Vaillant inbuilt monitoring vs MID meters

Well, it’s tough being as badly calibrated as the Vaillant sensors. Any DS18B20 is typically closer to the truth than those particular NTC10K.

You’ve got a baseline 0.6K delta, which means you overestimate COP. The amount depends on your actual deltaT when the compressor is on and ideltaT/(deltaT-0.6K) will give you the “wrongness factor”. For example, 1.3 would indicate 30% overestimation.