I wanted to share some thoughts about where I think we are with heat pump system design in the UK as we start 2025.
There is a large performance gap between heat pumps that have been designed, installed and configured well (SPF H4 4.0 HeatpumpMonitor.org) and what most customers are likely to be getting (SPF H4 2.8 Electrification of Heat. The heat pump industry is diverse and while there are some amazing installers out there, the wider industry is struggling to deliver on this same quality and performance.
A significant factor in this difference is that the good installers know when to deviate from industry guidance such as CIBSE default air change rates and U-value assumptions in heat loss calculations. Whilst those who go by the book, inadvertently and arguably at no fault of their own, build in a lot of errors into system design that make higher performance results more difficult to achieve.
Overestimated heat loss = over estimated design temperatures and weather curve settings!
Over-estimated heat loss calculation is at the heart of the problem but this is not primarily about over-sizing the heat pump unit itself as many of us (myself included) have focused on.
Arguably the most important issue with over-estimating heat loss is that it over-estimates the design flow temperature that the system needs to run at.
If a system design is based on an over-estimated heat loss, it can appear that even with upgraded radiators that a 50C flow temperature at design temperature is required.
If this design temperature is then used to set the weather compensation curve, as one would expect, the system will run hotter than it needs to. It will run up to this high temperature, a room thermostat will then likely turn the system off for a period before the cycle repeats again. This looks to be a common issue with systems that were installed as part of the Electrification of Heat trial that achieved an average performance of SPF 2.8.
A simple case of lowering the weather comp curve would allow the heat pump to modulate back, run at lower flow temperatures and deliver better performance. Brands with degree minute algorithms such as Vaillant/Viessmann/Nibe will handle mild weather cycling pretty well even if the unit is over-sized.
In reality with accurate heat loss calculations itās relatively easy to design systems to run at design flow temperature of 35-40C, even with radiators, and it is these design flow temperature and importantly associated configured weather compensation curves that deliver on the high performance results we see on HeatpumpMonitor.org.
This issue of over-estimated heat loss leading to over-estimated design temperatures and weather compensation settings can be solved by either 1. Improving heat loss calculation accuracy or 2. Heat pump manufacturers adopting automatic optimisation of weather comp curves. 3. Customer education on tuning heat pump settings, why low temp is better and how to avoid too much zoning etc. Or perhaps a mix of all threeā¦
Right sizing the heat pump
Right sizing the heat pump is of course an associated factor, but is complicated to a greater degree by variations in how different makes and models of heat pump handle mild weather modulation and cycling and what their real world maximum capacity outputs are during defrost conditions. It seems that a 30-40% over-sizing factor on an accurate heat loss gives good results, but adding an extra factor on top of an over-sized heat loss is less than ideal.
Does the above seem like a reasonable summary of where we are? Any thoughts welcome!
Simple Heat Loss tool:
Explore how default CIBSE air change rates and other heat loss assumptions in pre-2000 properties can give the false perception that high design flow temperatures (~50C) are required even with radiator upgrades when 40C flow temperatures are not actually that hard to achieve in reality, see: Simple heat loss tool (40C or lower being the design flow temperature that really delivers on SPF H4 4.0+).
Related reading
- Blog: How default assumptions in heat loss calculations over-estimate heat loss.
- Blog: Steph Willis (Spruce): Why Everyone Oversizes Heat Pumps
- Is an oversized Daikin really a problem? (Yes if your heat loss is 4-6 kW and you have the 9-16kW model)
- Vaillant maximum output capacity testing (Beware, maximum output table in the Vaillant datasheet does not match real world defrost conditions, size accordingly, this is common for other manufacturers as well).
- Electrification of Heat trial data (Deep dive into the Electrification of Heat trial heat pump performance data and related discussion).