My Journey to an efficient ASHP
Hi Peter, which menu option does this (compressor frequency) fall under in the NIBE set-up?
From main screen hold the back button to get service menu to appear.
Enter the service menu which has the spanner logo.
5.1 Operating Settings->5.123 Compressor Curve.
Mine is set for -10 Max compressor & 2 Min compressor.
The HWS is on Auto.
Ah you mean the compressor curve.
Yeah I found it useful to adjust that setting too.
I’m sure the reason I had to change it manually is because the settings that influence the Auto function are incorrect. However I couldn’t find any information that detailed which settings these might be.
Glad you had already found the setting. It’s made a real difference to the compensated setpoint control.
Hello. I have been in touch with David for most of 2023 and my NIBE HP is functioning a lot better thanks to his guidance. Coincedentally, we were talking yesterday about manually changing the compressor curve to influence the maximum frequency, because there appears to be a rise in consecutive cycles (perhaps linked to the outside temperature falling slowly). David’s GSHP does not have that service menu option because his older model is “on/off”, not modulating. May I ask what sort of numbers you came up with in the manual setting? I have attached a screenshot from yesterday, the period that triggered the conversation. Thank you
Peter
I adjusted the temperature at which the compressor ramps up to max downwards to -10C with the slope adjusted to start a zeroC. So the rate at which the compressor ramps up is now very gentle and will very rarely or never reach the max value…
This twitter thread covers this change https://x.com/Zapaman/status/1525554131435405313?s=20
Thank you for the photo and note. Unfortunately, I have never signed up to the social media world so I cannot read your twitter thread. Is it publishes anywhere else?
No not posted elsewhere, but the thread doesn’t provide much additional information (just a little background) so you aren’t missing out on any key details. But you can probably still read that thread without having to sign up to Twitter-X
Understood. Thank you again
Hi, the only nibe recommended way of setting up two climate systems (rad and UFH) is to use smo-40 with ecs 40 or 41 add ons for UFH.
Ive started with smo-20 and there was no way to set the system correctly.