It is 3degC, this graph shows it rather well (around 9 and 10 am)
Caveat here is that I have moved the outside temperature sensor to a more sensible position. The standard place behind the coil is theoretically a good place (lots of return air flow, so should be a good measurement of ambient conditions). Unfortunalely it has several drawbacks
- It is very close to the coil. I noticed when the heat-pump was running it would drop by a degree or two. Could have been picking up recirculating air but it is installed according to the manufacturers clearances.
- When it rains the measured temperature drops, since it is exposed. My other external sensors also show a drop in air temperature when raining, but only about half the Samsung drop. The other external sensors are in Stevenson screens, so I tend to believe them.
The Samsung sensor is now in a Stevenson screen (well, conduit box) under the eaves on a north facing wall and it no longer exhibits any weirdness.
It’s every 24h, see
This is from the summer.The large spikes are the HEMs exercising the heat-pump if it hasn’t run for 3 days (best to find out it’s broken before you actually need it). The small spikes you can see on the 1st and 2nd of August are the anti-seize pump cycle. They happen exactly 24h after the heat-pump is exercised OR the last anti-seize cycle was run.