I opened up my 10 kW aroTherm plus today to look at the temperature sensors. The top sensor (red wires - is that flow or return?) indeed had the insulation stuck partially below it. I freed the stuck insulation and applied some thermal grease on both sensors, then fixated the surrounding insulation with some electrical tape. Unfortunately this has only marginally improved the situation, as evidenced by the graphs below during a DHW run followed by a short cooling run where I mainly wanted to get to a “compressor off/flow pump on” situation to see whethe flow & return converge to the same temperature. Return measures almost the same as my own sensor (+0.2 °C), flow measures significantly higher (+1°C), leaving me with a 0.8 K dT during this compressor idle phase. During the DHW run, the Vaillant sensor measures +1.4 K so there seems some other effect at play there. The different temperature offsets between DHW and heating were there before; and they translate to different errors for DHW COP and heating/cooling COP. As I also saw some environmental temperature influence before, it might be a combination of effects: Sensor calibration/nonlinearity issues, internal heating of the heat pump housing during operation and external environmental heating of the heat pump housing on top. All in all I think I need to get my flow (edit: flow temperature) sensor replaced - which ones of the two is that?