New MCS heat load calculator and EN 12831

I’ve been invited to attend a MCS working group meeting next Monday, discussing among other things heat loss calculation, so this post alongside looking through the new MCS heat demand tool is part of my preparation for the meeting.

1. New MCS heat load calculator
I’ve been given access to the new MCS heat load calculator Heat Load Calculator - MCS. This was released December 2024. I noticed in the discussion at the time that this new version included the option to use an air tightness test result, a welcome step forward.

This new tool also implements a ventilation heat loss calculation that does follow the EN 12831 standard as opposed to the simpler calculation that originated from the CIBSE domestic heating design guide.

2. My earlier analysis of EN 12831
I wrote up my own analysis of the ventilation calculation in EN 12831 back in April 2024 in my post here Measuring air change rates with CO2 sensors for heat pump heat loss calculation - #84 by TrystanLea and then in more detail in the documentation page here: Air change rate calculation methods — OpenEnergyMonitor 0.0.1 documentation.

The key thing to note is that the total ventilation heat loss for the building is not the sum of the ventilation heat loss for each room. The building ventilation heat loss is half the sum of the rooms, at least in naturally ventilated buildings.

As I mention in the documentation post, the exact reasons for these factors are not clearly articulated in the standard. A logical explanation could be that under wind load, rooms facing the wind might have cold air pushed into them. This air would then move, pre-warmed, to adjoining rooms on the other side of the building, resulting in higher heating requirements for wind-facing rooms than those on the leeward side. The latter halving likely reflects an averaging out of these effects across the entire building.

3. MCS EN 12831 uses pre-2000 air change rates which then halve for whole building..
Interestingly rather than using 0.5 ACH for n.min.i as I had read from the EN 12831 standard the MCS calculator uses the pre-2000 air change rate values from the CIBSE domestic heating design guide (for my pre-2000 house), BUT the halving factor in the calculation halves the impact of using these air change rate values from an average of about ~1.7 ACH for my house to ~0.8 ACH.

Is there an evidence basis to use the pre-2000 air change rates from the domestic heating guide in the EN 12831 calculation?

4. Are other domestic heat loss tools adopting EN 12831?
It’s interesting that the MCS calculator is now using the latest EN 12831 calculation method but Im not aware of it being used yet in popular heat loss tools used by most domestic installers? These tools still use the simpler calculation that’s originates from the domestic heating design guide. Are there other domestic heat loss tools adopting EN 12831?

5. Radiator design and system temperatures
There a bit of a peculiar practical radiator system design & control point that results from the EN 12831 calculation in that you need to size the emitter system to be able to output more heat to each room individually than the total heat actually required by the sum of all of the rooms.

Taking the logical explanation (mine, not stated in the standard): that under wind load, rooms facing the wind might have cold air pushed into them. This air would then move, pre-warmed, to adjoining rooms on the other side of the building, resulting in higher heating requirements for wind-facing rooms than those on the leeward side. The latter halving likely reflects an averaging out of these effects across the entire building.

This would require higher flow temperatures in the wind-ward facing rooms and lower flow temperatures on the leeward side.. I guess it assumes that when it’s windy you increase the system flow temperature and then that TRV’s in the rooms on the leeward side partially close as they need less heat..

From a heat loss and system design perspective it seems like an over-complication, why not just design to an even whole house air change rate, heat loss and flow temperature but then just check that the heat pump is capable of delivering the higher temperatures for a scenario where you do balance the same heat output differently across the different rooms & emitter system?..


I’m looking forward to learning how the MCS working group process works and what the thinking is of members on the above. Comments and reflections on this welcome!

7 Likes

It’s a shame they are hiding the tool behind a sign-in, a benefit of the old excel sheet was that you could download it yourself and use it to check if any mistakes or poor assumptions had been made. The estimates for my house came back at 13kW before corrections (we ended up at 7kW). The largest proportion of the inaccuracies were from air change assumptions, so any improvement in this is very welcome!

2 Likes

It was an interesting meeting today. I realise I cant share any detail due to confidentiality requirements but it’s encouraging that MCS and group members are open to external input.

I’ve been updating the various documentation pages that I’ve written on air change rate calculations this evening to reflect what I wrote above about the use of the EN 12831 ventilation calculation in the new MCS heat load calculator. Updated pages include:

Technically the requirement to use the EN 12831 standard for heat loss calculation by MCS (I think adopted in 2012) means that both the older MCS Excel heat loss calculator (in use until December 2024) and many of the popular heat loss calculators are not actually compliant with the MCS MIS 3005 D design standard. I’m guessing that MCS are providing a grace period at the moment given that their own calculator was non-compliant for quite a few years..

This might be useful information for anyone arguing the case for a lower heat loss value in their assessment, but don’t blame the installer, this is more an issue that’s resulted from inconsistent industry guidance.

2 Likes

Agreed, it should really be open source and the EN 12831 standard should be freely available.

I got quite optimistic when they made the Home Energy Model open-source, but I see that is changing very slowly these days, and the news hasn’t reached other parts.

The good news is that there does seem to be a free PDF of EN 12831 online (one of the East European countries has the English version available)

I don’t understand what you mean there? More heat into each individual room than the total required to heat the whole building? That can’t be right.

This is the older version I think not the newer 2017 version

Yes you read that right :+1::laughing: that’s the result of the calculation! Make sure your reading the 2017 version of the standard as it all changed.

A few useful links:

The new MCS heat load tool was part developed by Build Test Solutions and also includes the option to enter a measurement based HTC value:
#heatpump #uvalue #airtightness #mis3005 #mis3004 #energyefficency | Build Test Solutions | 20 comments

This is good overview of the ventilation heat loss calculation changes by Heat Box: New MCS requirement: heat loss calculations must follow new standard from June 2025 including a note that compliance is expected by the 2nd of June 2025:

image

1 Like