Samsung 5kW Gen 6 Air Source Heat Pump Installation with monitoring

Thanks Glyn, that is very interesting to find out and puts the COP of my system in a very different light (I had also been calculating the COP from the Samsung data as Energy Generation/Energy Consumption).

I wonder if you could give some advice on how to configure my emoncms.org inputs to get closer to the values obtained from the Samsung controller.

Year Month Energy Consumption Energy Generation Energy Output COP Emoncms COP
2023 June 71.9 204.8 276.7 3.85 2.38
2023 May 102.7 306.6 409.3 3.99 2.59
2023 April 184.1 560.3 744.4 4.04 2.71
2023 March 408.3 1215.1 1,623.4 3.98 2.65

These are the calculations I have used in Emoncms:

image

image

I used the formula below as the basis of my calculation:
kW (heat) = water flow (litres/sec) x 4.2 x Temperature rise (dt in Celcius)

I have used an SHC value of 3.9 as this was the closest I could find a reference for (20% Glycol) although I think my system is closer to 10% Glycol