Might be one for you @Andre_K …… and others. 
I wrote this new article, helping people understand why their Vaillant doesn’t run at DT5 very often. It’s a question I see a lot, why doesn’t it run at DT5, as they’ve heard that’s what heat pumps should run at.
Anyway, it got me thinking about my own system.
The heating pump on my 5kW is set to auto, so it defaults to 860 L/h
My heat pump spends a lot of the shoulder months at minimum output (2.2kW), so is always around DT2.2 ish when running 860 L/h.
But my heat loss is only around 3.6kW at -3C, so really I don’t need 860 L/h.
It would be more like 618 L/h
618 L/h (0.171 L/s x 4.2 x DT5) = 3.591 kW
So I’ve initially set my heating pump to 60% which gave me 686 L/h
Now I know that the vaillant doesn’t seem to care most of the time, it just gets on with the heating cycle, even at DT2.
But i’m thinking it’s surely better to run at a wider DT where possible?
In this example, DT is around 3, so perhaps better?
I might go and drop the pump a little more to get closer to 618 (the minimum is 50%).
And because it’s rarely -3C outside, I bet 50% could work well too.
I suppose the bigger question……. is this more efficient? running a wider DT at minimum outputs?
anyone done any trials?