Yes.
For the avoidance of doubt that is exactly what I am implying.
You were fortunate that they turned up and installed a heat pump. Over the road some chump monkey of an Octopus “engineer” surveyed a property, didn’t understand that it was a one pipe system, and the (contracted out) installer who arrived had to abandon the job with a “FFS you had one job” type opinion of his client. In other cases they’ve surveyed, arrived, actually started the job, then abandoned it leaving others to finidh.
You’ve found that it wasn’t setup. That seems to have been your decision. You’re now suggesting that it’s oversized too. That is also not entirely unexpected.
Others are finding that the Octopus installs don’t win any awards for in use performance either. (reference the league table that open energy monitor provides)
If you’re prepared to start with the assumption that they’re not particularly good at what they do you can troubleshoot the system. If you assume that the sun shines out of their backside and they know what they’re doing…then you’re not going to question all the decisions that ought to be questioned and you will get nowhere. That’s why I’m suggesting that you start with the assumption that the installer was at best an enthusiastic newbie and work from there.
It is not unfair or unreasonable to start with that assumption. They may have joined the pipes and wires very neatly. This does not make a quality installation though. (joining pipes and wires is the easy part)
Let’s go back to the beginning.
- The temperature of the water sets the heat output from the radiators
- The weather compensation curve sets the temperature of the water for a givne outdoor temperature
- The compressor will run until the water is at the temperature the controls demand
That’s it on a basic system.
Sometimes there will be an error (undershoot or overshoot on room temperature)
What you are calling a “thermostat” is NOT a thermostat but a device for setting “room influence” [on water temperature]
- The load compensation takes the room temperature vs the setpoint (works out the error) then tweaks the desired water temperature up or down to suit (room influence)
- The compressor runs to maintain that desired water temperature.
If your weather compensation curve is too low, or your load compensation influence is too low, then the target water temperature will be too low. There probably isn’t ANY load compensation if the controls are set for fan coils.
Are you still on speaking terms with Octopus after you told them to go away before they finshed their work? If so, and you trust them to do a good installation, then the best option might be to as them to come back and commission the heat pump for you. Else what does the manual say?
If it continues to put heat into the water, even after the water is at the right temperature, then the water will be too hot.
Sometimes the radiators are able to emit ALL the heat the units puts into the water and so it can run continuously. Typically, if you’re designing for 45C at design condition with type 22s, and your radiators are capable of dissipating the full output of the heat pump when they are at 45C, then they will still be able to dissipate the minimum output of the heat pump when they are at say 30C.
If you are designing for higher temperatures at deisgn condition, then when you dial down the water temperature in the radiaotrs they are not able to emit enough heat even with the heat pump running at minimium output.
Also if your heat pum pis larger than the radiator area than you have, then evern if you are designing for say 45C at design condition the radiaotrs cannot emit enough heat even with the heat pump running at minimium output.
Think of this two ways:
-
Your target water temperature is too low for the radiators to put enough heat into the proeprty to acheieve your target set point. Work out how to use the weather and load compensation controls to make this happen.
-
Your radiators can’t kick out enough heat to let the heat pump run continuously even at it’s lowest output. Either somebody (and yes, I’m looking at Octopus) has fudged up the system design with far too big a heat pump on far too small a set of radiators; or there is somethign else amiss such as horrible balancing (they haven’t configured the hating system to ensure that each radiator gets the flow it needs - towel rails and auto bypass valves are classics for shortcutting water around a system) or user error (turning off radiators or using TRVs to limit temperature in too many rooms etc.
Share the Octopus design (the MCS calculations) and we can comment on #2. Invite them back to finish the job is easiest for #1; else you’ll need to become skileld enough to install Daikin units yourself?