In the quest of reaching the higher CoPs, and to better harness the inertia of my under floor heating, I made an experiment last night.
FSV 2093 = 1, WL min = 40
No cycling, although the CoP is not the best it averages around 4.1.
So clearly yes, the 2093 setting has a real fat impact on how to avoid cycles. I just added an automation to stop the zone 1 heating when ambient temperature raises of 0.2 (to try to cope with the high inertia of the underfloor heating).
Cheers,
fsv 2093 can be 1 or 2 or 3 or 4:
Samsung documentation (DB68-08470A-15_IB_EHS_Wired_Remote-Control_Kit1_EU_Boook_EN_231117-D01 page 29/60) says:
Remote controller room temperature control
••Control by room temperature sensor (Service mode)
‒‒ If set to #2093 1, the compressor can be turned on or off only by Room temp sensor.
‒‒ If set to #2093 2~4, the compressor can be turned on or off by Room Temp. sensor or according to the
WL discharged water temperature.
(#2093 2, WL Thermo off → Water pump off, #2093 3, WL Thermo off → Water pump on, #2093 4,
WL Thermo off → Water pump 7min off → 3min on →.......).
I’ve tried many of the values, I could also tries the 3 and 4 and make graphs, but I’m not sure the water pump schedule wouldn’t change much.
Actually they both are set to 0. I just checked to be sure.
I’m not using the MWR remote neither but I wished to rely on 2 different water laws for ufh and fcu, and more importantly I didn’t want to install more wires to control both zones!
Hope that’s helpful.
Cheers