Hi Terry,
In answer to your original question I have the 6kW Daikin. Mine is capable of and does output its full specified output power, or near enough. However it doesn’t do it very often because there is rarely the demand put upon it. As a basis for comparison the 3 bedroom house (80m2) in Scotland I live in has had a maximum heat requirement of 3kW when it was -8C at night rising to -2C in the day.
My gut feel is that the situation is the same for you. The heatpump (and I mean specifically the heatpump, not the whole heating system) is not being asked for 8kW of heat, and therefore it doesn’t produce it.
Lets forget all the technical stuff and return to the basics. What is the actual problem you are trying to solve? I assume that it is that your house is not kept warm when its cold outside. You mentioned in one post that the lounge stay at 13C. This is clearly not a heating system working properly. Can you give full details of what the problem is (whole house, specific rooms, all the time, only when cold out, etc)?
Here’s the technical bit to try and explain, as Ben & Matt have, about what is going on. But I think the answer lies above in the fundamental problem rather than what the heat pump is doing.
You are correct that a combination of a 10C difference between LWT and RWT combined with 7Lpm flow rate equates to ~4.9kW of heat. However, lets be clear about the settings, in selecting radiator in the Daikin MMI you have asked the heat pump to target a LWT/RWT of 10C. However there’s no setting that says use 7Lpm flow rate, that is being selected by the Daikin control algorithm.
You allude to the fact it is higher before it reaches steady state, which is what I would expect. The low flow rate is being selected because not enough heat is being dissipated by the radiators to warrant a higher flow rate. So the situation is back to front from what you suggested. Its not that a 10C difference & 7Lpm implies in a 4.9kW limit its that a targeted 10C difference combined with 4.9kW demand implies a flow rate of 7Lpm.
Its also worth noting that 7Lpm is the lowest flow rate the 4-8kW Daikins will flow at. At heat demand of less than 4.9kW the flow rate will stay at 7Lpm and the difference between LWT and RWT will drop below 10C (this is that state that my heat pump spends most of its time in).
You mention the Daikin spec of 12Lpm minimum of flow for the radiator circuit. This is correct, the specification for the heat pump requires a minimum possible flow rate (at maximum pump speed) of 12Lpm round the radiator circuit. It doesn’t mean that this is the minimum flow rate that the heat pump will choose. The fact you are seeing 7Lpm is normal. If you start the system from cold, I’d expect that you would see more like 15Lpm flowing until such time as LWT rises to your desired temperature.
I doubt there is anything wrong with your heatpump, but if your living room only gets to 13C there is definitely something wrong with your heating system. Your radiators look plenty big enough, my guess is that the problem lies in the pipework.
Finally, if you want to confirm that your heatpump is capable of producing 8kW for heating you can do the following. Let the water in the system get cold (turn the heating off for a couple of hours). Turn the heating on. In the MMI Information screen watch the LWT, RWT and Flow rate. From the instantaneous values of these three you can calculate the heat being produced. As a rule of thumb at 15Lpm each degree of difference between LWT and RWT is 1kW of heat. At 7Lpm its about 0.5kW for each degree of difference. As your system heats up the water in the heating system you should see it producing in the region of 8kW. I’d expect to see for example LWT 34, RWT 26, Flow 15Lpm. You’ll see it maintain roughly 8kW up until it reaches your desired LWT.