Enhancing setup

Hi Robert,

Thank you for your responses.

I really like the sound of this idea. The single phase boards are on different phases, so it would look something like this:

Garage DB - 3-phase
Basement DB - 3-phase
FF DB - single-phase (L1)
Office DB - single-phase (L2)

emonTx 1:
AC adapter on L1 for voltage reference
Garage DB (L1)
Basement DB (L1)
FF DB
optional: desensitise 4th input for grid L1

emonTx 2:
AC adapter on L2 for voltage reference
Garage DB (L2)
Basement DB (L2)
Office DB
optional: desensitise 4th input for grid L2

emonTx 3:
AC adapter on L3 for voltage reference
Garage DB (L3)
Basement DB (L3)
optional: use 3rd input, or desensitise 4th input, for grid L3

Have I understood correctly?

Could you expand on this further please as I think I’d like to capture the grid supply too – it seems like a waste not to. I found your response to someone in 2018, below, is this still current/correct?

I can’t seem to find a 27 Ω / 0.5% / 0.1W - do you have any ideas? From RS I can get a 27 Ω ±1% / 0.25W (here) but I’m happy to shop around if it exists.

Would it make sense to modify all three emonTx units and put the grid on input 4 on each, so that each phase of the grid supply is on a “modified” input… or doesn’t it really make any difference?

What is the reference to the calibration constant in the sketch when using this fourth input?

Thank you for your help here and on my previous posts – you are a real asset to this forum!

Ben