Hi folks,
I’m trying to reduce the amount of cycling my heatpump does. I wonder if you guys have any advice…
My system was originally installed as part of the electrification of heat scheme back in 2021. I suspect it was a touch oversized to begin with tbh.
To make it worse the heatpump is an arotherm plus 12kw running 351.06.07.
Anyway, after the scheme ended I hooked up a pi and tweaked emon to read their heat meters and I now i have a couple of years of data to play with 
During the summer as part of a major renovation i replaced our suspended ground floor (+rads) with solid 200mm pir and 60mm of liquid cemfloor screed with UFH at 100mm centres. I can already see from emoncms that this is doing its job.
The radiators upstairs were untouched but placed into their own zone with a separate stat. The UFH does not have a mixer valve. Both rads and UFH are fed from a buffer tank. The system did have glycol, but since the summer its just water, theyre supposed to be putting glycol back in it. (not sure if i should persue this..). The house is a 1990s build and approximately 230 sqm.
The problem is that rads and ufh have such different demands. If only the rads are in use then the system excessively short cycles, if the rads + ufh are active then too high a flow temp is sent to the UFH.. etc. This wasn’t as noticeable before because everything was a single zone..
I would like to try it with both zones tied together, this would effectively run the rads at a lower temperature but for longer and without the cycling.. but i’m fighting the vaillant controls to do so..
For now, I’ve set the rads + ufh to the same time periods and heat curves etc. but minor offsets in the ‘stat temp readings still can still cause hours of short cycling when only the rad zone is calling for heat. The system is in expanded mode, past experience was that active mode cycled much more in spring/autumn, though I haven’t tried active since adding the UFH.
If i try to set both zones to use the main stat (a vrc 720f) it will throw an error saying it cant have the rad stat unassigned. As a hack, I created a dummy Zone 3 just to assign the rad stat somewhere that kinda worked but also had issues
…
Does anyone have any setup suggestions? is there anything i can do to persuade the vaillant controls to treat the two zones as a single? I can send some screenshots from emoncms etc. if it would help…
Cheers
Al.