My Journey to an efficient ASHP

If your buffer and pumps are set correctly and the correct stratification is achieved then the there should be very little temperature difference in the flow in and out of the buffer and the return to and from the buffer. So if you want a dT of 5 degrees then it should be obtainable across the system.

Well… the deltaT has come down (now showing 4.5 rather than 6.5 in the dashboard) and consequently so has the Flow Temp (average “when running” is now 36) so that’s all good.

What I’m not seeing is any improvement in CoP - which has actually got worse - but that’s confounded by a couple of other variables:

  • One issue with a Ground Source system is that the ground gradually cools down over winter and just now the ‘brine’ is coming in from the ground loops at 6.3 degrees, whereas it was more like 10 degrees at the start of December, That has the same impact on CoP as for an air temperature change of that magnitude with an ASHP.
  • In the warmer weather we’ve had for the past few weeks, my system has been spending more time on standby which is pulling about 60W for zero heat output (and about 20W of that is the Charge Pump). That makes the CoP look bad - but the running costs are excellent.
    • I’m #2 in the daily cost rankings (and winning hands-down in £ per m^2)
    • I could get a better CoP by shifting more heat, but then I’d be paying more…
3 Likes

Indeed. I’d assumed you’d reverted to “heating, auto” = On but if that’s Off then it’s just using the 90% when the compressor is running and the 25% when it’s not - hence the ‘square wave’ on the Charge Pump Speed graph.

Yep. That’s rather cryptic but it’s telling the heat pump to adjust the Charge Pump speed to aim for 5 degrees dT (at the Dimensioned Outdoor Temperature, which is a measure of the nominal design condition).

A lower dT will tend to raise the pump speed (more water through the heat exchanger to cool it quicker) - but clearly it will max-out at 100%,

I don’t get how Nick is ever going to set his pumps correctly though Mike. If I understand his system properly, he’s got:

  • One pump running the Radiator circuit, with its own thermostat and zone valve
  • A second pump running the UFH circuit

If both those pumps are running, it will be hard for the Charge Pump to move enough water through the heat pump to satisfy them both - and if the Radiator pump is turning on and off (without the Heat Pump controller being aware) that’s surely going to mess up any attempt at pump speed balancing, isn’t it?

1 Like

It’s never going to be perfection but more of a balancing act, so if we forget about temperatures at the moment and think more of flow rates, if the flow rate from the heat pump is 20ltrs then the flow rate to the zones needs to be 20ltrs but if the radiator circuit pump is running faster and demanding 25ltrs that will pull cooler water up from the bottom of the buffer lowering the temperature of the radiator circuit. The same applies to the ufh and this why good stratification is vital when using a buffer. If we look at temperatures you want to try and match flow in and out and return in and out and the only way is by adjusting pump speed

1 Like

OK, but if the UFH pump wants to move 15 litres and the Radiator pump wants to move 10 litres - but the Radiator pump is switching on-and-off then what does Nick try to match with the Charge Pump speed: 15? 25? 20 as as halfway house?

I just can’t understand how a big, 2-pipe Buffer Tank piped as a ‘short circuit’ between Flow and Return is the right choice for Nick’s installation, whereas I can understand how a smaller, 4-pipe Buffer Tank would isolate the multiple pumped circuits from each other - something like the black tank shown in this other thread (which appears not to need it, since it only has a single emitter circuit).

1 Like

Yes you are right a 2 pipe buffer will only add volume to the system whereas a 4 port will give some hydronic separation to the two zones. I am not over familiar with the ecodan so unless all of the pumps on the system are modulating pumps and all wired in to the control center to be controlled by the sensors, then the heatpump will see 1 circuit between that and the buffer and the other two circuits rads and ufh have to be controlled manually.
Don’t bother ever adding a volumiser to a system just use a bypass on the radiator furthest away from the heatpump, it’s only there to help defrost cycle.

1 Like

Thanks Mike; 100% agree.

Nick: I can’t see how you’ll properly fix this without some plumbing changes. You don’t need the additional Volume that is added by the existing 2-pipe Buffer Tank whereas you would benefit from the ‘separation’ or ‘isolation’ that a 4-pipe Buffer Tank (or Low Loss Header) would provide, letting each of the pumps work (more or less) independently.

I’m still curious how the original installer thought this was going to work, but if they’re not engaging with you then it’s probably better to look elsewhere.

1 Like

Hi Mike,

Quick update! The installers finally agreed to send a plumber around who took one look and told me the cold return should not be plumbed to the UKV and it would need changing! Work is underway to make this happen. I’m sure he said it should be the hot water return instead feeding the UKV but didn’t mention a 4 pipe buffer at all.

Will chase this up once we’ve confirmed the work is going ahead.

ASHP performing well, Delta-T still pitiful though. The biggest gain for me by far (so far) has been modifying the DMS value.

Will update further.

Thanks,
Nick

1 Like

That’s great news that you’ve got them to agree there’s something wrong with how it was originally plumbed.

When you get a bit further with planning the changes, the key question from me is what happens when the multiple pumps on the heating circuit are moving more (or less) water than the heat pump’s charge pump is producing.

I’ve not digested this thread fully but I have a NIBE system similar to yours so I feel your pain as there is not a large resource of community information.

Its been four years but each year has been a learning experience to optimise the ASHP performance. This heating season I plan to get the data into OpenEnergyMonitor although we don’t have a heat meter.

The biggest issue I found on our system was the compressor was cycling too frequently and the flow temperature varied wildly around the calculated setpoint. First I thought it was to do with the degree minutes but no change I made resulted in what I was looking for. The solution I finally found last October was to manually cap the maximum frequency of the compressor inverter based on the outside air temperature. In short I set it to it’s lowest unless it’s sub zero outside. At the coldest point this year it almost ran all day and the house temperature was fine. It’s possible to also limit it for HWS but I’ve left that max freq in auto for quick recovery.

2 Likes

Hi Peter.

Welcome to the forum. I agree that NIBE systems are much less common than some of the other brands but they do natively report a lot of operational parameters and once you setup some way to access those values and include them on a dashboard there are a fair few of us on here who’d be happy to take a look at the data and what that implies for how your system is behaving.

Nick has been very good at posting photos of his installation on this thread to help others understand his slightly unusual combination of pipes and pumps. I’d recommend you start a separate thread if you’re planning to post information about your own installation.

David

Hi Peter, which menu option does this (compressor frequency) fall under in the NIBE set-up?

From main screen hold the back button to get service menu to appear.

Enter the service menu which has the spanner logo.

5.1 Operating Settings->5.123 Compressor Curve.

Mine is set for -10 Max compressor & 2 Min compressor.

The HWS is on Auto.

Ah you mean the compressor curve.
Yeah I found it useful to adjust that setting too.

I’m sure the reason I had to change it manually is because the settings that influence the Auto function are incorrect. However I couldn’t find any information that detailed which settings these might be.

Glad you had already found the setting. It’s made a real difference to the compensated setpoint control.

Hello. I have been in touch with David for most of 2023 and my NIBE HP is functioning a lot better thanks to his guidance. Coincedentally, we were talking yesterday about manually changing the compressor curve to influence the maximum frequency, because there appears to be a rise in consecutive cycles (perhaps linked to the outside temperature falling slowly). David’s GSHP does not have that service menu option because his older model is “on/off”, not modulating. May I ask what sort of numbers you came up with in the manual setting? I have attached a screenshot from yesterday, the period that triggered the conversation. Thank you

Peter


I adjusted the temperature at which the compressor ramps up to max downwards to -10C with the slope adjusted to start a zeroC. So the rate at which the compressor ramps up is now very gentle and will very rarely or never reach the max value…

This twitter thread covers this change https://x.com/Zapaman/status/1525554131435405313?s=20

1 Like

Thank you for the photo and note. Unfortunately, I have never signed up to the social media world so I cannot read your twitter thread. Is it publishes anywhere else?

No not posted elsewhere, but the thread doesn’t provide much additional information (just a little background) so you aren’t missing out on any key details. But you can probably still read that thread without having to sign up to Twitter-X