Vaillant pump settings changed by Heat Geek
Hi All,
So I got a unsolicited call from a Heat Geek (my system was installed by heat geek) saying they have been looking at monitored systems and I was on the call list for some small changes.
My system is a valiant arotherm plus 7kW.
They got me to change my DHW.build.pump to 50% (previously 100%)
and heat.build.pump to 50% (previously auto)
Just wanted to run this by the community here to see if this is a sensible change. As I was under the impression move flow = better.
Cheers
James
More flow is not always better, you want the correct flow rate. Do you have monitoring?
This change seems reasonable, I’m sure Heat Geek have good a lot of data behind this change.
Hey Glyn,
I do have monitoring.
What date was this change made?
Today! 4PM so not much data to work with yet
Glyn, under what circumstances is more flow not better?
Auto sets the flow rate to a fixed value dependent on the output rating of the outdoor unit. 50% is invariably lower than that flow, requiring a higher flow temperature to provide the heating power needed.
James, I’d question Heat Geek and have them explain the rationale for changing the setting. It’s worth noting that HG use the built-in monitoring that Vaillant heat pumps provide, which is often wrong as the two temperature sensors (flow and return) aren’t matched at the factory. That’s easy to fix though.
I’ve just emailed them asking them to explain the change. Will update when I hear back.
I guess you need to get the water hot enough to allow the radiators to emit the heat into the room. A higher flow rate means lower temperatures for a given amount of heat.
Though I guess if the heat isn’t emitted into the room, the water temperature will continue to rise until it can be emitted. In which case you’re just wasting pump energy pushing the water around faster than necessary?
I changed both those settings to 60% last winter (after along discussion with Claude and looking at my emoncms data and individual rad deltaTs - seems to have worked well. Maybe I’ll tweat to 50% to try
From a heat perspective a radiator’s heat output is determined pretty much by the average temperature between flow and return.
A heat pump running with a Delta T of 8 degrees might have Flow of 44C, return of 36C for an average radiator temperature of 40C.
Double the flow, halves the Delta T to 4 degrees, the equivalent is Flow of 42C, return of 38C for an identical average radiator temperature of 40C.
Those two system will produce the same amount of heat at the heat pump, transfer the same amount of heat through the pipes and emit the same heat from the radiators, but because system two does it at a flow temperature 2 degrees lower it is slightly more “efficient”. More flow => better so far.
However increasing the flow rate requires more power to the water pump. Its not a linear relationship either, doubling flow rate will need more than double the power. Some of the larger water pumps can consume up to 200w at full throttle. This is why “efficiency” was in quotes, the power consumed by the water pump is a factor in total system COP.
The second reason is noise, at some point a flow rate will become noisy. More flow is certainly not better in this regard.
I personally run a 6kW Daikin system that targets as low a flow rate as possible. Without knowing anything about @James_G system my gut feel is that Heat Geek’s suggestion is sensible for both of the reasons above.
The Vaillant controller auto flow rate targets the badged heat output of the outdoor unit with a difference between flow and return temperature of 5 K, just for info (and that flow rate is “100%”).
If the target flow rate is too low the water can’t take away the heat being delivered by the compressor even at its minimum speed, and the heat pump will shut down and thereafter do (genuine) short-cycling. That’s a near certainty with a heating circulation target of 50%.
I really can’t see any reason for ever using something other than auto for dhw. There shouldn’t be any problems of resistance or noise pushing water through a tank coil!
Hi All, I got a reply from Heat Geek,
For context my question was:
I’m interested in understanding the scientific rationale behind the changes.
My previous understanding was that higher flow rates generally improve heat transfer and can allow the heat pump to operate at lower flow temperatures, improving COP. So I’m curious about the mechanism by which reducing flow rates would be beneficial in this case.
Is the improvement primarily from reduced pump electricity consumption, or does changing the flow rate also improve the heat pump’s thermodynamic efficiency, perhaps through changes in flow/return temperature differential or heat exchanger performance?
I’d also be interested to know why 50% was selected for both pumps, particularly given my 110L Heat Geek Mini Store, and whether there’s any potential trade-off in DHW recovery times or heating performance.
Specifically, how does reducing the building pump speed from Auto to 50%, and the DHW pump from 100% to 50%, physically improve the system’s efficiency?
Heat Geek’s response:
Where your understanding does hold
At design conditions, higher flow rate narrows the dT across the emitters, which raises their mean water temperature for a given flow temperature and gets more output out of them. That is real, and it is why flow rate matters when the system is working hard on the coldest day of the year.
Why it inverts for the rest of the year
Your system spends almost all of its hours at part load. Once the weather compensation curve has dropped the flow temperature, the emitters are hugely oversized relative to the demand in the room, so emitter-side heat transfer stops being the limiting factor. Nothing is gained by pushing more water through them. What changes is:
  1. Pump electricity. Our efficiency figure is heat delivered divided by total electrical input, including the circulation pump, not just the compressor. A pump running at Auto is continuously consuming power and that load is present every hour of the heating season. Pump power scales roughly with the cube of speed, so halving the speed drops the consumption dramatically. That lands straight on the bottom line of overall efficiency.
  2. Control stability. At low load with a very high flow rate, the dT across the heat pump collapses to a degree or two. The unit then has very little temperature signal to modulate against, and it tends to sit at minimum compressor speed and cycle rather than running long and steady. Widening the dT by slowing the pump gives the unit something to work with, so it modulates down properly and runs longer, lower cycles. Long steady cycles are consistently more efficient than frequent short ones.
  3. A secondary thermodynamic gain. The flow temperature is set by the compensation curve and does not change, but a wider dT means a colder return. That lowers the average water temperature the refrigerant has to condense against, which lowers condensing pressure and therefore lift. The gain here is smaller than the two points above, but it is in the same direction rather than against them.
The hot water pump
Different mechanism again. During a cylinder charge you want the return to the heat pump to stay as cold as possible for as long as possible, because the compressor only has to work as hard as the water coming back at it. Blasting the circuit at 100 percent mixes the store and shortens the time the return stays cold, so the unit is pushed up to high condensing temperatures earlier in the charge. On a small, deliberately stratified store like the MiniStore that effect is amplified, because there is not much volume to play with and stratification is doing a lot of the work.
There is a genuine trade-off here, and you are right to look for it. Slowing the secondary-side flow does reduce the heat transfer coefficient at the coil, which increases the approach temperature needed. The point of a setting like 50 percent is that it stays on the right side of that curve: still enough velocity to keep the coil performing, but wide enough dT to protect stratification and keep the return cold through most of the charge.
Why 50 percent
It is a starting point drawn from monitored performance across a large installed base rather than a figure calculated uniquely for your property. We then validate it against your own monitoring data over the following weeks and adjust if the data says otherwise. That is the whole point of monitoring every system. Obviously if you experiance any flow faults you can increase this by 5% increments to lift your system away from the flow faults.
On recovery time
Expect a modest extension, in the order of minutes on a 110L store, not a meaningful change to availability. If you notice hot water running short or any room falling away, tell us and we will revisit the setting rather than leave it. Your comfort guarantee of the designed temperature in every heated room, and the minimum overall efficiency guarantee including hot water, both stand regardless. If the system does not reach the guaranteed figure, we come back and upgrade it at our cost until it does.
Hi Dan,
Are you saying the heating pump setting should be set to Auto?
and DHW 100%?
Cheers
James
My very first thought is that the built-in monitoring on Vaillants isn’t accurate enough to use for tuning a system, unless you get lucky and both the flow and return temperature sensors read the same when the temperature of the water they’re sensing is the same. Depending on which way I swapped the sensors I had a COP of 2 or 5. Once I had a matching pair of sensors I have a SCoP of 3.1.
I don’t really get HG’s comments around the Mini Store (I have one too). Supply of heat while drawing hot water and reheat time trump everything in my humble opinion, unless you’re on your own or have a very underestimated family! “Keeping the pump cold for longer” means exactly that, cold ‘hot’ water for longer. Sure, that flatters the CoP, but that’s not the goal.
The heating side I’m going to have a think about, but HG don’t set up their systems correctly – they do the opposite of what Vaillant intend. Vaillant recommend using the ‘Expanded’ setting for ‘Room temperature mode’. My HG wanted Inactive and iirc that does leave the circulation pump running all the time the outside temperature is below the ‘Outdoor temperature switch-off threshold’, which may explain the sentence “A pump running at Auto is continuously consuming power and that load is present every hour of the heating season”; right diagnosis, wrong solution!
If you go to ‘usage’ in the Vaillant app and select Year, what’s the ‘energy efficiency’ number?
Running in ‘Expanded’ during the heating season is a cop-out (excuse the pun), and I believe only recommended by Vaillant to absolve them of support calls.
‘Expanded’ mode can effectively mask a grossly misconfigured weather comp curve, which can be set much higher than the dwelling requires, causing excessively high flow temperatures (with the associated poor efficiency), but masked by short cycle times as the ASHP is shut off by the ‘Expanded’ mode once the room controller senses the setpoint temperature has been reached. The room temperature then drops below the setpoint, the ASHP fires up, belts along at an unsuitably high flow temp, then shuts off again. Rinse and repeat.
You could end up only ever running the ASHP at wildly excessive flow temperatures, and be none the wiser, as the room temps will remain around the set point. This is exactly how the Electrification of Heat study ended up with an average SCoP of 2.8 across thousands of installs… Misconfigured systems running at excessive flow temperatures, cycling and masking the poor configuration.
That is true, same as using 3rd party thermostats. But does it cause short cycles - most likely not, less than optimal cycle length for a good overall CoP maybe.
But the effect also depends on your heating system radiators or UFH. It’s generally pretty bad for radiator systems, maybe not so bad for UFH which use lower flow temperature especially if well insulated. I can in theory run at 10 degs outside at a flow temp of 24 degs, but reality ASHP restart hysterisis doesn’t allow it, as floor would need to below 19 degs to get a restart permission - floor is never that cool ever in the heating season. So I run a hybrid of thermostat control that merges into WC when it’s cold enough. Run at start WC of 29 degs flow, this ensures prompt restart when I want it and continuous ASHP running for the 3 to 4 hours to charge the floor and the thermostat 0.2 Deg hysterisis to be satisfied, and generally get a CoP high 5s to mid 6 while running. Once the outside temp start to average around zero the heat pump starts to run close to 24/7.
In the Vaillant “Installation and maintenance instructions 0020330791_03”, page 46, the maximum flow rate is given as 860 l/h. This morning, out of curiosity, I changed my Conf. heat. build. pump. 75% from Auto and the flow rate… went up from 860 to 900 l/h. I’ve changed it again to 60% but it won’t be cold enough to run the heating again until tomorrow.
I didn’t want to put too much into one post but I also recommend using the adaptive heat curve to let the controller find what’s needed. I set my heat curve to 0.4 last year and the heat pump bumped it all the way up to 0.75. That was just right – when I had been running 0.6, as a manual selection, the house was cooling down on the coldest mornings.
What surprises me is that the Vaillant UK guidance recommends against auto adapt, saying “UK weather is too variable”, which is obviously nonsense. German weather is much more variable!
It’s been over a month now. Changing Conf. heat. build. pump. to 60% didn’t change performance as far as I can see (maybe there’s a signal but there’s too much noise from different temperatures outside, sunshine levels etc.)
Auto adapt has put the heat curve up to 0.8 from 0.4 (I reset it), after we had one of the coldest November nights for years. In the past when I would manually set the heat curve to 0.5 or 0.6 the house would fall below target temperature early on cold mornings. Auto adapt can be set up by going into the SensoComfort’s menu, Settings, Installer level, 00, Installation configuration, Installation, set Adaptive heat curve to Activated. You’ll also need Settings, Installer level, 00, Installation configuration, Circuit 1, set Room temp. mod. to Expanded. “Expanded” is a prerequisite for auto adapt and also prevents over-heating when heat from occupants, cooking, sunshine etc is sufficient to keep the house at target temperature; maybe not something that happens in large old houses with high heat losses, but is common in smaller modern homes.
Interestingly Heat Geek are now bothering me for remote access to my heat pump. I’ve not had any contact from Heat Geek directly, just this. Unless I hear a good reason for allowing access I’ll deny the request.
Dan, I had a request from my installer a couple of weeks ago, I’ve allowed access, but emailed them to say, if you want to change any setting, email me first.
Russ.