gjones84
(gjones84)
29 October 2021 08:39
2
Hi,
I remeber having touble doing this.
In the end i enable modbus tcp in my CCGX and wrote via modbus. I have posted a while back how to do this. Need to add some code to your emonhub config file. Set the IP address and you should be away
Cheers
Gareth
HI all,
For those who have a CCGX connected to a multiplus/quattro and want to read registers via Modbus TCP and import them to the inputs page of emoncms. I have worked out the code that is required for the config file in the interfacers section of the emonhub.
As @James_Hill mentioned the unit ID must be included as there is multiple unit ID’s/slaves on the Victron VE Bus system. See below.
[image]
I wanted the SOC and charge/discharger power feed for the My Solar & Battery app.
[[Modbus…