Just started looking at power monitoring, having had 12kW of solar panels since 2015. We’ve had an Apollo Gem solar diverter from the start connected to 3kW immersion water heater. As a quick and easy intro to monitoring I am trying a Shelly EM device, planning in time to move on to emon system once I have more time, as it seems somewhat more involved to set up than the Shelly app, albeit a lot more comprehensive. But I am seeing something very odd that I imagine may well have also have come up with emon users?
What I seem to observe is that when the Apollo diverter is routing full 3kW to the immersion, or zero, the readings for power used by the house are dead accurate, but when the solar diverter is routing any other amount of power to the immersion, worst case scenario half power, so 1.5kW to the immersion, the power consumed by the home appears to be over reading.
It seems to me that, roughly speaking, the power monitor thinks the diverter is delivering full power to the immersion, when it’s absolutely not. The net effect is that it reports the house is importing power from the grid, when in fact, as confirmed by import/export reading on the Apollo diverter, and also at the electricity meter itself, there is zero import/export, which of course is the intended function of the diverter.
I wonder if (a) anyone on here has come across similar behaviour affecting emon power readings with a solar diverter and (b) if anyone knows for sure what the waveform output of the Apollo Gem diverter actually is and how this may distort the power reading on the energy monitor? Monitoring is via standard CT clamps, one on the solar AC output (seems dead accurate at all times) and one on the supply to the house, after the Henley block to which the solar is connected i.e. it’s just the house consumption. This is the one that’s reading inaccurately when the diverter is in action. Also of course the Apollo has its own CT clamp on the grid/meter input.
Any emon users come across this before? (for one thing I’d like to know if the emon is immune from this error?. And can anyone throw light on waveform output of the Apollo? I can’t find it documented anywhere.
Thanks for looking.
Max
Hello @Max2 and welcome!
What hardware do you have? and when did you buy it?
It sounds like you may be running our earlier discreet sampling firmwares? These don’t work very well with PV diverters. The newer continuous monitoring firmware should give much better results.
No OEM hardware yet.
I suspect it’s your diverter. The Apollo was one of the early ones.
Winding down the power into a 3kW resistive heater is not a trivial problem.
It’s probably using a triac to turn the 240V on/off very quickly. This causes all sorts of issues, with harmonics induced into the usual 50Hz sine wave of the mains.
Have you or your neighbours noticed the lights flickering at all?
These harmonics are probably messing up the Shellys power monitoring. At the full 3kW, the immersion is “full on”, at 0kWh it’s completely off. In between all bets are off.
How are the house lead readings, when the diverter is off?
If these errors are still there, then it could be a power factor issue.
On my own system (no diverter) I am seeing up to 10% error between the measured loads, and GTI outpur. The difference being the import.
The CT driving the GTI does not sense voltage, and so is not going to compensate for power factor. Whilst he monitoring is an emonTX4, which does have voltage phase sensing, so I can rely on the readings more.
My base load is mostly capacitive from SMPSUs.
When I start adding resistive loads, the errors reduce. My assumption is, that this is watering down the power factor errors.
Might he a bit obvious, but where is your shelly device measuring the immersion power? It definitely needs to be on the input side of the diverter to have any chance of reading accurately, even then subject to harmonics re other responses.
I previously had a shelly power monitor on the input to my cheap and cheerful Solic diverter and it worked fine as does my emonpi now.
Rachel
Many thanks for replies. Yes Lee, you are correct as per my post, no Emon yet. I was just after dipping my toe in the water by a quick and easy solution with the Shelly EM prior to going down the Emon route. I thought that given the fact that just about anyone with solar PV will almost certainly have a solar diverter of some description I thought this must have come up many times, but alas a search of the group does not see this issue mentioned as far as I could see.
I have two CTs into the Shelly. One on solar PV AC out and one on the feed to the dist board after the Henley block that the solar connects to. In other words CTdist minus CTsolar = Grid export/import.
The readings are very accurate with the diverter either fully off or fully on, but anywhere in between causes large errors. TrystanLea I am borrowing a 'scope so in next couple of days I will be able to see the exact output of the Apollo unit. I’m certainly led to think by the behaviour of the readings that, as you say, it’s very simply rapidly turning the AC on/off with differing mark/space ratio. My guess is the Shelly takes short samples then uses the highest sample to get the power reading. So from what you said about the latest Emon using continuous sampling then yes, it would seem that this would make Emon largely immune to this issue? Perhaps that’s why nothing much seen on here about it.
It’s not a small error. With solar delivering excess power, and diverter delivering about 2000W (from the Apollo display), to hold import/export at Zero (confirmed by revolving disk stationary on DNO mechanical meter) the Shelly says Grid is importing 770W, so a 770W over-reading of grid import.
Anyway, for those interested once I can get a scope reading and see the actual waveform out of the Apollo (and into it… my guess it will be very similar) then I will post it here.
But I would still be interested in anyone’s comments on whether this could be an issue with solar diverters generally, although it seems there are quite a few different methods employed to achieve the same result. Perhaps the more modern units don’t tend to use this “burst” mode (if that is indeed what it turns out to be…but seems likely). Perhaps they chop the AC more like a large light dimmer so it largely preserves a more continuous AC waveform? I guess this begs another question. Would large numbers of overhead spots with light dimmers in a system potentially cause inaccuracy in power readings?
But overall I think TrystanLea may well have answered my question to a large degree in the issue being sample-length related. I think I read somewhere that Shelley uses 1 second updated instantaneous samples so that could well be the issue is my guess?
Thanks again for all inputs.
What is its rated power?