Ron,
If you follow @Andre_K advice of waiting until the compressor/fans outside stop (for me this was when my set back kicked in), then use the ASHP Controller console to read the flow and return temps (when the compressor not running for a while) these two temps should be the same, if not then there’s a issue with sensor calibration and that will throw the Vaillant COP off by quite a large %.
In my scenario these reading with the compressor off were …
1Hr into setback, Flow Rate: 1137 L/hr, Flow Temp: 26.0C, Return Temp: 26.6C.
2Hrs into setback, Flow Rate: 1130 L/Hr, Flow Temp: 25.2C, Return Temp: 25.8C
As you can see the flow temp is consistently 0.6C lower than the return causing my COP to be under reported by 22% (See @Andre_K calcs for more detail). In your scenario its likely to be the other way around.
To get to read the flow and return temps…
In the ASHP Controller, navigate to the Installer Level, select it, enter the access code 17, navigate to the Sensor/Actuator test and keep pressing the + sign to get the Flow Rate, Flow Temp and the Return Temp readings. If you do this when the compressor isn’t running you can calc by how much your COP is mis-reporting.
All that said, if there’s one thing I got from this entire super helpful thread is that if you have low flow temp, you have an efficient system, no matter was the Vaillant COP says!
This weekend I’m putting in an Open Energy Monitor my plan is to log both and compare, just like @Zarch has done. This is great post … Vaillant aroTHERM | DT5 | Mass Flow Rate Triangle