I recently installed an Axionoma heat meter to our Mitsubishi 14kw heat pump. I has been giving useful info but like many others I have suffered problems with air in the system during the hot water cycle. I tried the various methods discussed in the topic about removing air, these have given temporary relief but the issue reappears after a while.
I had a look at various devices for removing air - the gold standard appears to be vacuum degassing but these units are very expensive (c £4000) and generally only used in commercial applications. So I thought why not have a go at making one!! how hard can it be?
I took some inspiration from the spirotherm vacuum degasser - whilst very expensive it is in principle quite simple - a batch of system water is fed into a vacuum vessel - a vacuum pump then pumps out the water feeding it back into the heating system , creating a vacuum so that entrained gas in released by the lowering in pressure(Henrys law), the vessel is then refilled and the released air is purged out from the top of the vessel.
I had a self priming pump laying about which I normally use for pumping water out of our well to fill the fishpond, this type of pump is available from a well known website for about £80. It claims a suction head of 8M (-800mBar vacuum) and delivery head of 46M (4.6 Bar) so capable of pulling a reasonable low vaccum and to pump water back into the heating system at 1.5 - 2 bar.
I have a flush/fill valve set in the heating circuit , one outlet feeds a 12v solenoid valve to control the inlet of water, this feeds into a T junction on outlet feeds a vertical piece of clear tube which forms the vacuum chamber, a non return valve is fitted to the top of the tube to allow for purging out air, The outlet of the T junction feeds the inlet to the pump, the outlet of the pump feeds water back to the heating system via a non return valve and back in via the fill flush valve. All made from standard plumbing fittings.
I have a level sensor at the top of the vacuum vessel to detect when it is filled with water, this is connected to an arduino uno , which controls the solenoid inlet valve with the following sequence
- open solenoid valve
- wait till level sensor detects water then close inlet valve
- wait 6 seconds then repeat from step 1
The vacuum/water pump runs continuously, the flush/fill valves are adjusted so that the vacuum is filled at about twice the speed that the pump can empty it , in this manner when the solenoid opens the vacuum chamber fills till it is full (detected by the level sensor) , the pump then pumps away the water for 6 seconds , lowering the pressure in the vacuum chamber and releasing air from the water, after 6 seconds the inlet valve open letting in more water and the cycle repeats.
Photo Below
The contraption appears to work - and sucks out an amazing amount of air. I have used it in conjunction with a low pressure bake out (1 bar system pressure) I ran it for about an hour till the heat meter was happy even at 55 DegC - it was still pulling out air after an hour. I calculated it would take about 4 hours to process the whol system volume - expect to have to have a few sessions.
I will see if I can upload of video oof it in operation.
I have lots of ideas how to improve it.