Samsung Gen6 and anti-freeze pump cycling below 5C OAT

I don’t think the hot water theft incidents are connected. The bulletin only mentions cyclic pump operations as part of heating off due to the outdoor temperature being higher than the FSV for heating off, ie not related to anti freeze strategy.

I can’t find it now but I do remember reading something about the antifreeze strategy using whatever the last heating mode was (Heat / DHW) but I have never confirmed this.

1 Like

Thanks @SarahH

Unfortunately I will not be able to email as I don’t have any monitoring, so no available evidence other than my own informal observations.

Having installed my manual switch, I was able to make further observations last night during a further cold spell.

Firstly, the AF cycle lasted 7 mins for me (not 5 mins as previously thought).

I have a Joule pre-plumbed tank, which has a 3-way valve for selecting space heating / DHW, combined with further 2-way (open/closed) valves for space heating zones. I also have a 50L volumiser plumbed in the primary return to the ASHP.

When I lock the 3-way valve in the space heating position to protect the DHW tank, the circulating water simply loops round the primaries through the 50L volumiser. The 2-way zone valves for the heating circuit do not open (as the call for heat is off) so I’m simply circulating the 50L of warm water in the volumiser combined with the volume of water in my 28mm primary pipes, some 25-30m of it for both flow and return, combined.

My flow temps for heating are typically ~32C, with a dT of around 3C, so when a heating run ends, I’m assuming the temperature in the volumiser is around 29C as it’s located on the primary return. After an hour, when the first AF cycle ran, the LWT sensor in the outdoor unit was registering 26.5C after a few minutes, which seems reasonable. I left the heating off all night, and nine hours later the LWT sensor was reporting closer to 20C after a night of AF cycles - still sufficiently warm not to present a risk of freezing (and I have glycol anyhow). However, if I had such a pre-plumbed arrangement without a volumiser fitted on the primary return (for example, installed within the emitter circuit, or no volumiser at all), then the AF cycle would have a very limited volume of water to work with using our hack. Thus I can maybe see why Samsung defaults to using the DHW circuit, as in these circumstances just the volume of water in the primary pipework with no additional source of heat may provide insufficient protection.

Still, it would be nice to have an installer configurable option giving the choice.

Anyway, I’m happy with my solution but it would be nice to see Samsung take this on board.

Great news Sarah! I’ll find some evidence from my own monitoring at send them on. Thank-you for getting the conversation started.

Hi Sarah, here some proofs for the guys. Can’t believe they are not aware of it…. You can easily see that when pump is running AF or AS cycles it opens always DHW circuit even if the pump is actually at CH circuit but not heating. You can see each AF run takes 2C from the tank. 5 cycles during the night steals 10C from hot water tank!

This was when I didn’t have DHW connected. You can see no problem for AF/AS cycles. It simply run the water in a circuit for 3 minutes or so and then finished. No issues, no freezing, no stealing.

2 Likes

Many thanks, @Michal_S, I’ve forwarded the more compelling data to Nick.

Sarah

I’ve emailed Nick directly with some evidence from my own system last night

Well done, @jakeymd1. Nick has just emailed to say thanks, he now has enough data.

2 Likes

Do you guys think there will be any outcome from this initiative? I can’t really believe they are not aware of this behavior. I’m not sure if R290 units do behave same like R32 HTQ units or older. I think there was some discussion with Nick about this topic few months ago and he said something like it’s normal it takes heat from DHW because there is a good chance there is some extra heat. So don’t know what to think. A very easy FSV could sort this out, for this you don’t need any analysis or anything. Just have switch - operate 3-way valve or not during AF/AS cycles. Let’s see but my hopes are low.

Btw, seems Samsung is not the only one doing this but probably on ecodan you can change this behavior in settings? Look here.

Hi everyone,
I just read the entire thread and found a lot of interesting information.

I seem to be the only person who doesn’t mind the AF mode drawing heat from the DHW. I have a parallel backup heating source (pellet boiler) and I don’t want the HP water pump to interfere with the backup boiler’s water pump when in use.

But I can confirm that the temperature drops on the 300L DHW tank are 1 to 2 degrees per AF cycle.

What I’d like to change is the default position of the 3-way valve. It’s set to UFH by default, and I’d like it to be set to DHW by default. I can’t change this either with the wiring or via the FSV.

The second thing I’d like to change is the hysteresis of the room thermostat. The hysteresis is one degree and can’t be changed to my desired 0,5 - 0,7. There are no settings for the FSV 106x on my HP (manufactured 2022 or 2023), but they probably wouldn’t help. I’m considering using an external thermostat.

Hi @szybkowar, welcome to the forum.

Can this not be changed by FSV #3071, default direction of 3-way valve (3071=0 [heating]; 3071=1 [DHW tank])?

I use an EPH C4 external wireless room stat which works really well for me. The hysteresis can be set in the range of 0.2-1.0C.

no, unfortunately if I change 3071 the valve position will change but then the pump thinks it is heating DHW but the water flows to UFH and vice versa.

Thanks for the thermo recommendation, I see that it is a simple dry contact, I will look for something similar on the Polish market or use a zigbee switch to control via HA.

Hi, first question Old Scientis replied but for the second…

It’s truth that hysteresis is fixed 1C which is ridiculous. I’ve complained many times for that. Unfortunately I have older firmware where it is not possible to change. I guess some new firmware has this possibility but I guess it’s still limited to like 0.5C or so but I’m not sure.

Nevertheless if you have pump connected with home assistant and have access to Modbus registers you can trick the pump and mimic the hysteresis as you want by automation while still using the HP remote controller as a roomstat.

This automation checks when target temp is reached and lower the target temp by 1C so the pump will turn off immediately and not start any time soon. E.g. target temp 23C is reached so the automation set target temp to 22C. So normally the pump would start only when room temp reaches 21C. But then I have another automatization which monitor real room temperature all the time (trigger on indoor temp change) and if it will find it’s below the set hysteresis - e.g. 0.2C then it will set target temperature back to your desired room temperature. This immediately makes the pump start heating. This little trick works very nice and you can simulate any hysteresis you want with original remote controller and don’t need to use external thermostat.

Cheers.

1 Like

The newer firmware does now support hysteresis adjustment for room control, it also makes low output far more stable / efficient with less cycling.

Unfortunately to update the firmware you need an SNET interface and the correct file (email support for the file but you will need to know the PCB version of your controller).

It’s does appear Samsung do improve the firmware post production and the ability to update them, more than can be said for Vailant where a PCB swap is needed.

1 Like

Not sure about below 5c OAT but mine does this sort of the thing around 5c..

Does the newer firmware make much difference to lower o/p running? I’m monitoring on S-netpro 2 and comp never goes below 20hz.

When you say newer fireware, do you know release date and software version. I would love mine to be a bit more stable.

I would also like if the PWM for the pump would remain active and not require the unit to go though a heat demand off and on cycle to kick it back on.

The most recent AFIK MIM firmware was released in late 2024 but the firmware file is dated much earlier (in my case the “new” firmware is DB91-02103B_231214, so 2023), my original MIM firmware was 220614. The newer firmware is listed in a service bulletin on the Samsung service portal but the files were not, in the end I emailed technical and they replied back with the files and a helpful installation guide.

@SarahH the newer firmware still has terrible PWM pump control and still ignores any max speed settings during startup, leads to cycling due to abrupt speed change etc. This drove me mad, so I made an ESP32 man in the middle pump controller with soft start, throttle back during valve changeover etc. It works far better now.

On the subject of minimum compressor inverter frequency, have a glance at the traces from my 8kW HTQ today.
Story so far. I run a 5degC setback overnight so the HP has to work hard to re-warm the house. To minimise the time it takes for this, I have a high WL setting (hotter radiators = quicker warm-up), which with #2091 set to 3 was causing a lot of cycling during re-warming because LWT was hitting WL target repeatedly. Once the living room was up to target, the roomstat took over control, but the high LWT when there was a demand was still giving a poor instantaneous CoP. So yesterday I decided to I change #2091 to 1 (so the HP would keep running at minimum inverter frequency even if WL target was satified), and to drop the WL target once the room was warm, in the hope of improving the CoP. Here is what I saw:

  1. (06:50) HP starts per roomstat programme, LWT (red) quickly rises towards WL target (yellow), inverter drops to 20Hz (magenta line), regarded as “normal minimum” for the HTQ range, and stays there (per #2091=1 rules, even though LWT gradually rises to >2degC above target).
  2. (10:20) Seeing that the roomstat was within 0.1degC of setpoint I reset the WL target down a few degC (you can see the yellow line respond).
  3. (10:50) Room reaches roomstat target and switches off the HP.
  4. (11:25) Room has cooled by hysteresis setting (1.5degC) and restarts the HP. Because the WL target is now lower, the inverter drops to 14Hz. This is something I’ve noticed before at milder OATs (today is ~9degC per brown line).
  5. (12:50) room temp back up to target, so stat switches HP off again.
  6. (13:25) back on again due to roomstat demand, and inverter returns to 14Hz.

The energy figures appear along the top and you can see that the instantaneous values at end of trace (top right) were 0.77kW consumed, 3.26kW generated. (The figures 1.07kW in/5.38kW out/5.0 CoP just to the left are the time averaged values over the prior half hour or so.)

So my preliminary conclusion is that, at mild OATs at least, it may be possible to force your HP’s output well below the “~50% turndown” capability that Samsung normally state.

Any comments so far?

I have a question, though. As is obvious from the above trend, I don’t operate PWM on my circulating pump (black line), and the LWT-RWT delta is typically about 2degC - well below the ~5degC often sought as “optimum”. I get what I feel are respectable CoPs running like this. My question is, where do I find a technical explanation for seeking to run at 5degC delta by varying the circulation rate? (I can’t believe it’s just the handful of Watts saved by running the pump slower.)

This is kind of how I run my Gen 6.

It’s oversized, so running overnight would result in a house temp that is uncomfortably warm for sleeping, so we normally turn off the heating around 11pm and the house has cooled by 1C by the time we go to bed, and like you maybe 5C by morning.

We use the timer function of our 3rd party room stat to turn the heating back on at 6am and the house reheats during the course of the day. It’s normally around 18.5C by the time we get up, and ends up back at 20C by late afternoon until bed.

Like you propose, we run in what I refer to as “always on” mode (#2091 = 1) and allow the room stat to turn on/off as required. I actually don’t adjust the LWT too much. The minimum LWT we can achieve is ~32C. We find that even at minimum LWT, the house initially reheats quickly as the deltaT between room and radiators is large, so more heat is emitted into the rooms meaning the heat pump works harder to maintain that 32C LWT. As the room temp rises, and the room to radiator deltaT narrows, less heat is emitted and the heat pump output falls back accordingly until minimum output is it’s reached, all the time running a low flow temp with decent COP. Obviously the house would warm back up quicker at higher flow temps, but at a cost of lower efficiency.

Our LWT-RWT deltaT has always been low, somewhere in the 2.5-3C range I’m guessing (we have fixed flow rate, ~24.5L/min). Initially I thought this may be an issue and was fixated with reducing flow rates trying to widen deltaT to 5C, but a low deltaT does not appear to harm efficiency. Other Samsung owners seem to have reached a similar conclusion. If you have fixed flow rate and COP values are good, I see no issue with a deltaT below 5C.

2 Likes

Hi Sarah, I also run mine at a fixed flow rate and have found the performance to be a lot more stable than when running with PWM, which its seems to be has brought with it better COP, especially at milder temperatures.

As to why we use PWM to chase DT5? I only suspect that lower is better, but there’s a practical limit due to water velocity and flow resistance. You could have DT2 at design temperature, but your water velocity would need to be 2.5x higher and resistance would be 6.25x higher. So there probably comes a point when upsizing pipework and circulating pumps is just no longer worth it.

But this doesn’t explain why we use PWM to chase DT5. Why not just run at fixed flow rates achieving DT5 at design temperature and lower DT at higher outdoor temps. So I’m perhaps wrong, perhaps it’s something to do with the thermodynamical properties of refrigerant. But Vaillant run at fixed flow rates, and they’re some of the best heat pumps on the market.

Make of this what you will, but AI says:

It’s matched to the evaporator and compressor design

Most modern air-to-water heat pumps are engineered around LWT 35–45°C and ΔT around 5°C, because:

  • The plate heat exchanger is sized for this range

  • The refrigerant superheat/subcooling balance sits here

  • The compressor modulation curves assume high flow

Manufacturers tune the whole system expecting ΔT≈5, so if you run ΔT much higher:

  • The compressor may surge or cycle

  • Flow switch trips can occur

  • Efficiency drops

  • Hot water delivery becomes less stable

I did do some more digging with AI, but I’m hesitant to just copy and paste too much AI output, but you might find it helpful to get the answers you’re looking for.

2 Likes