Hi everyone,
Thank you all for your responses to this thread - I have been reading them with much interest and really appreciate everyone’s contribution. Unfortunately I’ve yet to be able to figure out how to quote others to reply directly to their points raised, so make my comments generically below.
I now have a better understanding of the different issues due to the contributions above, and would break them down into 2 areas:
- The anti-seize cycle that runs after 24h of inactivity to prevent the pumps from seizing, and mostly affects in summertime.
- The ‘Freezing Control’ cycle that runs during cold weather to prevent freezing of the outdoor unit.
Starting with (1) above, this occurs after 24h of pump inactivity and the pumps will cycle for 5 mins with the DHW valve open. This can cause issues in the summer if the DHW is not reheated every 24h, draining heat from the DHW tank. I was affected by this issue last summer as I was varying the time of the DHW reheat cycle to coincide with the cheapest 30min Agile pricing slot, so on some days the period between reheats would exceed 24h. As we have a 50L volumiser, this effectively transfers heat out of the DHW tank into the volumiser, reducing the water temperature.
I have found a manual workaround solution to (1), and that is to manually cycle the pumps every day, within the 24h period. To do this, I enter Self Test mode, open the DHW valve and turn the pump on. You only need to run the pump for a couple seconds before turning off again for the system to register pump activity and reset the 24h period, and manually running the pumps for a few seconds will not drain anywhere near the amount of heat from the system as running for 5 mins.
Regarding issue (2) above - I am in a near identical situation to @Peter_Reid. We too are currently on the Cosy tariff, and turn off the heating for the peak period between 4-7pm. I can confirm on my Samsung gen6 12kW unit, the ambient temp at which the Freezing Control kicks in is definitely 5C and below, not 3C as suggested above (I observed my system the other evening as the temperature dropped to 4.5C and the freezing control kicking in just over an hour after the heating was turned off). It’s actually worse for us as our external ambient temperature sensor reads around ~1C low, so it’s actually activating at ambient temps of around 6C and below (not 5C), and I have no way to recalibrate (that I know of).
I have not found a good workaround or solution yet to manage this situation. We typically reheat the DHW during the 1-4pm cheap slot and turn off the heat pump during the expensive 4-7pm slot. When we come to wash up after the evening meal, all the hot water is gone again which is a ludicrous situation. During the off period, I have tried putting the unit in Self Test mode, which prevents anything running, but it then throws an error code after an hour when the pumps cannot start (E911). I then exit Self Test mode at 7pm, clear the error and turn the heating back on, with DHW still intact. Sometimes the system ends up throwing multiple errors and the system locks up requiring a power off/on to restart the system. The other option is to just turn the whole system off at the wall during the period and back on again when ready to turn the heating back on. I would appreciate any thoughts if this type of power cycling of the indoor controller is doing any long term harm?
This issue also affects me overnight. Unless the weather is freezing cold, we also tend to turn the heating off overnight and reheat from cold the following morning which costs less than running constantly overnight. If it’s freezing, it’s not an issue as we’d run heating overnight, and if it’s mild (well above 5C) it’s not an issue as the Freezing Control won’t activate, but where it’s in the 3-6C range, it’s an issue and the DHW tank is stone cold by morning. Again, my solution at present is to just turn the whole system off at the wall overnight and back on in the morning.
I have tried to put the issue into financial perspective. I have casually observed that reheating the DHW from stone cold vs if that tank had normally cooled to mid 30’s C, probably costs an additional 1kWh for us. At Cosy cheap rate, this is maybe only costing us 12-15p per day, on a handful of days per year. So financially it’s not a disaster by any means. That said, it’s the inconvenience of not getting up to any hot water, and then we’d have to reheat it as standard rates which costs twice as much, or we end up boiling a kettle to wash up having just lost a cylinder of hot water that we’d only just reheated.
I just wish there were a way to override the controller to tell it to work how I want it to work, to suit our environment and needs. We have glycol, so the anti-freeze control for us is almost pointless and I’d welcome a setting to be able to adjust the activation temperature and/or disable it.