I did the @SarahH Sarah Hanson test which I find v.interesting. Details below
Test conditions
Parameter | Value |
---|---|
Location | ***, UK |
Test Date | 18-19 March 2025 |
Time Period | 8 PM – 6 AM (10 hours) |
Heating | Off during test |
Outdoor Temperature | 3.55°C (average) |
Indoor Temperature Start | 21.2°C |
Indoor Temperature End | 16.4°C |
Heat Pump Output | 4kw |
House Type | Well-insulated with radiators |
Findings & Observations
Metric | Value |
---|---|
Temperature Drop (°C) | 4.8 |
Cooling Rate (°C/hour) | 0.48 |
Surveyed Heat Loss of house | 2.254 kW |
Estimate heat loss in the period | 1.74 kW |
Average heat loss in the period | 2 kW |
c.Thermal Inertia | 9,000 kJ/K |