Really?! I’m not familiar with Vaillant, controls but I would be very surprised if there’s no way to set the max temperature.

That sounds like a good plan, I’ve also disabled legionella on my Samsung heatpump since it insists on using the immersion even though R32 in my Samsung is able to get the tank to 55C. I heat to 45C daily since my tank gets a high turnover.

Everything about DHW is configurable: target temp, temp of water being added to reach target temp, timing of when to create it etc.

Except for the legionella run.

(And it’s impossible to create a schedule for creating hotter water on one day than others. Then one could create one’s own legionella run.)

1 Like

I do find it astonishing that we are still using tanks that store potable water rather than pass the incoming cold through a coil especially when the heating circuit passes through a coil instead.

2 Likes

Isn’t it a matter of heatpumps not being able to provide the necessary flow (volume per second) at the right temperature precisely when it’s requested?

Not just that, but also the number of compressor starts/stops would increase significantly. And that’s one of the primary factors determining the service life?

Unless by coil you’re referring to the immersion/resistor heating. That could work. But is wildly inefficient: COP 1.

1 Like

Nah, the suggestion here is storing hot water from the heat pump directly in the cylinder, and then having a coil that heats up potable water later on request, using the heat stored in the cylinder. I believe that phase-change thermal storage devices (e.g. Sunamp) work in a similar way.

3 Likes

Oh, wow, very interesting! That sounds indeed very interesting. Sounds like that would also diminish legionella risk!

I’m guessing it’s not yet widely deployed because of the additional complexity and/or because it’s fairly novel?

P.S.: I’d definitely appreciate a link or two to learn more about this! :nerd_face:

Water filled tanks used in this way (ie a body of non potable water with a coil passing through it containing potable water) are called thermal stores and are used in the domestic heating industry quite widely. The problem, when used with heat pumps, is that you really need either to heat the stored water at a temperature quite a lot higher than the desired dhw temp, or to have a much larger tank, to get adequate capacity.

From time to time there is discussion about this in the heat pump thread over on buildhub. With more modern heat pumps that can achieve flow temps of 70+C, and using a plate heat exchanger instead of a coil to heat the dhw, it might well be possible to make it work. Unfortunately the heat pump industry has pretty much adopted as a religion the idea that any existing DHW system needs to be thrown out and replaced with a new UVC based system. When heat pumps could only reach a flow temp of 50C or so, that was probably true. Now probably less so but the industry is a bit stuck in a rut IMHO (others may disagree).

1 Like

I think you mean store the water at a higher temp than the CH temp.

On that basis, yes an no. If the tank has good stratification, then the CH (Rads or UFH) can draw off the bottom first and work it’s way up, blending to achieve the desired flow temp.

The advantage, is the HP can be driven at its optimum flow/return temperatures as you can control the temperature of the water flowing to it, you are not trying to do this simply on the Heat Loss from the building at the time.

However, if you did mean DHW temp, then no, my thermal store gets to about 55°C and that is plenty high enough for DHW (I’m still on a boiler).

I do mean ‘hotter than the DHW temp’ (as well as hotter than the CH temp).

Suppose you want 200l of DHW at 45C with an incoming water temp of 15C (ie you have to heat up by 30C).

To do this with a DHW tank you need to store 200l at 45C, assuming perfect stratification, or less if you store it at a higher temp.

To do this with a thermal store operating at say 55C you need 600l stored, again with perfect stratification and assuming perfect heat transfer.

Thats not to say thermal stores cant work, they definitely can provided you dont need vast amounts of hot water in a short period, or can configure the system for frequent reheat. However the heat pump ‘industry’ seems to want to design systems with 200-300l hot water tanks in order that you can have several showers and run two batch simultaneously without needing to wait or reheat. I’m not condoning this, but its a fact I think driven by the modern trend to expect essentially infinite hot water at 10-15l per minute so several members of the family can shower every morning.

So thermal stores are deprecated by the ‘industry’ and I doubt you would find an MCS installer who would countenance one.

1 Like

I’m not necessarily disagreeing, but why? Because a part of the tank can cool significantly and still provide the 45°C water? I do have a big tank (long story) so it isn’t an issue, just curious on the physics.

Two basic physics principals

a) Heat will only travel from a hotter body to a cooler one (second law of thermodynamics)
b) Energy can neither be created nor destroyed (first law of thermodynamics)

Consider a storage tank with volume v which is at a temperature deltaT above another incoming body of water also of volume v. The maximum energy which can be transferred to the incoming water before the two bodies of water reach the same temperature is v c deltaT/2, at which point no more energy can transfer (c is the specific heat capacity of water, the amount of energy required to raise 1kg by 1C). This assumes complete mixing of the water in the tank, no stratification.

This energy transferred is enough to heat v litres of incoming water by deltaT/2. So you need 100l at 75 to heat 100l from 15 to 45 if you keep the storage tank completely mixed.

I think you can do a bit better than that if the stratification is ideal. I cant quite work out the complete maths (40 years ago id have written down the differential equations and solved them) but I believe it boils down to this.

Consider the situation where you have incoming water at 15C with a target outgoing temp of 45C.
Pass this through a tank with volume 100l and a thermocline (thermal gradient) from 30C at the bottom to 60C at the top. This tank can cool down to the point where its temperature is 15C at the bottom and 45C at the top, before it will stop supplying heating the incoming water to 45C. Since the tank has cooled on average by 15C it has supplied enough energy to the incoming water only to heat 50l through 30C.

Combining these two I think that the maximum energy you can extract from a tank of volume v initially at temperature T into a stream which enters at t1 and exits at t2 (so has an average temperature of (t1+t2)/2 =tavg is

v c (T-tavg)/2

The volume of water this will heat from t1 to t2 is

(v c (T-tavg/2)/(c (t2-t1))

= v (T - tavg/2)/(t1-t2)

This is a bit better than the figures above now I have (hopefully) correctly accounted for stratification, but the basic principle that you need to store more water or water at a higher temp than if you simply supply the stored water to the tap still applies.

Of course in the real world you need a little more (or higher temp) than the equation says because a perfect heat transfer doesn’t occur and/or takes too long. With a coil in a cylinder the limitation will be the rate of energy exchange once the tank temperature gets near to the incoming temperature. This can be improved by increasing the coil area but coil area detracts from tank volume so there is a limit to this (unless we invoke fractal coils which have an infinite area but occupy no volume).

1 Like

@borpin Would it possible to pull all this DWH chatter out into a separate thread at all?

It seems to have taken over this Arotherm thread a little bit and seems more generic heat pump than just Vaillant? Thanks.

1 Like

Hi all, interesting discussion! I’d suggest on demand hot water is where a phase change store wins out, since it can dispense energy to the outlet water without the associated temperature drop of a water store, so needs much less ‘spare’ energy and can be small. Perhaps also similar/same unit could replace the buffer in a HP install if you needed a buffer for space heating to keep your COP up? Also can charge the store from PV divert and direct solar water panels. No potable hot store = no legionella risk.

Bit worried about that 70C input though!

I am presently considering my next move here to get away from an older oil boiler for space/water heating. Presently have 4k PV and divert to charge the EV via an OpenEVSE unit. Also zoned radiator controls with their own thermostat schedules but so far no attempt to optimise oil use as prime target, more just avoiding the obvious waste of an old central stat and broken wax TRVs that you can never get right …!

Hi Glyn an everyone,

How did you solve it at the end? I’m in the same boat now. Last week installed DHW tank and lived in an impression that my AHSP which is Samsung HT (high temperature) Quiet 8KW pump can handle 70C with ease only to find out for some strange reason DHW tank can be set only 55C max and immersion (booster) heater is required for disinfection cycle of DHW tank! I suspect false advertisement of Samsung here. This pump disappoints me every day.

I can’t understand why I can set 70C for UHF/FCU but I can’t set more than 55C for DHW ? Also I would be fine with 55C for DHW but why booster heater is required for disinfection cycle for a god sake if pump can be set to 70C of flow temperature ?? Now I need to buy booster heater for my tank for 200 eur just to kill some legionella.

Does anyone understand this or am I missing something ?

Also one question to you guys let’s say you disable this legionella disinfection run, but as I understand the set temperature is where your probe is so if you set 48C you have this temp in the middle of the tank so at bottom there can be even 40C… This is ideal for growth or ? If you heat to 70C you have 60 at bottom which is safe.

Thanks.

With a well designed conventional DHW tank, the heatpump spend much of the time well below the target temperature as the coil is in the bottom with the colder water. Few thermal stores truly have 15c water in the bottom at the time of a recharge, most mix up the water to a common temperature as soon as the recharge starts.

But what if two Heat Geek Ministores are
ueed?

  • Connect a preheat mini store as a volumizer on the central heating loop, so it heats incoming water to something like 35c with a very high COP as it is charged to 37c most of the year.
  • Use the 2nd ministore to increase the water to 48 by charging it to 53c. (I chosen 48c as example due to many thermostat showers claining they need 48c.)
  • Why can’t the thermostat shower bland the 35c water with the 48c water so less 48c water is needed?

(Have a simple undersink small electric tank for the kitchen, likely combined with a boiling water tank, so we are not heating a long pipe to fill a pot with hot water.)

But for most people with electric cars, better to heat a tank to 60c overnight then to have to reheat a tank to 45c on daytime electricity, maximising COP does not minimize running costs…

Other then very high cost, phase change have the issue that the “charge temperature” is fixed, so can’t configure onsite for the minimal charge temperature that works for the user. None of the phase change chemicals have a good thermal connectivity when solid, so need lots of heat exchanger area to melt them.

If the water in the tank is being used up every day, there’s no risk of legionella growing.

2 Likes

Thanks for the chart. Thing is sometime the turnover is 25%, sometime 50%. It’s unlikely to have more than 75% and sometime it can be nothing. That’s why I wonder what temperature should I use and If I should install this booster heater to do 70C disinfection cycles. I think weekly disinfection would be the best for me in this case.

From the chart it looks like at 50C minimum turnover is 50% which is hard to achieve. At the other hand at 50C and no turnover legionellas seems to be dormant so low risk of growth but what’s the real temperature at the bottom of the tank ? There could be optimal temperature for growth. What role plays this ? In the middle tank i have 48C but really don’t know what temperature is at bottom.

The original observation was before the Ministores were available. Yes, I’d suggest chaining two together is probably a sound solution. The coil in my tank isn’t as efficient as I’d like so I need to heat more at a higher temperature to ensure there is DHW available especially when I have a full house. I have a relatively small volume UFH circuit and the manifold has a TRV to maintain the temp of the water flow, so as and when I go the HP route, I’ll need some form of volumeiser.

For bottom part of the tank to “cool significantly”, the part of the coil in the bottom of the tank needs to be large enough to transfer ALL the required heat when the bottom of the tank is 5c higher then required DWH temperature. (So something like 20kw heat transfer with dt of 5c.)

This needs a costly double coil in bottom of tank, then connected to a seperate costly double coil in top of tank. Both of these coils are significantly more costly then the coil in a standard heatpump dwh tank.

If a plate heat exchanger (PHE) is used, the pump needs to run at the minimal rate to transfer the heat needed for the DWH flowrate, so the buffer water existing the PHE is only 5c over the cold mains water that enters the PHE. This is a hard control problem… (Or two PHE/pumps are needed, with one using the bottom of the buffer and the 2nd using th3 top.)

As we see with the Heatgeek ministore there is also a cost premium for a low volume product made made in UK by a custom DWH tank company. But a custom PHE controller could be used with a mass macket 4 port buffer tank, and mass macket PWM pump. (Or two PHE exchangers with a digital controlled mixer to keep top PHE always at 5c over target DWH temperature.)