Vaillant inbuilt monitoring vs MID meters

@glyn.hudson and I have been involved in a remedial project locally, a poorly performing LG high temp heatpump has been replaced with a Vaillant arotherm, the good news is that the COP has improved from 2.2 with the LG to 4.8 so far with the Vaillant :grin:

It’s been interesting comparing the Vaillant app figures to the class 1 electric and class 2 heat meter that we provided to the installers. Here’s a screenshot from the app:

and comparison with electric and heat meter values:

Vaillant app Class 1 electric & Class 2 heat meter Error
Date Electric Space Heat DHW Combined COP Electric Combined COP Electric Heat
29/03/24 30.4 175.1 7.9 183 6.0 30.1 144.8 4.8 1.12% 26%
30/03/24 21.9 100.1 16.9 117 5.3 21.9 94.4 4.3 -0.15% 24%
31/03/24 14.4 91.1 1.8 92.9 6.5 14.0 73.3 5.3 3.20% 27%
01/04/24 19 107.7 5.7 113.4 6.0 19.0 90.9 4.8 0.18% 25%
02/04/24 13.3 77.4 6.3 83.7 6.3 13.4 67.0 5.0 -0.46% 25%

The electric values are pretty good but looks like a temperature offset error is pushing up those heat values again. This has to be a relatively easy one for Vaillant to fix.

@glyn.hudson got some good pictures of the temperature sensors I think on his parents system, they look like they are in pockets and so should be good but perhaps they are just not calibrated pairs??

4 Likes