Which SCT-013? There are many variants. Only the SCT-013-000 is directly suitable for use with the emonTx.
SCT-013-000 and SCT-013-000V are NOT the same, if you have the -000V that would almost explain your problem. The SCT-013-000 has a 50 mA output at 100 A, the SCT-013-000V has a 1 V output.
Can I check? Your supply is 230 V measured line - neutral, and 400 V measured line - line.
And you have the “Ideal Power” 77DE-06-09-MI a.c. adapter, plugged in at a 230 V socket?
Have you set up the c.t’s on the correct cables? If the “phase rotation” is wrong, then the values you read will be wrong by exactly ½. The instructions for setting up and calibration are in the “User Doc”.
Before you spend money, if you have a multimeter, take a c.t. from its cable, disconnect it from the emonTx and measure the resistance between tip and sleeve. You should read about 100 Ω if it is a SCT-013-000, or about 20 Ω if it is a SCT-013-000V.
If it is the SCT-013-000V, you can (if your electronics skills are good) remove 3 resistors in each emonTx to convert it and make it suitable.