Hi everyone,
I know this is a topic that has come up before, and as it turns colder so we begin the fight again.
The problem: When OAT falls below 5C, the Samsung controller runs an anti-freeze protection cycle which runs the pumps circulating warm water for 5 mins to prevent the system from freezing when the pumps have been idle for 60mins.
Normally, for most systems, this would never happen as the system should be running constantly when OATs are below 5C (or at least cycling on/off within a 60min window), but because our ASHP is so oversized for our property, we cannot run constantly until temps drop closer to 0C. This means that overnight the pumps will cycle for 5mins every hour which in our case ‘steals’ hot water from the DHW cylinder, transferring it into the 50L volumiser and 28mm primaries, and we wake up each morning with not so hot water. Note we also have glycol in the system and full home battery backup so it’s extremely unlikely the system will freeze.
I know one other user here managed to trick the diverter valve into switching to the circuit rather than the DHW cylinder, but unfortunately that solution was not viable on our Joule pre-plumbed tank due to the way it’s wired.
So I’m back to scratching my head and thinking about solutions. Last year I resorted to going out in the night and grabbing hold of the temp sensor in my warm hand to temporarily increase the reading to above 5C once per hour, but that’s not sustainable if I want a full night’s sleep!
Today I’ve had the case off and measured the resistance of the thermistor at different temps (with a pint glass of water and ice cubes). The thermistor is reasonably accurate, so swapping it out isn’t really going to help unless I can find an inaccurate sensor. The sensor is a 10k Ohm at 25C type, and typically reads 20K at 7C and 22K at 5C. The full table of resistance/temperature values are in the attached document.
So I’m considering just replacing the sensor with a fixed 20K resistor and let the heat pump think it’s ~7C all year round, but I’m worried what other implications this may have:
- Weather Compensation. Obviously the WC curve is based on OAT and would be rendered unless as the ASHP would see a constant 7C. This isn’t really an issue for us as we run at a flat 32C LWT all year round (as the lowest LWT the system can achieve) and manually bump it up a couple degrees on the controller if the weather gets very cold and the house drops below 20C.
- Defrost cycles? I don’t know about defrost cycles? Does the controller use OAT at all in determining when to run defrost cycles, and would a constant OAT of 7C affect or prevent defrost cycles from running?
- Anti-freeze protection: This is what we are trying to fix - prevent from running.
- Anything else I’ve not considered that uses the OAT sensor value?
I’m hoping those with good technical knowledge of the Samsung unit will be able to help bounce around this idea with me to help find a solution.
Thanks