for those seeking my views and experience here goes…
The system is a EDLA04E2V3 Atherma 4KW. I live in a three bedroom bungalow, NW England, built 1949. Part open plan with eight radiators . all radiators were replaced by Octopus to meet design spec. hot water cylinder tank was installed in the loft. installation was completed March 2024.
I had octopus back probably around September October when I started feeling cold the main issue was that there were perioda of the day … and it was usually the same periods … where it will go too hot and then too cold . felt like the system was off for an hour , three times a day. about 8 engineers come in , each one adjusted settings to different values then their colleagues. Then they gave up.
I then started reading and learning and decided that I would remove the thermostat influence and run purely off the heat curve adjusting and tuning settings over a period of several days and weeks.
where I am now is that aWD curve is set for OAT from -5 to 20C . The system runs 24/7 now but at a much reduced LWT than previously. The system no longer modulates and cycles and the unit runs 24/7 with lower temperature so less wear and tear and maintenance needed probably.
I use homeassistant to monitor the kilowatt hour usage and I brought the usage down from around 28kwh to 18kwh with OAT at zero C. So around 50% improvement naturally my monthly electricity billing payments have halved, there are no dead spots in the day, The house is more comfortable, And it doesn’t take FOUR hours in the morning to get from nighttime backstop to “normal daytime temperature”
The major takeaway for me is that octopus do not install these systems for maximum efficiency there seems to be a common design setting and customers are left with that. In my case the system was under thermostat influence the monoblock would cycle and modulate regularly, I generally was not the best way to run a pump. Additionally there’s very little competence in the engineers to understand the entire scope, dynamics of the house and the system, and to commission it accordingly for maximum efficiency. nevertheless they are polite and Octopus send out engineers in a very quick time but they just don’t have the full knowledge and training in my experience to individually customise individual customers installs. I suppose that’s a commercial decision.
I would advocate an air source heat pumps over gas boilers anytime
Set correctly for maximum efficiency and 24/7 runtime with lower LWT , tune to the ambient temperature and thermal dynamics of the property, homes can be made toasty comfortable everyday every year for far less operating cost than a gas boiler system would cost. conversely left at installation settings energy consumption is on par and can be even greater than a gas boiler and with perhaps not ideal room heating.
So I’m very happy but I had to put a lot of time and effort in tuning the weather curve over a period of days and weeks during which the house was very cold or very hot but now as I say it’s perfect. What I should have done earlier which I’ve done now is create a spreadsheet with all the values which shows tabular data and plots the WD curve lines, for the difference between the current setting and proposed new settings This allows me to fine tune for ranges of OAT and visualise the impact of tweaking X1 X2 Y1 Y2.
hope this helps