Samsung MIM-C02N S-NET Pro Dongle

Hi Glyn.

  1. Do I recall you mentioning the MIM-C02N for ASHP monitoring (but dismissing it as not very helpful except for initial commissioning)? It’s expensive (£200 from Midsummer) but looking at the manual it looks like it might be useful to understand some of the Samsung controller algoithms.

  2. Ref Quiet Mode. Samsung sent me the following table:
    image003
    I infer from this that this mode will reduce the compressor speed to about 60% of nameplate when the default (low-noise) option is enabled. (The other levels require access to the outdoor unit circuit board to select.)

  3. I tried Quiet Mode on DHW and it does indeed use less peak power, but it does so for longer (same number of kJ required for tank heating, so no overall power saving).

Sarah

1 Like

Sorry, if I’ve caused confusion moving this to a new topic, I just thought that discussing MIM-C02N merits its own topic.

The Samsung S-Net Pro Dongle MIM-CO2N allows your to connect a Samsung heat pump to a Windows PC running Samsung S-net software.

This S-Net software shows all the diagnostic sensor info from the HP and allows the FSVs to be adjusted. It also allows the firmware of the outdoor and indoor units to be updated. Here are some screenshots:


While it’s nice to be able to see all this extra info, the logging and graphing tools on S-net are very limited compared to OpenEnergyMonitor Emoncms, although I am biased! :slight_smile:

I’ve found the MIM-CO2N is mostly useful for checking FW versions and updating FW. Also for sending data logs to Samsung technical if a unit has any issues.


In terms of monitoring the system and understanding performance, the MIM-B19N Samsung Mobus interface is more useful, EmonHub supports reading from the MIM-B19N via a modbus adaptor to get the data into Emoncms where it can be data logged and put into the Emoncms MyHeatPump graph

However, the MIM-B19N only reads data from the onboard sensors, which I’ve found to not be very accurate, for independent accurate billing grade COP calculation the Level 3 HP Monitoring Bundle is the best option.

There should be some efficiency gains since heat transfer via the coil will be more efficient at lower power, although the trade-off vs re-heat time may not be worthwhile. Here’s an excellent blog by @Zarch where he looks at the effect of lowering the power during DHW, he’s got a Vaillant Arotherm and a Mixergy, but the physics of heat transfer will be the same for Samsung!

2 Likes

Thanks Glyn, useful data.

But with my winter mean total household energy consumption of 22kWh/day (about £6/day) it’s hard to justify spending much on monitoring equipment… :face_with_diagonal_mouth:

Sarah

I was wondering how you did it! have samsung tech given you any meaningful info about different firmware version behaviours?

No, apparently the UK Samsung technical don’t get to see any FW change logs themselves :roll_eyes:

I have a AE050RXYDEG-EU heat pump.

All I know is that updating my indoor controller MIME03CN (DB91-02103B) to 220614 seem to fix my pump PWM. It wasn’t modulating at all before, now it’s modulating correctly :slight_smile:

My Main Micom (DB91-02091B) is running firmware 190704, the latest firmware for this is
221130. However, without a changelog and because my HP is working well, I’m a bit hesitant to update. There’s no path to roll back without involving Samsung support. I’ll probably do it in the Spring when HP operation is less critical!

The FW files can be downloaded from https://partnerhub.samsung.com with an installer login.

Hi Glyn, is there any way of updating the firmware without buying the dongle?

I’d have to get my hands on a windows pc as well, so it would be a significant expense just for an update of firmware

No, dongle is essential as far as I know for FW update.

  • sent from my mobile device

Hi Glyn.
Finally connected the C02N today :slightly_smiling_face:.
The spreadsheet shows Main Micom version DB91-02450A 220706 and EEPROM version DB82-07081A 220622.
Are these the latest as far as you know?
(The online manual is not very helpful about FW updates…)
Thanks,
Sarah

Nice work!

I think partner hub is showing that DB91-02450A_220706 is the latest version for your HP

Same for the EEPROM

1 Like

Thanks for that @glyn.hudson.

I’ve been busy trying to reverse engineer my HTQ using your C02N and it has given me some interesting data for DHW and CH runs. (Though I won’t be able to scan a defrost cycle for a few months :face_with_diagonal_mouth:. Did you ever collect spreadsheet data over defrost?)

Also, did you ever figure out how to extract compressor power? There’s a column called “Compressor Current (degC)” ( :face_with_raised_eyebrow:!) but even if it’s really amps it makes no sense, with numbers around 2.5 when the remote display was showing about 1.2kW and the calculated heat to CH (from m.Cp.DT) was about 4.5kW (a believable 3.75 CoP for an ambient 8degC). (Just a thought - if I double the readings the numbers make sense. 2.5 x 250V = 625W, if I double this I get 1250W which is what the remote display was showing…)

Finally there’s a column called “OCT1 (degC)” with values ~10-18 when heating. Any idea what this is? (Samsung Tech Hotline hadn’t a clue…)

Thanks again.

Great! Please share your findings

No spreadsheet but I’ve got plenty of data on defrosts.

Here’s a typical defrost when its -1C outside: Emoncms - app view dashboard

If we zoom in on just the defrost section, we can see it took 5min to defrost and used 0.031kWh of elec and extracted 0.24kWh of heat from the house, which reduced the return temp by 8C. However, the heat has previously been provided in the prior 30min with a COP of 3.1 therefore the heat extracted equates to only 0.077kWh of elec in total to defrost used the equivalent of 0.11kWh of elec.

When it’s -1C outside, defrosts happen about every 60min:

1 Like

5 posts were split to a new topic: Samsiung Gen7 PWM Pump?

Hello Glyn,

On the Partnerhub site is a Service Bulletin for my unit. Do you know what it means? Is it like a recall?

@glyn.hudson I now believe those were not defrosts but frost prevention cycles - see the “When is a defrost not a defrost?” thread.

Hi all,
I’m new to this forum but I’ve read a lot of very interesting stuff here so decided to sign in !
I have been playing with my Samsung AC100 ducted unit and was searching also for a way to monitor and perform maintenance. Samsung MIM-C02N was the official way to go but a bit expensive especially after you discover it’s just a RS485 to USB converter.

So I could successfully work with a RS485 to ethernet converter (USR-TCP232-304) and can now use SNET pro 2. I’m happy to share more details on this setup if anyone is interested.

My main question is about accessing firmware files. I’ve registered on partnerhub.samsung.com (France), but my account only shows general product information and Climate Solutions commercial data, not the .hex firmware files.
Is a specific account type or registration needed on Partner Hub?

Niels

Welcome @NielsM to the forum.
This is quite an old topic and things have moved on a bit since.
Can I suggest you look at Contribution: Samsung ASHP NASA link <-> MQTT bridge (Home Assistant), particularly the later posts? There are several very knowledgeable users (@toadhall, @Topaz) who may be able to help you.
(Personally I use a cheap RS485-ethernet adapter to bring in serial data to my laptop for SNET to monitor, but don’t need anything more sophisticated, so can’t answer your questions myself.)

PS @NielsM, it would be useful if you summarised for other potential users the setup steps for the TCP232, particularly its configuration and IP assignment.

I found that the maker’s config software didn’t work and I had to use another supplier’s (Waveshare), and I had to change the default IP address (I managed, but only through guesswork - comms is not my long suit.)

I suspect we could all benefit from your experience…

My MIM-CO2N dongle is available for loan to anyone who wants to use it.

It’s only really useful for FW updates, since data logging can be done using a normal RS485 dongle.

1 Like

For info I could create an account on partnerhub.samsung.com and have access to all firmware files (needs to register a company details).

I was able to upload a firmware successfully with the RS485 adapter.
But now I experience a firmware “failed to download” (even with a new EEPROM)

I think in order to upload a firmware, SNET asks the indoor unit to switch to “download mode” to clear the communication.

Maybe there is something more than a RS485 adapter to this MIM-C02N dongle as I also have corean ? character in the "controller "and “communication check” part

I suspect also that Micom is located in the PCB, not the EEPROM as when I switched to an old PCB, the Micom changed…

Yes, there’s a ribbon cable you can connect to update firmware