It could be a couple of things in my experience with the 9/11/14/16 variant of the Daikin Altherma 3M:
-
If outside air temperature at or below ~6C, then regardless of Space Heating mode (on/off), then then pump will run (compressor off) to circulate warm water to outside to prevent freezing
-
If outside air temperature at or below ~6C, then if you have
Antifrost
still enabled (think it’s a default and I turned mine off), then regardless of Space Heating mode (on/off), then not only will the pump run, but the compressor will run a lowest frequency for a short-ish period to get water temperature up to a failsafe level
In all cases including the above, the following pump control configuration should be looked at, with “Sample rather than Continuous” and “60% limitation on Sampling” modes strongly advised: