Hi Trystan,
I will try to keep this simple and confine it to the relevant part about the conservatory.
The house was surveyed on 24 March 2023.
The surveyor said initially that the conservatory would be unheatable, the radiator removed and the room excluded from the heat loss calculations.
At the end of the survey he said good news, you can keep the conservatory as the heat loss is only 827w and the radiator is big enough.
The total heat loss was 7,300w so I got the 9kW heat pump.
The heat loss was 6,500w for the house and 827w for the conservatory.
Then my problems start when I want to heat.
I told everybody from the surveyor to the installers that I wanted to run at 35c or less on pur weather compensation. Nobody at any stage said I have no chance with those radiators, perhaps because I wouldn’t as they can handle about 2,500w at a delta t of 15c
The house was resurveyed on 23 November 2023.
The heat loss is now 7,400w but split differently, 5,100w for the house and 2,300w for the conservatory.
The differences are that the conservatory had been surveyed in March with a tiled roof and 300mm of loft insulation. If it had been done properly in March the conservatory would have had to have been excluded as they don’t have a suitable radiator for it.
By coincindence, or otherwise the house heat loss is now only 5,100w instead of the 6,500w surveyed in March.
This means the overall heat loss is the same.
Now Octopus say my conservatory must be heated, it cannot be excluded, I don’t know why the change of stance.
Concentrating on the house, the heat loss is actually a bit less as the MCS treat all houses equally based on age in terms of air changes, our house is an epc B89 so the heat loss is overstated somewhat because of this.
So what I find is that if it is 10c outside the house might require 2,000w and the conservatory 500w but the conservatory has to have 1,000w as it makes up one third of the total heat loss.
The heat pump is sized to deliver 2,300w of heat to our consevatory when it is -2.3c outside. It can’t do that as the radiator isn’t big enough.
The radiator is actually sized to provide the heat required by the original heat loss calculation, 827w, it actually does more than that but not 2,300w
I have a heat pump that puts out a minimum of 4,500w if I try to run it efficiently
My house needs 2,500w, the heat pump is putting out 4,500w so either the house gets hot, the COP is poorer than it could be or I run i in shorter bursts.
If I run it in shorter burst the initial power consumption of the massive compressor (from a 16kW heat pump) and the circulation pump designed to cope with properties three times the size of mine is so much that the COP is even worse. I find it no more costly to run for longer periods than in short bursts, I may as well be warmer for the money.
All this is because we have a bigger heat pump than we would have had if the heat loss calculation had been performed correctly in March.
Now Octopus are saying it is still the correct heat pump because the conservatory needs it.
So what I have is a heat pump that’s primary purpose is to produce enough heat to satisfy our conservatory with the secondary function of the remaining heat produced going into the house that we actually live in.
I hope it’s not just me, I can’t see how it is possible to design a heat source that can supply 31% of the heat produced to 12% of the heated space of the property using just radiators.
That is my problem with it.