i Have noticed that my weather temp sensor that the weather compensation is using is reacting to the heat pump loads and starts and stops
as seen here Emoncms - app view
my question is octopus fitted a external sensor on the north side of the house (HP is on the south side ) is it possible the sensor on the north side is not active or not been setup correctly in the commissioning process.
you can see here the HP flow temps reaction to the external temp but this sensor is dramatically changing when the heat pump stops or goes in to defrost
can you see in my posts the flow temps changing with the sensor in the graphs ? and that sensor is reacting to the heat pump starting and stopping ??
my gut feeling that this is the sensor that is used for the defrost in the heat pump
yes i am getting the temp from the heat pump but this is where the sensor on the north side of house is connected to , but its the way the heat pump is reacting to the sensor i am using which is of concern , as this suggests the north side sensor is not being used
These are the two outdoors sensors provided by my Daikin(ESP Altherma), you can guess which one is the remote and yes I’ve had a lot of defrosting overnight.
Leaving aside what the heat pump is using for it’s wdc for a moment, why publish R1T which is affected by the heat pump when you have R6T which is the actual outside temperature? It seems a bit pointless?
I am not at home, but I am sure there is a setting in the MMI to tell it an external;temperature sensor is fitted?
i used to use R6T but i was seeing the heat pump was clearly not reacting to that sensor so have moved to R1T which i have seen a correlation between what the heat pump is doing and the R1T sensor
this is why i am asking what others are seeing to see if there is a setting i can change , which so far i have not specifically looked for , and was waiting to see if what i thought i was seeing is correct or or not. but after looking it appears to be using the sensor on the hp rather than the one on the north side
theres also currently 1.5 degree difference in two sensors because of the heat pump running
With a wdc, overshoot, modulation and Daikin’s inability to generally follow a requested flow temperature I would say that it is difficult to say what is influencing the flow temperature.
My outside temperature comes from OEM via a local weather station.
I would say that the actual outside temperature is most valuable to me, not what is influencing the flow temperature.
But, your heat pump’s wdc should respond to R6T if fitted together with any other influences on flow temperature.
yes i agree with you , it should but i am trying to see if that is the case ,
i did notice you have temp running in the future and thought it must be weather station data , but that seems to me as usual information unless the weather station is at you home and connected to the heat pump wdc
i am not disagreeing with you R6T should be the one i am using this is more about what my heat pump is using
i have just setup HA to record R6T and R1T and the power usage and power out put all in one place so we can see what the heat pump is reacting to mean while i will take a look through my settings to see if i can spot anything but assume its in the commissioning setting somewhere .
i will revisit this tomoz when i have the data in one place
Thers’s a setting in installer mode as to which temperature sensor should be used. I’d suggest you give the installer reference guide a read as it does hold this information, search for EBLA04-08EV3.EBLA04-08E3V3.EDLA04-08EV3.EDLA04-08E3V3_Installer reference guide_4PEN685228-1B_English
You’re looking for section 9.B “External Sensor”. I’m not sure what the Heat Pump will do if Octopus didn’t connect up the additional sensor correctly.