Hi Chris,
Welcome, I think you’ll find the forum useful.
I assume you have a 9/11/14/16kW model from the pump consumption.
The circulation pump is an electricity guzzling monster!
I doubt you can hear the pump running indoors, you will be hearing the water in the pipes at 30lpm.
The pump is outside in the heat pump.
All current Daikin monobloc models work the same way
They try to maintain the set dT between flow and return temperatures and they do this by varying the pump speed. They actually use the return temperature as the controlling part.
They aim to maintain a return temperature. If you have a flow temperature set of say 40c and a dT of 5c then the heat pump will aim to maintain a return temperature of 35c using the pump speed. The return temperature is set by the flow temperature set (either fixed lwt or wdc in your case) minus the dT requested.
If the dT is too small it will reduce the pump speed and vice versa.
The flow temperature may vary based on overshoot and modulation settings.
At the beginning of every heating cycle the pump will run at maximum speed for around 20 minutes and then ramp down over a further 10 minutes or so.
10lpm is the minimum pump speed on the 9 to 16kW models so your flow rate has reduced so that the heat pump can get to, or as close as possible to your requested return temperature.
You can adjust the maximum pump speed and set how the pump operates between cycles i using the installer settings in the MMI
I suspect you have been experiencing short cycles up until now and that is why you have not noticed a drop in pump speed, sounds like it has never made it past the first 20 minutes due to warm weather.
25c is too low for these heat pumps, they don’t like it below 30c and often not much below 35c.
It depends on the rest of your installation.
Tell us more.
These are the basics and I would suggest looking at the data on heatpumpmonitor.org to see how these heat pumps behave in detail.
I assume you have no monitoring installed?