Ok, it’s not as simple as that… some days we may only use part of our Altherma 250l tank, others more so.
Below is the last 3 days. Schedule heats the tank at 1am for as long as it takes, no reheat.
Starting on the left, Tuesday morning, the tank was 33ish, just under an hour to bring it back to 50c and 7kWh of produced heat.
As it was mild, and space heating wasn’t running, I manually ran a hot water cycle that same evening. Another just shy of an hour run and around 5kWh of heat produced.
The next day, Wednesday, the hot water seemed to run out earlier than usual.
Thursday morning a full reheat from cold to 50c, about 90 minutes and 11kWh produced heat.
We’ve had three showers today and you can just make out their blips in the line for Thursday. Barely any impact on tank temperature.
Yesterday it was three showers as well, but there just didn’t seem the same amount of hot water to go around.
I don’t have any evidence to suggest this but it feels like when the tank reports, say, 45c, everything below the sensor point (a good 2/3 of the tank as I understand it) could be 15c or whatever the incoming cold water temp is. During the 1am reheat, it doesn’t take long for the warmer water around the sensor to reach 50c leaving everything below it some way below that point. Result is a tank which didn’t fully heat, presumably, since the hot water doesn’t go as far.
If the sensor temp is much lower before the 1am reheat, like 30c or something, we tend to get a full tank for the next day.
Does anyone else recognise this sort of thing?