toadhall
(Alun Hawkins)
15 September 2026 14:03
28
Should have thought of this earlier. You could possibly avoid the problem by moving the B19 next to the control unit and make the 20m of Modbus cable redundant. See …
Hello @Sykes , and welcome to the pit .
In your MIM-E03 controller (may be within the Indoor Unit if you have one, or a standalone box if you don’t), you’ll see the controller circuit board which contains a 6-terminal block labelled F1-F2-V1-V2-F3-F4:
F1/F2 are used for serial communication with the Outdoor Unit
V1 is a 12V DC supply
V2 is digital ground
F3/F4 are used for serial communication with the Remote Controller (MWR-WW10N)
Here’s a photo showing my (gold colour…