Hi Thierry,

I’m in the US, so am on the same type of grid you are.

200 Amp service is quite oftem very misunderstood. More info here:

Your 18 kW heater draws ~75 Amps, so you might be better served by a 100A:333mV CT.
(150A:333mV CTs are also available) The downside is finding one with a large enough wire-window to accommodate your Service Entrance Wires.

Info on said CTs here:

https://learn.openenergymonitor.org/electricity-monitoring/ac-power-theory/use-in-north-america

The table is about half-way down the page.