Hi All, I got a reply from Heat Geek,
For context my question was:
I’m interested in understanding the scientific rationale behind the changes.
My previous understanding was that higher flow rates generally improve heat transfer and can allow the heat pump to operate at lower flow temperatures, improving COP. So I’m curious about the mechanism by which reducing flow rates would be beneficial in this case.
Is the improvement primarily from reduced pump electricity consumption, or does changing the flow rate also improve the heat pump’s thermodynamic efficiency, perhaps through changes in flow/return temperature differential or heat exchanger performance?
I’d also be interested to know why 50% was selected for both pumps, particularly given my 110L Heat Geek Mini Store, and whether there’s any potential trade-off in DHW recovery times or heating performance.
Specifically, how does reducing the building pump speed from Auto to 50%, and the DHW pump from 100% to 50%, physically improve the system’s efficiency?
Heat Geek’s response:
Where your understanding does hold
At design conditions, higher flow rate narrows the dT across the emitters, which raises their mean water temperature for a given flow temperature and gets more output out of them. That is real, and it is why flow rate matters when the system is working hard on the coldest day of the year.
Why it inverts for the rest of the year
Your system spends almost all of its hours at part load. Once the weather compensation curve has dropped the flow temperature, the emitters are hugely oversized relative to the demand in the room, so emitter-side heat transfer stops being the limiting factor. Nothing is gained by pushing more water through them. What changes is:
-
Pump electricity. Our efficiency figure is heat delivered divided by total electrical input, including the circulation pump, not just the compressor. A pump running at Auto is continuously consuming power and that load is present every hour of the heating season. Pump power scales roughly with the cube of speed, so halving the speed drops the consumption dramatically. That lands straight on the bottom line of overall efficiency.
-
Control stability. At low load with a very high flow rate, the dT across the heat pump collapses to a degree or two. The unit then has very little temperature signal to modulate against, and it tends to sit at minimum compressor speed and cycle rather than running long and steady. Widening the dT by slowing the pump gives the unit something to work with, so it modulates down properly and runs longer, lower cycles. Long steady cycles are consistently more efficient than frequent short ones.
-
A secondary thermodynamic gain. The flow temperature is set by the compensation curve and does not change, but a wider dT means a colder return. That lowers the average water temperature the refrigerant has to condense against, which lowers condensing pressure and therefore lift. The gain here is smaller than the two points above, but it is in the same direction rather than against them.
The hot water pump
Different mechanism again. During a cylinder charge you want the return to the heat pump to stay as cold as possible for as long as possible, because the compressor only has to work as hard as the water coming back at it. Blasting the circuit at 100 percent mixes the store and shortens the time the return stays cold, so the unit is pushed up to high condensing temperatures earlier in the charge. On a small, deliberately stratified store like the MiniStore that effect is amplified, because there is not much volume to play with and stratification is doing a lot of the work.
There is a genuine trade-off here, and you are right to look for it. Slowing the secondary-side flow does reduce the heat transfer coefficient at the coil, which increases the approach temperature needed. The point of a setting like 50 percent is that it stays on the right side of that curve: still enough velocity to keep the coil performing, but wide enough dT to protect stratification and keep the return cold through most of the charge.
Why 50 percent
It is a starting point drawn from monitored performance across a large installed base rather than a figure calculated uniquely for your property. We then validate it against your own monitoring data over the following weeks and adjust if the data says otherwise. That is the whole point of monitoring every system. Obviously if you experiance any flow faults you can increase this by 5% increments to lift your system away from the flow faults.
On recovery time
Expect a modest extension, in the order of minutes on a 110L store, not a meaningful change to availability. If you notice hot water running short or any room falling away, tell us and we will revisit the setting rather than leave it. Your comfort guarantee of the designed temperature in every heated room, and the minimum overall efficiency guarantee including hot water, both stand regardless. If the system does not reach the guaranteed figure, we come back and upgrade it at our cost until it does.