Hi Sarah,
I have done a draft of the post I am preparing for the Samsung group but would appreciate any comments you have first, as below thanks
Path to a stable COP of up to 8.5 with a Samsung Gen 6 8kW
· Installed by local contractor to my design / specifications (based on the many posts I had read on the Forum thank you)
· Am in Jersey, so similar weather to South of the UK
· Self built detached house 350sq m, all underfloor heating (150mm spacing)
· High thermal mass as block built with external insulation
· High levels of insulation though not to Passivhaus standards
· Hot Water supplied by gel battery storage cylinder fed by solar (so not connected to Heat Pump)
· Old boiler was by oil with separate zone for each room
· No hydraulic separation (i.e. no buffer / volumiser etc)
· Changed to open loop by increasing temp setting on all thermostats to +25 degrees apart from lounge thermostat which was connected to heat pump controller (though not now used)
· UFH manifold mixers left in place but turned to maximum heat setting (so shouldn’t be activated)
· Monitoring using SNET-Pro 2 / Waveshare + Emoncms
· Tried all the usual settings on the controller, “Indoor Zone”, “Water outlet”, “Heat”, “Auto”, Water law, Thermostat controlled, fixed flow temp, different flow temps, different delta T / circulation pump settings etc and go some good COP numbers around 5
· However, whatever I did the Gen 6 seemed to never be in a stable state. It either did full cycling, ramping up flow temp and then shutting off for a number of minutes, or in the case of fixed flow temp it kept changing compressor frequency which I could also see from the input power fluctuating
· Like most the heat pumps fitted, in normal winter weather (i.e. not during the 1 or 2 cold spells we have per winter) my unit was clearly well over powered and likely that is why it wouldn’t stabilise.
So could I force it to work at a really low flow temperature and hence minimum output heat power and get it stable, well as it turns out yes!
· 2091 & 2092 set to not use
· 2093, suspect this should be set to not use but on mine it is on setting 3 however my controller is in an outside plant room so would never get to the required temperature.
· 2021 & 2022 both set to 25 degrees (so using water law setting but actually not doing any weather compensation)
· At a flow temp of 25 degrees my delta T became really low, so to compensate I set circulation pump to minimum setting which helped
· Delta T now around 2 degrees as opposed to recommended 5 degrees but Heat pump doesn’t seem to mind
· Set controller to “Auto”- as documented this shouldn’t make any difference to operation but it really does!
· Then followed this procedure: Increase flow temperate offset on front panel by 1 degree and leave system for a couple of hours, then change back to 0. The flow temp should then reduce down to 25 degrees and stay there. Note- without doing this I found the heat pump could go into a compressor oscillation cycle where it keeps cycling through compressor speeds and won’t break out of this. (Maybe Weather compensation also sometimes causes this instability?)
So how does it perform?
· I did the above on Jan 9th.
· Really is Low & Slow! Heat pump consumption between 284 Watts & 341 Watts which seems to correlate with compressor speeds of 14 – 16Hz, which I believe is as slow as it will go.
· Around 8kWh total usage per day which at £0.15 cheap heating tariff is £1.20 per day currently, way less than half what Oil was costing
· Circulation pump constantly using 13 Watts
· Heat output above 2kW which is enough to keep the house a pretty constant 21 degrees
· Instantaneous COP of up to 8.7 and sometimes above 8 with external temperatures between 2 & 11 degrees
· Self inflicted issue on 24th Jan, we had one UFH loop that was never turned on, I turned it on and the flow temp dropped as expected, but rather than just recover back to stability it went into the compressor oscillation cycle again (left it for 24 hours and it was stuck) so had to do the +1 degree for 2 hours then back to 0 degrees on the controller and it went back to being stable.
· As of end Jan seeing weekly COP of just under 7
Next steps
· Of course I haven’t tried these settings in a cold spell. I am hoping that it will simply be case of raising my outlet temperature by a few degrees to compensate for additional house heat loss.
· It will also be interesting to see what happens when outdoor temperatures increase with such a small delta T. I suspect I will quickly get to the point where I can’t dissipate enough heat and will run into cycling, maybe increasing outlet temperature will help and opening the windows
Worst case I just start using external thermostat.
· It will be interesting to see if I can make it stable below or above 25 degrees and keep the COP / low compressor speed, at some point I will try
Points of note
· I am hoping the above will work for some
· I don’t know what the impact of doing hot water cycles will have on your systems
· I also have a large emitter area (circa 1.5km of UFH pipe) and suspect I am able to run such low flow temperatures (and hence high COP) as I can still dissipate the required heat and therefore reach stability
· I am able to use my high thermal mass to absorb any daily fluctuations in internal temperature from external temperature changes which weather compensation would normally be required for
· Isn’t it nice to see a Samsung at the top of the tree 
· I very much look forward to hearing what you can achieve, please don’t hesitate to contact me with any queries. I am no expert but have had some experience now in optimising this unit.