Heat Demand vs Calculated

Our Vaillant Arotherm + 10Kw has been running for a good few months and coming up to first winter.

Everything is working good, the HP is cycling 60min and running for roughly 15 ish minutes(we have not had any seriously cold days).

I’m fairly certain our heat loss is closer to what the calculated one is, as we have been using a 7.5Kw Mitsubishi Aircon for heating for the last few years, and it used to keep most of the downstairs warm except on the very cold days. Our hot water cylinder is in the Garage (not insulated or heated)

Is it normal to see a big difference between the Calculated Heat loss (8.07 Kw) and Heat Demand 2.53 Kw)? Or is this just due to lack of data, I had a peruse around a few other systems and could not find any others with such a big difference.

Hi ispookie666, I think you do need more cold weather days in the data set. Keep gathering data over the next 4 months.
Good luck,
Frank

The temperature has dropped, but the cycling has not; it seems to be like clockwork. I tried flattening the heat curve from 0.4 to 0.35 to 0.3, but it hasn’t made much difference.

I adjusted the pump speed (fixed at 70%) to auto, and the result is the same (it was in Auto previously). I am tinkering with the energy integral - it was set to -60deg min, and I have changed it to -90deg min, will increase it to -120deg min.

All this seems to point to low system volume(detached, floor area is roughly 160sqm house, and I’m surprised) - will adding a volumiser help with this?