant had any known information about poor sensor calibration or re-fitting and if any rectification procedures, he replied no. He said it’s not something they commonly need to replace and seemed a slight reluctance. It was just by luck that he managed to find sensors in the van (despite a 5 hour return journey and being the second engineer to visit, the previous didnt have sensors in his van). 1 sensor was in a sealed packet with a clamp. The other didn’t seem to come with a clamp, looked like he had to prize off the old clamp to reuse. It’s a pity they don’t come as a calibrated or matched pair.
No resistance tests or heat clamp tests were carried out before or after, so the level of tolerance mismatch under or over is left to chance and of no interest to Vaillant to check. Left to the customer to identify.
No pipe cleaning was carried out and no thermal paste applied. Clamp fit seems not that tight and easy to rotate round the pipe.
I asked if he could cover the damaged and open insulation gaps around the sensors and pipe. Fortunately he had some Armacell tape in the van to do so.
The engineer said the same sensors are used in boilers. These issues may be less apparent with wider DT boilers. However, with narrow DT heat pumps that rely on small DT to modulate and also report sensible yield/ output figures, the mismatches are more of an issue.
A consolation from what i can see, kWh electrical consumption running costs don’t appear to be noticeably affected. Not sure if and how general running and operation may or may not be affected.