New heat pump Grant R290 - hot water advice

@glyn.hudson I tried this yesterday and part of today. I love the idea of this setting - I see it as helping the flow temp to sortof “gravitate” toward the thermostat temp which is good.

Something I didn’t like - I set my thermostat to 21 and didn’t touch my hysteresis which is 0.4c (I haven’t ever touched this setting) and the result was obvious - the ASHP switched off when I hit 21 and then only turned back on again when I hit 20.6.

What I would prefer is that the thermostat didn’t deactivate the circuit but instead was used with the room temperature correction to sortof gradually guide the flow temp back down to where it needs to be to maintain the thermostat setting. Not sure if this is possible or not or whether it makes sense, it feels that it does in my head :slight_smile:

1 Like

It sounds like you have pump blockade enabled? This magic will only happen when pump blockade is disabled, which is the default option.

It’s interesting your hysteresis is 0.4C by default, mine is 1C by default.

This is exactly how it works for me with pump blockade disabled.

Potentially my installer changed the hysteresis to 0.4, they certainly disable room temperature correction (if the default is indeed 4).

My thermostat pump blockade is disabled (set to NO).

So my thermostat was set to 21 which was resulting in a target temp of 30, then at 09:55 this morning it achieved 21 and then the target temp was set to what seems to be “off” which is 26, so the ASHP stopped and the flow temp just coasted (as it does) until 11:21 when the thermostat hit 20.6 and then the target temp shot back up to 31 which caused the ASHP to go full pretty much full whack (65hz, 700rpm fan) for about 25 mins until it got back up to target temp.

0.4 is a very low hysterisis, I wouild recomend increasing this to 1

Does your circ pump run in been cycles?

Here’s the data from my system if you want to compare: https://heatpumpmonitor.org/dashboard?id=748

Yeh my pump runs when the system is idling, 14l/m it seems. Up until I saw your post I’ve been experimenting with using only the weather comp curve - e.g set thermostat to something it won’t ever reach and simply use the curve which does seem to work well.

I think if I did use the thermostat in the way intended and set a hysterisis of 1 I’d get some largish swings in temp - do you not find this?

Just found this Glyn…

7.14 - Circuit Operation

7.14.2 - Weather Compensated Circuits

With a thermostat

  • When a target air temperature is set on the assigned thermostat, the smart controller calculates flow based on ambient temperature, heating curve and current circuit air temperature.
  • If ‘THERMOSTATIC PUMP BLOCKADE’ is enabled, the circuit demand will be stopped once the target air temperature set on the thermostat is reached.
  • If ‘THERMOSTATIC PUMP BLOCKADE’ is not enabled, once the target air temperature is achieved the smart controller will use decrease the flow temperature target by the ‘DECREASE WATER TEMPERATURE’ value, which is set correctly will maintain the target air temperature. Refer to 7.3.1.3 for recommended setback values based on heat emitters for the circuit

Section 7.3.1.3 is talking about night air temp setbacks so it doesn’t feel very applicable, but here is the setbacks:

I think they mean Decreasing fixed water temperature (confusing use of the word fixed there if they do), which is in Service Parameters → Installer controller →Circuit 1 H1 → Decreasing fixed water temperature.

What is this set to for you? Mine is 17 which I think may explain things (set by my installer, not me!), because that effectively would just shut everything down as soon as the thermostat hits its limit. I’m guessing yours is set to something far more modest.

Not directly related to previous, so maybe needs a new thread, but I have seen a couple of defrosts recently, which happened at about 7c ambient, 99% humidity, as the compressor ramped up fast. You can detect it in home assistant since the fan stops, while the compressor keeps running. Obviously flow and return temps swap too, but that can happen anytime to a small extent. This is what it looks like.The impact on house temp was small to none.

Fwiw, my (room temp) hysteresis is set to 0.2c, and I check 17 temp sensors in 5 main areas, to decide whether to start or stop the heatpump. With very low wc curve it only cycles off when the sun come out big time, else it just about holds temperature in the 0.2c range. If it does cycle, I may need more hysteresis, but at current ambient 0.2c works fine. Did need some fine tuning of wc curve though.

Well I did want pump modulation and boy do I have it! :rofl:

Heat pump doing pretty serious short cycling. It’s running general factory defaults (after updates) other than set-temps, wc heating curve 0.6 and room temp correction at 1.0.

The sharp ramp from 11-23l/m every 4 mins was causing a lot of noise, so I reduced the max pump speed to 70 (see next picture for impact). This resolved the noise and improved COP, but feel I’m mitigating the problem rather than solving it…

Any thoughts as to what I should change? (live dashboard link).

Many thanks,

Matt

Mmm I’ve seen this before, an installer recently showed me the data from a recently installed 6.5kW Grant, it’s been doing this since day 1: Emoncms - app view

Out of interest, could you try increasing the WC curve to increase the flow temperature to see if this makes any difference. I think this could be some sort of software gitch.

Mine often seems to go into defrost at the beginning of a DHW cycle, not sure why since there’s no frost on the evaporator. Maybe it’s a preventative defrost? Emoncms - app view

Thanks for getting back Glyn, I agree that looks like an identical pattern to what I’m seeing, if it’s a new install it maybe running the same firmware. I’ll bump up my WC curve and see if that has any impact, frustrating as it’s already off for long periods as hitting temp.

Mine short cycled at flow temps below 31 or 32 - the problem is the heat boost when the compressor starts (always at full tilt for a minute or two) pushes the return water temp above the cutoff (which is 5c below the target temp) and the pump shuts down, only to restart asap. Raise the target temp and it doesn’t happen.

Interesting, thanks Dave. Can I raise the target temp without impacting the heat delivered as it’s pretty hot already.
Giving good results despite the short cycling but I do worry about unnecessary wear.
I’ll look into it more…

As the flow temperature is lowered, the emitters (radiators?) will be unable to emit as much heat. There becomes a point where the emitters are unable to emit the minium modulated output of the heat pump, cycling is then inevitable. UFH can run a lower flow temperature than radiators without cycling, since UFH generally has much more emitter area. But as long as not cycling more than about 4 cycles per hour, then this nothing to worry about.

Here’s a calculator to approximately calculate the minimum flow temperature for a system, in practice you may be able to run a bit lower than this, it’s just a guide Heatpump minimum flow temperature calculator - Google Sheets

No, assuming constant pump speed increasing the flow temperature will increase the heat being delivered: Heating Power = flow rate * (flow temp - return temp I.e DT) * Specific Heat of Water

You could turn on “Pump blockage” this will turn the heat pump off when the room set point is reached to avoid overheating. This will cause cycling, but as long as it’s not cycling more than 4x per hour I wouldn’t worry about wear. Inverter driven compressor are quite happy to stop and start.

It looks like the flow rate oscillation issue is still present, this looks like a bug to me. I reckon you should try and hassle Grant again :sleepy_face:

Thanks for your thoughts on this. I’m running at WC curve of 0.8 (up from 0.6), but the recent cold weather and higher flow temps (35-38C) doesn’t seem to address the cycling. Each cycle is between 3 and 4 minutes long, so 15-20 cycles an hour. You’ll see there is a short period between 5-6am where it is not cycling and working as I’d expect. I can’t match the cycling to either the flow temp or the proximity to room temp, so struggle to narrow down best settings to remedy.
I have to say limiting the maximum flow has really helped with the pump ramp up noise though.

I’ve radiators upstairs (which are a little oversized - due to a siting issue) and Variotherm in-wall heating on 4 of the walls downstairs (so the emitters are large). I did wonder about changing the setting from radiator to UFH?

Thanks @glyn.hudson, no hurry on this but when you’re next in there, below is the additional info (OEM ID: 717)

New Radiators - tick

Hot Water

  • Cylinder volume - 225l
  • Coil or heat exchanger area - 1.8m
  • DHW target temperature - 48c
  • DHW control type - schedule
  • Legionella frequency - none

Property

  • Age - change 1950s
  • Assessed space heat demand - 4902kWh
  • Assessed water heat demand - 2796kWh

Generation

  • Annual solar PV genertion 3750kwh
  • Solar PV self consumption 47%
  • Battery storage capacity 9.6kWh

I wouldn’t really call this cycling, since the compressor is not cycling. The fluctuation in heat output is caused by the circ pump speed oscillating. Quite bizarre

Sure, I’ll add that info

I would suspect the flow sensor lying.. Bubbles or microbubbles, If It is an ultrasonic sensor, really mess up measurement, or maybe there is some flapping valve someplace? Does the econet controller (Ok, much less accurate I know) show the same wobbles, or is it an artefact of the emon system??

The oscillation is definitely occurring the ramping up of the pump woke me up, which is why you see the heating being turned off at 3am. With the max pump speed limiter set to 70 this is much improved. The data history on the econet controller is at 5 minute resolution (averaged) and as the oscillation is over a 4 minute cycle it doesn’t show this effect.

Ah, i am querying the local econet api with home assistant so I get 30 second data granularity. I am urprised the water pump can/does ramp up and down that fast. Sounds like a bug in the control system to me.. Mine doesn’t (can’t?) change at anything like that rate.