ASHP sizing for Freezing Conditions

Thanks for the summary Trystan. I’m now convinced that the main difference in the max output we can see in the real world and the test data provided by the manufacturers is down to unrealistic (for the British climate) test standards. As mentioned at the top of this thread the standard tests are at a wet bulb dry bulb difference of -1c. This equates to a relative humidity ranging from 85% at 5c to 65% at -10c. I’ve checked the humidity data on the days Trystan has analysed in the summary immediately above - 82%, ~95% and 100%

As Trystan has pointed out, if you have a design temperature of say -10c, normal on the continent, then a rare foggy day at Zero C will still produce fairly rapid defrosts but a) your system will have a lot of spare capacity so the defrost losses will still allow your home to be heated adequately and b) the unit will not be pushing so hard for max output and c) the evaporator will be bigger and able to take more ice. So the current max output test standards should be adequate.

However when the design temperature is just below freezing, as in most of the UK and the humidity is high and freezing dawn fogs are common, then none of the above is true and the test standard will, as shown above, produce misleading max capacity figures which are not fit for a good engineer to accurately design a system with.

So should we be asking MCS and BS to come up with more suitable standards? Max output at 100% RH at Zero C would be my suggestion??

If you are a numbers person like me then you will see how important water content is in the data below (from Psychometric chart data)

gH20/KgAir DB-WB=1c gH20/KgAir Dew Point Spec Vol
Temp C 100% RH %RH at this RH at this RH Temp-DP m3/Kg
5 5.40 86.5% 4.67 2.9 2.1 0.79
4 5.03 85.7% 4.31 1.8 2.2 0.79
3 4.68 84.9% 3.97 0.7 2.3 0.79
2 4.36 84.0% 3.66 -0.4 2.4 0.78
1 4.06 83.1% 3.37 -1.4 2.4 0.78
0 3.77 81.2% 3.06 -2.5 2.5 0.78
-1 3.47 80.1% 2.78 -3.6 2.6 0.77
-2 3.19 78.9% 2.52 -4.8 2.8 0.77
-3 2.93 77.5% 2.27 -6 3 0.77
-4 2.69 76.1% 2.05 -7.2 3.2 0.77
-5 2.47 74.6% 1.84 -8.4 3.4 0.76
-6 2.26 72.9% 1.65 -9.6 3.6 0.76
-7 2.08 71.1% 1.48 -10.9 3.9 0.76
-8 1.91 69.1% 1.32 -12.2 4.2 0.75
-9 1.75 67.0% 1.17 -13.5 4.5 0.75
-10 1.59 64.7% 1.03 -14.8 4.8 0.75

At max output my Daikin runs with the evaporator about 6.5c below ambient. At half load it is 4 below ambient. At -10c the little moisture in the air will mostly stay in the air as the dewpoint is -14.8c - under test conditions. Whereas at zero c there is more water to freeze out and the foggy day freezeout could be more than 1.5g/kg.