Hi @PastGasman and welcome to the forum.

This may just confuse you further but have a look at Just a thought on bigger buffer tanks (including the links referenced from it).

and

I suspect that this is not unusual. The table Samsung publishes for my 8kW HTQ series ASHP shows that energy output is 8kW (or more) over a wide range of ambient temps and LWTs, and the only area where I’d get <8kW is at very cold ambient conditions (below -20degC). What does change significantly is the energy input to the compressor, hence the variety of CoP values.