@matt-drummer remind me have you got any modulation active , and are you on pure weather comp
I was thinking if turning modulation off next

I have no modulation, not possible as I don’t use the Madoka at all.

No room temperature control apart from me and the weather!

No wdc either.

Just fixed lwt that I adjust from my telephone as I see fit, which is not very often, normally just when it is out of control!

But I don’t even do that anymore.

If I am not happy with the flow temperature I just turn it off, set it to what I want and then restart.

Mainly actually if I want to turn it down, it tends to ignore the request for some time, turning it up when running isn’t so much of an issue, but if it doesn’t do it more or less straight away, I turn it off.

Generally though, I just set it and leave it, stopping space heating only to do DHW.

1 Like

Intresting , have you got a link to your system

Emoncms - app view

You haven’t looked before?

1 Like

I’ve looked at many :stuck_out_tongue_closed_eyes:
What is you location so I can look at a little more

Sadly, Ipswich :frowning:

My temperature sensor is in a bedroom, only place it works.

It is about 2c warmer downstairs.

It’s quite good really as I can see downstairs from the Daikin app and upstairs from this when I am at work. Just to make sure nobody at home is cold.

I forgot, I am also running in quiet mode (quietest) and have been for a week or so.

1 Like

Hi @Chris_Hill
As I see it quite a few of us have sub-optimal situations at the moment.
I happen to think it’s OK, and as @Timbones has said, it’s swings and roundabouts. After all, your heatpump may not be very efficient right now, but it is maintaining your set temperature.
This cold snap will only last a few more days and then the 2 issues ( low CoP made worse by frequent cycling) will melt away with the frost.
In the milder weather through the rest of the year we will be pleased to have the smallest possible heatpump because we will have lower energy consumption than if we had larger pumps.
But what to do for the next week?
Your idea of using the immersion heater sounds a reasonable way to avoid cycling and room heat loss during DHW cycle.
And how would it be to dial down everything by, say, 2 degrees? The house would be cooler, but if the flow was cooler too then the defrosts might be less frequent.
I see your room temperature is recorded at 21.5 where mine is around 19.5 and I’m still comfortable:-)
Cheers, David.

2 Likes

I expect the difference between measured power on the monoblocs and splits is what is included in the measurement. Maybe the pump isn’t included on the splits. for example, or maybe it’s the heating tapes. On a EDLA09 monobloc I’ve seen 828W minimum, only occasionally, and typically the minimum power is over 900W.
Otherwise, it’s errors - but the splits do seem to report lower minimum power draws.
I just think it would be odd if Daikin are using a different compressor on similar output heat pumps.

We’re at -3c outside right now and it’s been subzero since midnight.
There’s been about 12 defrosts in 10 hours.
Indoor temp has been maintained at 19c (the setpoint).
Due to the regular defrosts, it’s really tricky to determine the steady state heat output now.

I didn’t think it would frost up this much at a fairly cool indoor ambient temperature. It’s not like we’re pushing it for 21c or something.

I imagined that a steady state, ā€œlow and slowā€ would be a much more common event in the heat pump world. It seems like they have a knife edge for optimal operating conditions, at least in the UK.

I’m now wondering whether moving to an 8kw for optimal running during most of the year is right, or the extra capacity of the 11kw for the few days we get sub-zero temperatures. Makes me wonder how anyone gets the rated capacity out of the higher units in the ranges. Can the 8kw really do anything close to that? From this thread it looks questionable. I assume the 16kw can’t get anywhere near close to that either without defrosting every 10 minutes.

We have 6 independent heat sources here with 5 of them being A2A heat pumps which were doing the heating for the last 2 years quite well. Just noisily, and draftily and not in every room. So if need be, I could press some of those into service.

I’ve also been running at 60% pump speed. I’m testing today with it back to 100% to see if it changes the behaviour any (other than making additional noise). But certainly we were getting plenty of defrosts here at 60%.

This seems fine and reasonable to me. I’m watching 5 kW Vaillant do exactly the same and my oversized 11 kW Mitsubishi is defrosting almost hourly. As you say, this is only a problem for a few days each winter, and your house is still maintains the set point.

This may help a little, as it reduces power, and slows down the build-up of ice. The effect may be too subtle to see though.

Thanks!

I’ll leave the pump at 100% until tomorrow - overnight lows are forecast to be the same so I’ll have a reasonable comparison.

If the calculated heat output figures from ESPAltherma are to be believed, it was producing 9kw briefly before ramping down to about 5kw from an input power of 3.5kw down to 2kw. Flow target was roughly 40c and dt5 was being met.

I’m sorry, I don’t have the same Emon graphs you guys use.

I do not think they are the same. If you look at the circulation pumps chart, the monobloc is a lot more powerfull, for example.

I mesure total power draw with a CT clamp on the HP supply, at the consumer unit. It accounts for both the internal and the external units.

ASHP sizing for Freezing Conditions is a good read. I’m not sure what to take from it personally - still on the fence about whether to downsize from 11kw to 8kw. I do have 14kw of capacity in A2A although I’d rather not use it for heating if I don’t have to (bothersome noise, air currents etc).

Remember a small difference in required room temperatures can make a significant difference in heatlos, so a heatpump that is OK for a 50 year old who likes it cooler then many 50 year olds may not work for a 80 year old who want it wormer then other 80 year olds.

I am not convinced there is a Diakin that can safely be installed in many homes, as you can’t predict who will be living in a home a few years later.

1 Like

Buy them a supplementary kerosine heater and they can reminisce about good times.

1 Like

The difference in heatlosses is a multiple of heatloss per degree. The significance increases if the heatloss for one degree is high.

Isn’t your point of view more of a comment on poor building insulation rather than poor heat pump design?

Perhaps improving the insulation in your property will reduce the range of heat demanded at different outside temperatures.

Irrespective of the occupants, different target indoor temperatures are more easily and cheaply maintained when the insulation and air tightness is better.

With a gas boiler a modulation range of 10:1 is common and best boilers giving nearly 30:1 modulation. Some of the Daikin heatpump seem to be little better the 2:1 modulation, that leaves practically nothing to cover errors in estimating heatlose or requirements of different occupiers.

Something like this?

ā€œ * Output Central Heating: Nominal heat output range at 50/30˚C (Condensing mode)- 2.8-10.6kWā€

That’s not all that much different from my 8kW Daikin which I have recorded at mean outputs of 8.7kW over 30 mins (15C ambient) and 2.7kW over 2hrs (7C ambient).

Which boilers with comparable nominal outputs to heat pumps have modulation ranges as large as you suggest?

The issue is the smaller Diakin have the same minimal outout, likewise the 9kw have the same minimal output then 16kw. The 8kw likely have the largest modulation range.

The Vitodens 200-W have 1:17 modulation, to get above that there are high water content boilers that are uncommon in UK. The output of boiler are also mostly independent of outside temperature, so they don’t have higher minimum outout at times you want less heat.

For some reason most heatpumps seem to start a cycle at maximum outout, rather then minimal outout.

I’m really not trying to be argumentative here, but I’m not seeing the practical advantage in modulation you are suggesting.
To get a 1:17 ratio on that boiler you need to buy the 35kW model. This spec sheet shows all models in the range have the same minimum output which isn’t an order of magnitude lower than the Daikins.


Agreed, the modulation is a bit bigger on these boilers, but nothing like the difference you mention (1:17 vs 1:2)