I should be getting a Vaillant 7kW ASHP installed early 2027 and I’m yet to decide if the full level-3 monitoring is for me.
My pump will have a run of around 20m, up an outside wall and through a loft space and down again to reach the plant room and the installer will use a continuous run of pre-insulated DW piping to minimize losses. This would mean that the flow meter will be >20m from the pump so maybe won’t be measuring the temperature or flow at the pump as I assume both will fall over 20m? Does this matter?
My alternative is to use an ebus reader to get the pump data into Home Assistant and a separate electrical meter to measure power. I know this won’t be the same and will depend on Vaillant numbers that may not be accurate.
Heat meter placement is a good question and one that’s not asked often enough, in my opinion - especially where long pipe runs are involved. Thanks for posing the question and kicking off the discussion.
The flow rate measurement will be the same all the way along the 20m pipe run. Such a long run will slightly increase the resistance to the flow, but - assuming no leaks - there’s nowhere else for the water to go, so the flow rate going in must be the same as the flow rate coming out.
It’s the temperature measurements which will be slightly different at different locations, because there will be some (hopefully) small but unavoidable heat losses to the environment (and potentially also a little bit from the Flow to the Return, if they’re within the same pre-insulated enclosure) along that pipe run.
From my research into System Boundary definitions (i.e. what you’ll see referenced as H4, H3 etc. in other posts) I concluded that you ideally want the heat meter’s Flow and Return temperature sensors located at the point where the pipes cross the ‘insulated envelope’ of the heated space - because you want to be measuring the heat actually delivered into the building. The key point is that it’s the performance of the overall heating system that you want to be measuring, not just the outdoor unit as one component of that overall system, and what’s important is how much heat actually makes it into the building (rather than being lost to outside).
In other words, you’d want to have the heat meter in your Plant Room anyway, not right by the outdoor unit. Placement within the Plant Room is less critical, assuming that’s part of the insulated space.
Hi David - Thanks for the detailed reply. It makes sense to me and seems to indicate that the equipment positioning will not be an issue although I guess, any conclusions about ASHP performance should always be considered in the light of some unmeasured lost heat between the pump and the metering.
Correct - although you’d be able to compare the temperatures the heat meter reports against Vaillant’s temperature sensors in the outdoor unit (or even add your own temperature sensors to the outdoor unit if you don’t trust the Vaillant ones) for some insight into the heat loss along the pipe run between the outdoor unit and your plant room.