Valiant Arotherm HeatPump 12KW

Hi all, Hoping for some guidance, I am a relative novice with heatpump and got the Valiant Arotherm installed last year. We live in a Victorian terrace in London with 4 beds and 2 baths, with a UFH downstairs (suspended floor) and radiators upstairs. We have 2 zones, downstairs is the UFH which has its own manifold and pump and controlled by the heatmiser thermostat. Upstairs rads have the sensocomfort. The Heating curve is set to 0.5 for both zones on pure Weather Compensation, in the MyValiant App, the UFH zone has marked as manual and set to 25 degrees with the HeatMiser controlling the demand for heat, the upstairs radiators are on between 4 am to 10 pm at 20 degrees and 19 degrees for setback. Although the upstairs temp never quite reaches 20 degrees (its stuck between 18.5 and 19), the heatpump is cycling at least once per hour, which seems a little strange especially as the upstairs temp is never quite reached. All Rads upstairs are open but there are rads downstairs which are permeantly switched off (otherwise it renders the UFH pointless)

I have tried experiemented with higher curve settings, lower curve settings but to no avail. I have been reading on here about the difference between Flow Temp and Return temp (and it seems to be about 2 - 3 degrees). I tried to change the flow rate to a bit lower but although the difference between flow and return seemed to increase to about 4 degrees the outcome seems to be the same. Would appreciate some guidance, I unfortunately do not have any open energy monitors to show the graph of what is happening.

Hello @JasonLee what is controlling the call for heat for upstairs? Is the issue that the call for heat is only being driven by the downstairs UFH zone?

Set the UFH Heatmiser permanently to 30C (or its highest desired temp setting) to effectively bypass it and run the whole house as a single zone. Open the UFH mixing valve fully. Set the UFH pump speed to its lowest setting. Get rid of the overnight setback schedule.

See how the house behaves in cold weather. If upstairs is still cooler than you’d like relative to the UFH zone, then balance the UFH loops to reduce UFH output relative to the upstairs rads and increase the heat curve setting. Give the house time to react, rinse and repeat until all rooms are behaving how you’d like them to.

…But my assumption would be that your 12kW Arotherm Plus, with a minimum heat output of ~4kW, is massively oversized, and you’ll be experiencing cycling most of the time, regardless of what you do. This in itself isn’t much of an issue with the Vaillants, as they use a degree-minutes control algorithm which precludes short-cycling. Focus on getting your system balanced, working as a single zone, and your heat curve dialled in over winter, to achieve comfort, then forget about it and let it do its thing.