5kW Vaillant
System ID | OutsideT | Peak FlowT | Mean FlowT | Flow rate | Peak elec | Mean elec | Peak output | Mean output | Datasheet | Missing W | Missing | Cycles | Dashboard link |
---|---|---|---|---|---|---|---|---|---|---|---|---|---|
308 | -2.8 | 36.3 | 33.8 | 14.022 | 2403 | 2016 | 6877 | 5169 | 6800 | 1631 | 24% | 3 | Emoncms - app view |
308 | 0.1 | 36.5 | 34.6 | 14.028 | 2422 | 2016 | 6934 | 5365 | 6900 | 1535 | 22% | 2 | Emoncms - app view |
308 | -5.5 | 34.1 | 32.4 | 14.02 | 2289 | 1976 | 5973 | 4731 | 6300 | 1569 | 25% | 4 | Emoncms - app view |
308 | 0.2 | 35.7 | 32.5 | 14 | 2410 | 1888 | 7370 | 5094 | 6900 | 1806 | 26% | 6 | Emoncms - app view |
433 | -2.9 | 32.8 | 30.1 | 14.416 | 2310 | 1809 | 7269 | 5062 | 6800 | 1738 | 26% | 4 | Emoncms - app view |
286 | -6.3 | 40.6 | 38.6 | 12.459 | 2440 | 2121 | 6184 | 4925 | 6000 | 1075 | 18% | 4 | Emoncms - app view |
286 | -2.3 | 40.1 | 37.6 | 12.485 | 2442 | 1993 | 6816 | 4840 | 6400 | 1560 | 24% | 4 | Emoncms - app view |
286 | -3.8 | 41.1 | 39.1 | 12.405 | 2479 | 2107 | 6338 | 4886 | 6200 | 1314 | 21% | 5 | Emoncms - app view |
286 | -3.2 | 41.1 | 39.2 | 12.414 | 2479 | 2110 | 6290 | 4899 | 6400 | 1501 | 23% | 3 | Emoncms - app view |
390 | -0.9 | 40.5 | 38.4 | 14.802 | 2493 | 2048 | 7430 | 4917 | 6500 | 1583 | 24% | 4 | Emoncms - app view |
75 | -0.3 | 46.2 | 42.4 | 14.582 | 2766 | 2217 | 7214 | 5141 | 6600 | 1459 | 22% | 5 | Emoncms - app view |
Looks like you can typically expect 5 kW from the 5kW Arotherm, though it’s probably worth avoiding getting too close to that when sizing based on accurate heat loss.
On average the 5kW is closer to the datasheet than the 7kW - but only marginally so, an average under-capacity of 23% rather than 27%.
10 kW Vaillant
System ID | OutsideT | Peak FlowT | Mean FlowT | Flow rate | Peak elec | Mean elec | Peak output | Mean output | Datasheet | Missing W | Missing | Cycles | Dashboard link |
---|---|---|---|---|---|---|---|---|---|---|---|---|---|
140 | -6.7 | 39 | 36.3 | 28.777 | 4285 | 3505 | 12800 | 9139 | 9800 | 661 | 7% | 4 | Emoncms - app view |
2.3 | 36.9 | 33.4 | 27.772 | 3954 | 3452 | 13172 | 10179 | 12800 | 2621 | 20% | 7 | Emoncms - app view | |
-5.3 | 34.6 | 32.9 | 27.373 | 3703 | 3307 | 11475 | 8908 | 9900 | 992 | 10% | 2 | Emoncms - app view | |
-0.9 | 37.2 | 34.7 | 25.593 | 3982 | 3510 | 12637 | 9769 | 11000 | 1231 | 11% | 2 | Emoncms - app view | |
-0.3 | 38.4 | 36.6 | 26.29 | 4091 | 3714 | 12613 | 10652 | 11000 | 348 | 3% | 3 | Emoncms - app view |
The 10 kW Vaillant seems to be closest to the datasheet so far, with the cycles above only 11% below datasheet capacity on average.
I’ve added all these figures to @glyn.hudson original spreadsheet as a new tab: