Help for calibration on Emonlib on ESP32

Hi Thierry,

I’m in the US, so am on the same type of grid you are.

200 Amp service is quite oftem very misunderstood. More info here:

Your 18 kW heater draws ~75 Amps, so you might be better served by a 100A:333mV CT.
(150A:333mV CTs are also available) The downside is finding one with a large enough wire-window to accommodate your Service Entrance Wires.

Info on said CTs here:

https://learn.openenergymonitor.org/electricity-monitoring/ac-power-theory/use-in-north-america

The table is about half-way down the page.