Here’s an odd one. I have dhw set on “comfort” from 3am to 7am to take advantage of off peak tariffs. This morning was my first proper defrost since install in April last year and it appears to have opened the three port valve to take heat from the dhw. Tank temperature dropped from 50 to 44 degrees.
If the volume of the radiator circuit isn’t very big, it might be better to use the hot water cylinder for defrosts instead. Means hotter water to defrost the coils, and the radiators won’t drop in temperature during the defrost.
I guess this is a setting within the Daikin? I can’t find any other systems doing this, though I think I remember a Samsung unit also defrosting from DHW.
I have noticed similar behaviour (at least from the sensors), but I still used backup heater during that time and it was unclear if the ESBE valve was actually opened as the flow temp dropped so much:
I changed the logic for mine, as I was incorrectly tagging the DHW ON for defrosts to:
My recently installed Daikin is doing the same thing. Every time it does a defrost it steals hot water from the tank. So with multiple defrosts a day I never have a full tank of hot water.
Its doing it daily for me right now. Got caught short yesterday morning with not enough hot water for morning showers as the defrost stole the hot water just before we got up.
Not sure about Daikin etc, but Panasonic now have a DHW for defrost option, to avoid cold rads/fan coils to improve heating comfort, if need be. If your diverter valve is actively switching to DHW position during defrost, then it suggests it’s something along these lines - if it’s not then maybe a faulty diverter valve, or odd pipework? Maybe ask your installer if there’s a setting and/or check valve etc.
Another data point for you:
Samsung UK Tech Helpdesk tell me that for defrost heat Samsung Gen 6s use whichever heat reservoir happens to be in use when the defrost demand starts, thus (by default) DHW tank if a DHW cycle is in progress, and the emitter circuit (including any installed volumiser/buffer tank) otherwise.
So if you have a Samsung it might be wise to programme DHW cycles when defrost demands are least likely (e.g. daytime) if cooler hot water might be a problem for you (though surely a cold shower never hurt anyone… .).
I am fascinated by this chart. My Daikin 9kW also switches the 3-way valve to DHW for some defrost cycles - when the DHW temp is much higher than house/flow temps, I suspect.
However I have never noticed an appreciable drop in the DHW tank temperature due to a defrost. It’s not actually using hot water from the tank, right? It’s just circulating water through the loop that goes through the tank, so it takes out a bit of energy, but surely not much in ~5-8 minutes?
I am suspecting the same thing, as it looks like it does not happen on every defrost event.
Good point, but it did leave me short of hot water for showers one day, which is what brought it to my attention, well more specifically my wife’s attention and then mine very shortly afterwards.
On the day we noticed the behaviour, it was doing multiple defrosts that day, despite it being a mild day (~15C). Its not done it since and we have plenty of hot water for showers without having changed anything.
so it takes out a bit of energy, but surely not much in ~5-8 minutes?
I could only fit in a 180L tank into my airing cupboard and need as much heat as possible to service the showers for the day whilst not boosting during peak rate times. I lost 6 degrees during the defrost that I initially posted about which is very annoying.
Here is another example. The first hot water temp drop is a morning shower and then the second a defrost. I’ve added in the leaving water temp for reference.
I will keep an eye on defrost events with higher leaving water temps
Rather cold this morning, got down to under 2 degrees. Had two defrosts, the first took energy from the hwt. Emailed Octopus again and they replied with the following suggestions: