Daikin occasionally choosing to use Immersion for DHW

Has anyone seen their Daikin (8kW) choose to use the immersion heater to top up the hot water tank instead of using the heat pump?

Twice now over the last week our unit has done just that. The “powerful” option on the app is disabled, so I was wondering if there was an upper outside temperature that would limit operation, as on both occasions it was a warm day with external temps in the mid 20’s.

Today’s run…

https://emoncms.org/app/view?name=Stanwick_8kW&readkey=12024526facbf56b318fdfc9ab490005

Yesterday’s when it switched to immersion half way through…

https://emoncms.org/app/view?name=Stanwick_8kW&readkey=12024526facbf56b318fdfc9ab490005

Isn’t the resistive heater 3kw? So I’d expect that order of a jump.

The 2nd screenshot shows a sudden and steady 3kW electrical input which looks like an immersion heater.

Could this be a legionella cycle? What’s your DHW set point? If set the point is higher than 50C it will need to use the immersion heater, R32 heatpumps mac flow temperature is around 55C. Usually a set point around 45C is plenty hot enough.

Apart from the use of the immersion heater above 50C or 55C, depending on your model, it will also use the immersion heater if the measured outside temperature is above 25C. This frequently happens if the sun shines on the sensor, and also if the sensor is in the shadow but the sun shines on and heats the entire outside unit. I think it will also use the immersion heater if the difference between setpoint and tank temperature is below a certain threshold.

Thank you for everyone’s replies.

Yes this is the resistive heater being used instead of the heat pump starting a cycle.

Legionella cycle is disabled, set point at that time is 50C and only recently have I moved the 50C DHW cycle from overnight to mid afternoon in the thought that running it when warm outside would result in better efficiency.

@Arnold I think you have hit on the reason. External sensor was showing 24.4C at start of yesterday’s DHW cycle but the unit temperature was recording 25.5C - It is supposed to be another warm day today, I’ll see what happens at the DHW cycle then.

Oh I see it now. On my unit, the 3kw resistive element is used in conjunction with the compressor during the disinfection cycle (DHW runs at 1am), so I see a clear 3kw jump up in addition to whatever the compressor is using. Here, it seems to switch from compressor to resistive which I’ve never seen mine do. Looks like it’s an outside temp issue, more Daikin madness!

I’ve had exactly this happen once.
Immersion / legionella all disabled. Still the immersion came on.

This is a good explanation of why that happened.

Must be happening a lot more in warmer climates than ours..

Cooling fan or tiny air to air HP required to cool the main HP :joy:

I too have my legionella and immersion disabled. On my Octopus-installed system there is an electrical interconnection box near the cylinder and this box has a rocker switch that makes/breaks power to the immersion element.

The software can do what it wants, but if this switch is “off” the immersion element won’t get any power.

Look for a booster heater setting and set to ‘Restricted’,

Booster heater operation is NOT allowed except for “Disinfection function” and "Powerful domestic water heating.

Yes have that too.

I assume if that’s off and the HP is too warm then you just get no DHW, and maybe an error?

Another way could be come persistent warmer weather to move the usual 1pm DHW slot to 10pm or 4am cheap slots..

Furthermore.

Here’s how it should look.

What the MMI sees for external temp (it’s still ramping up it’s temp at this point).

The HP temp top surface.

Warmest area where the compressor etc is

Check your field codes - (not the same as the ‘breadcrumb codes’ mentioned above but accessible in the installer menu).

As mentioned above the booster heater field code 4-03 should be set to Zero (restricted). Also it pays to make sure the more obscure codes are set properly too;

8-00 = 1 min (min running time for HP doing DHW)
8-01 =75 mins (max running time for HP doing DHW)
8-02 = 1 hour (anti recycling timer)
8-03 = 60 mins (booster heater delay timer)
8-04 = 95 mins (additional running time)

6-00 = 14 (Heat pump on hysteresis)
6-01 = 0 (how close you let the HP get to HP max temp)

I’m sure that someone will say that these have no effect if 4-03 = 0 but my experience is that the installation manual has lost something in translation on these settings and so the heat pump does not always do what the manual says it should. I have arrived at the above settings by trial and error and they have worked well for me for more than 2 years without the immersion coming on - except for when the HP is out of range. (ie the flow temp is higher than HP max) or if I choose ‘powerful’. Incidentally the HP max temp varies with the outdoor temp and could be as low as 50c in mid winter and as high as 60c in summer. Clearly if you want a 65c tank temp then you will need the immersion in any event.

I should have also mentioned;

7-00 = 0 Booster heater overshoot temp
7-01 = 2 Booster heater hysteresis

Time to wake this oldish one up.

I set the Booster Heater to restricted during the summer and had no issues.

Now the ambient temperatures are dropping and we might get sub zero temperatures soon, I just wanted to check - will these settings be all right for the heat pump to be safe during the cold season?

I left the manual switch that says “Do Not Turn Off” on all the time :slight_smile:

I’m still a newbie at this - less than one whole season under my belt. All help and reassurance gratefully received.

They should be OK. I leave these settings on all the time.

Thanks for the reply.

It does make sense as they are only restricting the DHW from using the heating element.

If the heat pump needed to use water from the space heating/volumiser it still could + it could fire the heating element in dire conditions.

Hi, first post. I came across this thread as also ran into this issue. However having been through the settings I now have the situation where I am not getting DWH come on at all. I was under the impression that by changing these settings will force the HP to run instead of the Booster, but is that not the case? Current temperature is 32 degress measured on the HP. TIA

Have a look in the controller menu under Information: sensors / actuators and see what’s happening when DHW cycle should be on.

What’s the outside unit temperature reading (not the water, the actual unit itself)?

If that gets temp gets too high it will not run up, or will heat the water so far and then stop.

With this heat wave we’re getting to 41°C DHW tank temp and then no more..

It would then use the booster immersion to bring it up to 45°C at low COP.. I’ve disabled it doing that.

It’s set to 45°C and usually reports 46°C..

Have you disabled the booster heater as in my pic above? Or turned off the “Do not turn off!” switch?

Other things I had problems with were Eco DHW scheduling with Madoka control! It would not run up most times..

Going LWT only solved that problem.

Position of the unit in full sunlight could cause it not to run up these very warm days. They usually position the Unit north facing or under shade for that reason.

Could also try a DHW schedule at night (4am to 7am) if you are on Cosy tariff..

Hi, thanks for quick reply.

32 degrees was the temp both for the unit and the external thermastat. Unit is in full sun until about 2.30, then shaded by a fence. I have it on Schedule Only, to come on at 1.30, though moved it back to 2.40 when it didnt come on at 1.30 and double checked the settings.

All the actuators were showing off.

I’ve not touched any switches, just settings. I assume I have missed something? I think Colin’s suggested setting are mainly for reheat, which I don’t use.

Tank temp was at 46, with Target at 50 (comfort setting) so may be that was the issue?

I should add last night it ran to the Eco temp (45 degrees) with no issues on the Heat Pump only

Peviously yes it would run on the HP then switch to the immersion at the end if needed, but in this heat it was just running the immersion, which uses a lot of energy and does a rubbish job of heating the tank.

TBH I have found the controls on this Daikin to be rubbish and incredibly frustrating. I ended up getting Home Assistant to control the heating, and now find I can’t have hot water in hot weather.

Hi @NickSprink, by coincidence this matter came up earlier today wrt Samsung heat pumps (Samsung (gen 6) #4013 space heating OFF Temp).