Praise be the installer! Credit where well earned etc.
Exactly this.
There will be slight differences in practice due to the pressure drops in the pipework. (the app will assume a certain differential pressure at all radiators, but in practice the pressure drops in the pipework will mean that each radiator valves see slightly different differential pressure)
If the pipework is VERY large then these will be negligible and you just balance on the lockshields.
If the pipework is VERY small (e.g. microbore) then these pressure drops may be large or even dominant and balancing is more of a faff.
The “easy” way of correcting for these pressure drops is from “cold start” with a thermal camera. With the radiators at an even temperature; crank the heat on and watch how quickly the radiators “fill” with the hotter water. They should all take the same time to fill if they’re the same style. You can also run around putting fingers on return pipes and guesstimating the moment they become say 5C warmer. Then tweak the baseline Kv from the app up/down to suit.